Can an Induction Motor be Used as a Generator for a Micro-Hydro Power System?

  • Thread starter Thread starter VooDoo
  • Start date Start date
  • Tags Tags
    Design Micro
AI Thread Summary
An induction motor can function as a generator when it spins above its rated speed, with the power angle determining its operation mode. For a motor rated at 1500 RPM, designing a turbine to run at 1600 RPM should allow it to generate power and connect to the grid, but synchronization requires careful management of voltage, phase, and frequency. If the generator is disconnected from the grid while generating, it will continue to run at no load, but the transition between motor and generator modes depends on the power angle. Doubly-fed induction generators (DFIG) may be suitable for micro-hydro applications, but availability and cost compared to asynchronous generators need further investigation. Understanding the electrical dynamics and operational limits is crucial for successful implementation.
VooDoo
Messages
58
Reaction score
0
Looking into “reverse engineering” a pump and running it like a turbine and using an induction motor of some sort generate power. Basically design/build my own micro-hydro power system. The system if I do go ahead with it, will be connected to the grid.

I am very capable of handling the mechanical side of things, however I have a lot of reading to do when it comes to the electrical side. From what I have read so far I need an asynchronous generator (or induction motor).

I will list my questions, it makes it much easier to read:

1. From what I have read, I understand if the induction motor spins above the rated motor speed it becomes a generator, anything below the motors rated speed and it becomes a motor. Is this correct?

2. Suppose the motors rated speed is 1500rpm, and I design my turbine to spin at 1600rpm and connected it to the motor, will it begin to generate power and automatically synchronise to the gird? What happens if there is a sudden increase in flow rate and the turbine spins up to 1950rpm what would happen to the generator, would it continue to produce power and synchronise to the grid? Is there a maximum speed the generator can handle? I know for a synchronous generator I can use that formula to calculate synchronous speed (depends on number of poles and grid frequency), is there a certain percentage of this that should not be exceeded by an asynchronous generator for example the turbine speed should not go higher than 10% of the synchronous speed?

3. What happens if the generator is happily generating and is suddenly cut off from the grid? For example it is turning at 1600rpm and then suddenly it is disconnected from the grid, it is turning too fast to be a motor. Or if there is a spike or instability in the grid?

4. I was told to look into a doubly-fed induction generator, (DFIG). Would a DFIG system suite my application? I have tried searching for DFIG manufacturers and couldn’t find anything, are there any companies that sell complete DFIG units? Are prices substantially more expensive than that of an asynchronous generator?


Thanks for any help in advance, I understand I have a lot of reading to do!
 
Engineering news on Phys.org
Apologies, just realized I posted this in the wrong section, was ment to go in electrical.
 
VooDoo said:
1. From what I have read, I understand if the induction motor spins above the rated motor speed it becomes a generator, anything below the motors rated speed and it becomes a motor. Is this correct?

The power angle will determine if the electric machine operates as a motor or generator. Essentially if you have a motor and its shaft spins faster than its rated speed it will change the power angle and cause it to back-feed the source (grid in this case). However, if no electrical power is being applied to the motor and you rotate the shaft, the motor becomes a generator and will provide an electrical power output.

VooDoo said:
2. Suppose the motors rated speed is 1500rpm, and I design my turbine to spin at 1600rpm and connected it to the motor, will it begin to generate power and automatically synchronise to the gird? What happens if there is a sudden increase in flow rate and the turbine spins up to 1950rpm what would happen to the generator, would it continue to produce power and synchronise to the grid? Is there a maximum speed the generator can handle? I know for a synchronous generator I can use that formula to calculate synchronous speed (depends on number of poles and grid frequency), is there a certain percentage of this that should not be exceeded by an asynchronous generator for example the turbine speed should not go higher than 10% of the synchronous speed?

If you are completely powering the electric machine via a mechanical source then you have a generator. To connect it to the grid the voltage, phase, and frequency must be within a certain tolerance or you'll have a big problem. If it is out of phase enough then it will damage your prime mover. If the machine is already connected to the grid and acting as a motor and you speed up the shaft so that the power angle changes (I forget off the top of my head which way) then it can start to provide power to the grid. However, you'll still have a big problem since your little generator won't load share properly with the grid (essentially an infinite bus).

VooDoo said:
3. What happens if the generator is happily generating and is suddenly cut off from the grid? For example it is turning at 1600rpm and then suddenly it is disconnected from the grid, it is turning too fast to be a motor. Or if there is a spike or instability in the grid?

If you somehow managed to load share with the grid and then disconnected your generator, nothing would happen other than the generator would be running at no load. The point you need to be aware of is that an electric machine will operate as a motor or generator depending on the power angle (which depends on the electrical load and mechanical load). If the electrical power input is higher the machine will act as a motor, if the mechanical input power is higher, it will act as generator.

Research "motor to generator transition" to find out more information. Most books on electric machines will have a section on this.

VooDoo said:
4. I was told to look into a doubly-fed induction generator, (DFIG). Would a DFIG system suite my application? I have tried searching for DFIG manufacturers and couldn’t find anything, are there any companies that sell complete DFIG units? Are prices substantially more expensive than that of an asynchronous generator?

I'm not familiar with DFIG's.

Hope this helps.

CS
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top