Copper loss, calculated using the formula P = I²R, refers to power lost due to resistance in electrical wires. It can be reduced by using larger wires, which have lower resistance; however, the "skin effect" in AC current can limit the effectiveness of this approach. For accurate calculations, factors such as the application type, wire dimensions, and temperature effects must be considered. Installing capacitors can help reduce reactive current in inductive loads, potentially lowering copper losses at the meter. Understanding these principles is crucial for effective loss management in manufacturing and commercial settings.
energysaver
Messages
7
Reaction score
0
Good day. just want to ask anyone about copper loss. How is it computed for example in a manufacturing plant or in a dept mall.Could anyone give an illustration/example?

Also , is it true that copper loss can be reduced by using big wires?What if the wire is big enough?

thank you. hope you can help me...
 
Engineering news on Phys.org
energysaver said:
Good day. just want to ask anyone about copper loss. How is it computed for example in a manufacturing plant or in a dept mall.Could anyone give an illustration/example?

Also , is it true that copper loss can be reduced by using big wires?What if the wire is big enough?

thank you. hope you can help me...
Copper loss is the power lost because of the resistance in the wires. P = I2R.

Big wires have less resistance, but with AC current there is such a thing as the "skin effect", which means that most of the current is concentrated around the surface of the conductor, lowering the effective cross sectional area of the conductor and increasing its resistance.
 
what estimated percentage of a copper loss in a certain manufacturing plant? if i install capacitors in loads , would the demand at the meter be reduced by 10% by eliminating copper loss?...

thank you...
 
You are correct. If you have an inductive load (induction motor, for example) with a poor power factor, a capacitor could reduce the reactive current and the resultant current demand at the meter. Power meters usually measure only real power, and not reactive power, however, so as you point out, only the extra I2R losses in the copper are reduced.

Bob S
 
Hello

as our colleagues says in the above replies , copper losses is equivalent to I^2 X R

but what type of application are you going to calculate copper losses for ??

for example , if you are going to calculate copper losses for a flat busbar just calculate the resistance by knowing the cross sectional area of the bar and its length and the grade of copper you are using and then calculate it by resistivity x length divided by area then multiply the result by the current squared

but if you need to calculate this losses for temperature rise or when considering the heat effect for a transformer as an example then take into your consideration the current density , and the heat dissipation to the surrounding , and there are specific tables which can guide you to select the value of the current density in the first place as if you only looks at the value of the losses , it will not give you good indication for temperature rise

hope information was useful for you
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top