Averagesupernova said:
I would think a properly designed circuit would have a current transformer that is matched to the circuit concerning inductive reactance. A CT designed for a 60 Hz circuit would be a poor choice for a 100 Khz circuit. It would probably have enough inductance to insert too much impedance in series with the load which of course would be reflected as a voltage across the primary. So, when the higher frequency CT is properly sized down inductance-wise it should behave the same as the 60 Hz version when the secondary is opened. For the sake of this discussion though, let's stick to 60 Hz at least until we get that part ironed out.
I think you are overcomplicating things. Consider this scenario: Suppose we have a laminated iron core with lots of windings on it which gives us many henries of inductance. Now, suppose we hook a battery to this coil with a resistor that limits current to 50 amperes. The full battery voltage will appear across the coil the moment the switch is closed. Slowly the current ramps up and is limited to 50 amperes by the resistor. At this point we will say that the core has not saturated. But suppose that by design it does saturate at 75 amperes. Now we will cut the value of the current limiting resistor in half and do the same thing over. Current is now limited to 100 amperes. We connect the battery up and the current ramps up and goes past 50 amperes and continues on towards 75 amperes. It ramps up as expected, but when it reaches 75 amperes the core becomes saturated and there is no longer a CMF to counter the current. Now at 75 amperes the circuit is only limited in current by the resistor and the current slams up from 75 amperes to 100 amperes almost instantly. THIS is what happens when a core saturates. In current transformers that have the secondary winding properly shorted, there is virtually no chance of core saturation to begin with no matter how small the core is (within reason) as long as it is run within design limits. I believe you have shown this in previous posts. So, the core by design is shrunk down as small as possible which puts it somewhat close to becoming saturated if the secondary is terminated into something other than a short or at least something other than what it was designed for. One reason for this is cost reduction by reducing materials, another is that less core means less series impedance. The idea is to keep the primary voltage as low as possible in normal operation so all the voltage ends up across the load instead of part of it across the transformer. So now we have a transformer core that easily goes into saturation if the secondary is opened or partially opened. The hypothetical case I gave above with the 50/75/100 amp will apply here too. Since the CT core will saturate easily when run this way, it saturates virtually right away in the AC cycle. A saturated core will offer little impedance to current. I don't know how many different ways I can cover this to try to get you to understand why I say what I do. I guess it all depends on how far into the AC cycle that the core actually does saturate, but it is my belief that by design they would be made to saturate fairly quickly for reasons I gave above.
I perfectly understand what you're saying about the current spiking upward at the onset of saturation. I've been a practicing EE 31 yrs. and am currently a doctoral candidate. After grad school (MS) I worked at an aerospace & defense corporation, fortune 50, in the magnetics design group. Among my products was CTs. Here is where you and I differ.
"Reactance" is a small signal linear concept. Inductance at the onset of core saturation is ambiguous. There is a "normal" inductance, as well as an "incremental" inductance. Picture a B-H curve where we are right at the onset of saturation. What is the inductance value? By definition, N*phi = L*I, or L = N*phi / I. But phi = Ac * B, where Ac = core cross sectional area. Hence L = Np*Ac*B / I. But B flattens out once saturation is reached. I, meanwhile, keeps increasing. A line drawn from the
origin to the operating point on the B-H curve gives the
normal value of L, or Lnorm. This value
gradually decreases as I increases and the core goes deeper into saturation. But, if we draw a line
tangent to the operating point, and take the slope Np*Ac*delta B / delta I, that is the
incremental inductance, Lincr. At the onset of saturation it is this value, Lincr, that plummets.
Nonetheless, if we force a constant B, i.e. as in a VT, then one saturation is reached, the magnetizing current will indeed skyrocket. Since B flattens out, while H continues rightward (or leftward for negative half of cycle), forcing an increase in B incurs a huge increase in H.
But what happens when we force H, i.e. current mode of operation where the current is fixed by an independent power source and a load resistor? Picture the B-H curve. We increase H up to the onset of saturation. When we continue to increase H. remember that increasing H results in only a small increase in B, by definition of saturation. B is related to
volt-seconds, not volts. Thus the volt-second product keeps increasing, but converges upon an asymptotic limit. As time progresses, the volts will decrease. The saturated core does not provide the near zero reactance you're saying it does.
Every 60 Hz cycle results in the B-H loop being traversed. The area inside the loop is the hysteresis loss (non-conservative), and more importantly, the area between the loop and the B axis is the stored and recoverable per cycle energy (conservative). Thus a core overdriven into saturation on both halves of the ac cycle stores much more energy and flux than an inductor with an incremental inductance value equal to that of the CT in saturation.
Your position is that since the CT core is saturated, its reactance is tiny and thus the Vp value is tiny. But you are not considering Lnorm, but rather Lincr. The B-H loop clearly demonstrates that the flux, energy and Vp value are determined by Lnorm, and not Lincr. Big difference. Is this helpful? BR.