Why does the magnetic flux in a CT core decrease with connected load?
In summary: CVS (constant voltage source) and the counter-counter mmf of the secondary current. The primary current increases to supply this additional mmf which restores the original core flux.For a CT, the primary current is the source of the primary mmf which establishes the core flux. The secondary current being the counter mmf which reduces the core flux. But the primary voltage is also an input to the mmf which is countered by the primary current. The secondary voltage is small, but the secondary resistance is small, so the secondary current can be large. The secondary voltage is the counter-counter mmf. It is this voltage which supports the primary current and the primary voltage source supplying the
  • #36
b.shahvir said:
Assume ideal conditions i.e. zero winding impedances in pri and sec. Also assume load or burden impedance to be zero. The sec will draw infinite amps, ideally! So, what will happen to core flux in this case? Will it increase, decrease, remain constant or disappear (become zero) altogether? The reply would be interesting!
Well, I suppose it depends on what ideal is, but with 100% coupling and no leakage, infinite current in the both coils will result in no flux in the core. Doesn't transformer design theory tell us this? The only way flux actually builds up in the core is when a voltage starts to appear across the coil right? Since the flux in the core is what indirectly causes the reactance then if we say infinite current this implies zero reactance. I know it may sound like I am contradicting myself but it really isn't a contradiction.
  • #37
Averagesupernova said:
I would think a properly designed circuit would have a current transformer that is matched to the circuit concerning inductive reactance. A CT designed for a 60 Hz circuit would be a poor choice for a 100 Khz circuit. It would probably have enough inductance to insert too much impedance in series with the load which of course would be reflected as a voltage across the primary. So, when the higher frequency CT is properly sized down inductance-wise it should behave the same as the 60 Hz version when the secondary is opened. For the sake of this discussion though, let's stick to 60 Hz at least until we get that part ironed out.
I think you are overcomplicating things. Consider this scenario: Suppose we have a laminated iron core with lots of windings on it which gives us many henries of inductance. Now, suppose we hook a battery to this coil with a resistor that limits current to 50 amperes. The full battery voltage will appear across the coil the moment the switch is closed. Slowly the current ramps up and is limited to 50 amperes by the resistor. At this point we will say that the core has not saturated. But suppose that by design it does saturate at 75 amperes. Now we will cut the value of the current limiting resistor in half and do the same thing over. Current is now limited to 100 amperes. We connect the battery up and the current ramps up and goes past 50 amperes and continues on towards 75 amperes. It ramps up as expected, but when it reaches 75 amperes the core becomes saturated and there is no longer a CMF to counter the current. Now at 75 amperes the circuit is only limited in current by the resistor and the current slams up from 75 amperes to 100 amperes almost instantly. THIS is what happens when a core saturates. In current transformers that have the secondary winding properly shorted, there is virtually no chance of core saturation to begin with no matter how small the core is (within reason) as long as it is run within design limits. I believe you have shown this in previous posts. So, the core by design is shrunk down as small as possible which puts it somewhat close to becoming saturated if the secondary is terminated into something other than a short or at least something other than what it was designed for. One reason for this is cost reduction by reducing materials, another is that less core means less series impedance. The idea is to keep the primary voltage as low as possible in normal operation so all the voltage ends up across the load instead of part of it across the transformer. So now we have a transformer core that easily goes into saturation if the secondary is opened or partially opened. The hypothetical case I gave above with the 50/75/100 amp will apply here too. Since the CT core will saturate easily when run this way, it saturates virtually right away in the AC cycle. A saturated core will offer little impedance to current. I don't know how many different ways I can cover this to try to get you to understand why I say what I do. I guess it all depends on how far into the AC cycle that the core actually does saturate, but it is my belief that by design they would be made to saturate fairly quickly for reasons I gave above.
I perfectly understand what you're saying about the current spiking upward at the onset of saturation. I've been a practicing EE 31 yrs. and am currently a doctoral candidate. After grad school (MS) I worked at an aerospace & defense corporation, fortune 50, in the magnetics design group. Among my products was CTs. Here is where you and I differ.
"Reactance" is a small signal linear concept. Inductance at the onset of core saturation is ambiguous. There is a "normal" inductance, as well as an "incremental" inductance. Picture a B-H curve where we are right at the onset of saturation. What is the inductance value? By definition, N*phi = L*I, or L = N*phi / I. But phi = Ac * B, where Ac = core cross sectional area. Hence L = Np*Ac*B / I. But B flattens out once saturation is reached. I, meanwhile, keeps increasing. A line drawn from the origin to the operating point on the B-H curve gives the normal value of L, or Lnorm. This value gradually decreases as I increases and the core goes deeper into saturation. But, if we draw a line tangent to the operating point, and take the slope Np*Ac*delta B / delta I, that is the incremental inductance, Lincr. At the onset of saturation it is this value, Lincr, that plummets.
Nonetheless, if we force a constant B, i.e. as in a VT, then one saturation is reached, the magnetizing current will indeed skyrocket. Since B flattens out, while H continues rightward (or leftward for negative half of cycle), forcing an increase in B incurs a huge increase in H.
But what happens when we force H, i.e. current mode of operation where the current is fixed by an independent power source and a load resistor? Picture the B-H curve. We increase H up to the onset of saturation. When we continue to increase H. remember that increasing H results in only a small increase in B, by definition of saturation. B is related to volt-seconds, not volts. Thus the volt-second product keeps increasing, but converges upon an asymptotic limit. As time progresses, the volts will decrease. The saturated core does not provide the near zero reactance you're saying it does.
Every 60 Hz cycle results in the B-H loop being traversed. The area inside the loop is the hysteresis loss (non-conservative), and more importantly, the area between the loop and the B axis is the stored and recoverable per cycle energy (conservative). Thus a core overdriven into saturation on both halves of the ac cycle stores much more energy and flux than an inductor with an incremental inductance value equal to that of the CT in saturation.
Your position is that since the CT core is saturated, its reactance is tiny and thus the Vp value is tiny. But you are not considering Lnorm, but rather Lincr. The B-H loop clearly demonstrates that the flux, energy and Vp value are determined by Lnorm, and not Lincr. Big difference. Is this helpful? BR.
  • #38
:confused: Hi, can someone please explain to me the logic behind the representation of 'Magnetic Hysteresis loss' as a resistance in electrical equivalent circuits?... will be extremely grateful.
I have studied some info on this subject on the net. Even though the physics of Hysteresis Loss has been explained appropriately, I wish to dwell deeper into the phenomenon to get to the source of my doubt. In spite of the relevant theories, it becomes difficult to visualize a magnetic phenomenon into an electrical parameter as mentioned by me earlier. When we talk of energy expended by the power source to ‘pump up’ the magnetic field in the core, sounds a bit abstract!
I want to understand what phenomenon in the magnetic hysteresis causes the machine (Xmer or motor) to suck an additional losses (wattful) current from the power source.
Is it a result of the delay caused by the magnetic dipole friction in the magnetic core... which prevents the magnetic field from building up quickly? I would be grateful if someone could elaborate on this part. Thanx.
Kind Regards,
Shahvir
  • #39
The asymtotic limit, [itex]B= B_n + H \mu_{i}[/itex] is obtained from the incremental permeability, which is, of course the permeability of air. It is one of a family of curves having constant slope. We should shift our perspective, with the permeability of air set to unity, to scales where [itex]\Delta B = \Delta H[/itex].
In best case, the incremental inductance approches a lower limit as [itex]\mu \rightarrow \mu_{0}[/tex]; the incremental inductance is that of an inductor with the core removed.
[tex]L=N^2 \mu_{0}A_e / l_e[/tex]
In reality it's less, as both A_e and l_e vary, taking up all space; the mutual inductance between windings is decreased.
  • #40
cabraham, can you explain how an SCR works?
  • #41
b.shahvir said:
:confused: Hi, can someone please explain to me the logic behind the representation of 'Magnetic Hysteresis loss' as a resistance in electrical equivalent circuits?... will be extremely grateful..
A piece of fermomagnetic material is full of domains. A domain is a region of uniform magnetic dipole moment. In a piece of deGaussed material the domains point in random directions constrained by the crystaline latice to discrete orientations. Magnetizing the material means you are making more domains point in a preferred direction. The more domains that align, the further up (or down) the B-H curve you are. It takes energy to reorientate that domains. I don't know why. Ask the guys proficient in solid state physics. It could be bulk lattice distoration, or energy state changes of the atoms at grain boundries--any number of things...
  • #42
Yes, I can, but the OP is about CT magnetics. For an SCR treatise, just visit a semiconductor OEM site. Since I do not produce SCRs, my explanation would just be a verbatim repeat of an OEM explanation. I'd recommend you go straight to the horse's mouth.
If you have a specific question about an SCR, that is not covered in the OEM treatise, I will gladly help you, if I can. BR.
Claude
  • #43
Claude
Saturable Core Reactor. Power magnetics should be right up your alley I'd say. I might add it is closely related to the discussion at hand. Thought you'd see the close relationship. Sorry for the assumption.
  • #44
Well, I've used semiconductor SCRs in my career, more so than saturable reactors, so that is what immediately came to mind.
SCR will now refer to sat core reactor. I was going to mention the SCR concept when replying to you, but for brevity I opted not to. It's worth discussing.
Examine a B-H loop. If we bias the inductor with dc, so that it has a quiescent point at a flux well beneath saturation, it has a permeability to an ac signal with a substantial slope. It's value is mu_inc, the incremental slope of the B-H curve at the dc bias point. The inductance, and thus the reactance, to a small ac signal swing, is determined by mu_inc which sets Linc.
If we increase the dc bias to a point beyond the onset of saturation, the slope to the tangent of the B-H curve is much less than before. Hence the mu value plummets, as does the inductance. Linc & mu_inc are eventually that of air for hard saturation.
That is the point you were making. But there is a difference when dealing with an overdriven CT. We are not biasing the core into saturation, and examining the small-signal inductance and mu. Rather, we are traversing through the entire B-H curve. The inductance is by definition, the flux linkage per unit current, or L = N*phi/I. Although the core saturates, the effective mu & L are much greater than the SCR case. If I get time, I'll make a sketch and attach it. For now, draw the B-H curve, and examine what happens for large signal ac stimulus. The energy stored and recovered is in the area between the B-H curve and the B axis (outside the loop). Of course, the area inside the loop is lost as hysteresis. But both ares increase greatly.
Did I help?
Claude
  • #45
I can't seem to find something I've read on the web before about saturable core reactors. You didn't mention it in your last post. At one point it was explained that an SCR is driven into saturation by the bias winding but it is actually 2 windings. Don't take this word for word because I can't remember it completely and can't find it through google. What was explained, and it made sense at the time, was that one coil saturates for one half of the AC cycle and the other coil for the other half. I recall having to read it twice at the time before it made sense. Right now I can't think of how that would work.
From what I read on wiki in the last couple of hours, the BH curve of the typical SCR is sharper than other types of cores. This is something I did not know. So it goes into saturation quickly compared to a slower transition of typical transformers. It has occurred to me that when an AC current runs through a CT that it is in fact running the core through the entire BH curve with every cycle. In fact, I realized this early on before this discussion got off the ground very far at all. But, it is still my belief that the amount of inductance the relatively small core of a CT offers is not enough to impede the current. If it is, then I have a lot of practical joking to do by ordering up a bunch of surplus toroids (no windings) and install them in some unsuspecting souls breaker box. (Kidding of course) However, something just occurred to me. A while back I was searching on forums.mikeholt.com. Not until now did I recall this:
http://forums.mikeholt.com/showthread.php?t=111133&highlight=phase+short
Read the thread and tell me what you think. Obviously current transformers get disconnected and left in place from time to time. The pic in the above link shows a problem that wasn't really related to current transformers and apparently the people residing in this house didn't have any complaints. So I would assume that these particular CTs didn't drop any noticable voltage on the 'one turn' with opened secondarys. Unrelated to CTs, the pics in that mikeholt thread just make me cringe. I've run into some things that have had melted and burned up wires before, but the near phase to phase short that was about to occur in those pics could have really caused quite the fireball/explosion inside that box. WOW!
  • #46
"The inductance is by definition, the flux linkage per unit current, or L = N*phi/I."
--except that it's not a relevant equation. This equation is applicable when coupling between each loop is unity.
  • #47
Ahh, I don't think so, please recheck your reference. The equation I gave has nothing to do with coupling between 2 loops. It holds for a simple inductor. Self-inductance is what it refers to. That is the most basic definition of inductance. Any EE, e/m fields, or physics reference will affirm it. If not, then just what is the basic definition of L?
Claude
  • #48
Claude
Maybe... How do you define \Phi ?
edit: I should add an example. You have an inductor consisting of a long wire with a single loop and a distance away two loops that are coincident. Obviously the flux through the two loops will be geater. Which flux is called phi?
  • #49
In transformer regardless of VT or CT, the linkage flux between primary and secondary is obtained by difference of primary and secondary's ampere-turn. In voltage and current transformers, the linkage flux is established by linkage EMF. The linkage EMF in VT is made by primary voltage (neglect from primary drop voltage) and in CT is made by secondary drop voltage on CT internal impedance and burden resistance. Indeed, the flux curve work point of CT is changed by load variation but it is fixing in voltage and power transformers if we can neglect the primary voltage drops.
REGARDS
M.S.J
http://electrical-riddles.com
  • #50
REGARDS
M.S.J
Not to confuse mmf with emf.
  • #51
Thank you very much for correction me, my means of "linkage EMF" is the EMF due to linkage MMF.:approve:
  • #52
  • Electrical Engineering
10K
