Currents on a three phase system

In summary, the conversation discusses the possibility of summing L1, L2, and L3 currents at any given moment in time and what value this sum would represent. The participants also discuss the complexities of calculating power usage in a three-phase system and the importance of considering phase shifts and voltage magnitudes. It is noted that simply summing the magnitudes of currents may not accurately reflect the total power usage and that further analysis and understanding is needed to accurately monitor and assess the system.
  • #1
mariano54
21
0
Hi everyone,

is it possible to sum at any given moment in time L1 + L2 + L3, algebrically speaking? If so, what would this value represent?

Thanks
 
Engineering news on Phys.org
  • #2
mariano54 said:
Hi everyone,

is it possible to sum at any given moment in time L1 + L2 + L3, algebrically speaking? If so, what would this value represent?

Thanks
If L1,L2,L3 are currents than their sum will represent neutral current (if there is a neutral conductor in 3- phase system, that current flows through it).
Generally, one third of the phasors sum of all 3 phasors represent zero sequence phasor (in treatment by symmetrical system components)
 
  • #3
Hi, thanks for answering. The neutral current, however, is a vector sum, am I correct? What if I sum L1 + L2 + L3, just the values?
 
  • #4
mariano54 said:
What if I sum L1 + L2 + L3, just the values?
Values must be taken at same instant of time, then the above holds.
 
  • #5
The problem I'm having is this, the documentation of the device I'm monitoring is giving me "L1-N", "L2-N", "L3-N", and all three are positive values. Maybe I'm missing what the "-N" means here. That's why I wanted to know what would I be getting by adding them up. Additionally, the vector sum is also provided as a different value, which is clearly different.
 
  • #6
I'm reading that in order to calculate how much power the system is using you actually use all three phases:

current L1 * voltage L1 +. ... + currentL3 * voltageL3 (the formula is more complex, but I'm interested only on the phases)

so the currents in the single phases are relevant. Logically speaking, if I can use all three phases to calculate how much power the system is using, shouldn't I be able to add them up and say how much current is going into the system and thus used by the system?

Thanks
 
  • #7
mariano54 said:
I'm reading that in order to calculate how much power the system is using you actually use all three phases:

current L1 * voltage L1 +. ... + currentL3 * voltageL3 (the formula is more complex, but I'm interested only on the phases)
Ok
Logically speaking, if I can use all three phases to calculate how much power the system is using, shouldn't I be able to add them up and say how much current is going into the system and thus used by the system?

Thanks
This sound very fishy/wrong to me. Show me calculation you have on mind on certain example.
 
  • #8
zoki85 said:
Ok

This sound very fishy/wrong to me. Show me calculation you have on mind on certain example.

P1 = V1 x I1
P2 = V2 x I2
P3 = V3 x I3

Total power = P1 + P2 + P3

is this formula/approach correct?
 
  • #9
P1 = V1 x I1 x cos φ1
P2 = V2 x I2 x cos φ2
P3 = V3 x I3 x cos φ3

Total power = P1 + P2 + P3

Now, it is correct
 
  • #10
Perfect, thanks.
 
  • #11
zoki85 said:
Values must be taken at same instant of time, then the above holds.

One more thing, regarding this point. What I meant was, what happens if I sum only the current values, without takng into account the phase shift, only the magnitudes.

I mean, even if th system is perfectly balances and the neutral is zero, there's still current going in, right?
 
  • #12
mariano54 said:
One more thing, regarding this point. What I meant was, what happens if I sum only the current values, without takng into account the phase shift, only the magnitudes.
Why would you do that? For a balanced 3-phase system you'll get 3x higher line current and do what with it?

I mean, even if th system is perfectly balances and the neutral is zero, there's still current going in, right?
The phases have currents of equal magnitude. Phase shift between any two is 1200 el.
 
  • #13
The way the currents ( and voltages) are related needs to be looked at as vectors ( a magnitude and an angle) - if you ONLY sum the magnitudes - you can (with a lot of assumptions) estimate the total power used, but this will really tell you nothing about the neutral current, because you can have a "balanced" load with different phase currents - and no neutral current - or this sum could be All Phase 1 - and all of that current is flowing in the neutral. There is just too many things to consider - to be able to use 3 Magnitudes ( scalars ) to tell the whole story.
 
  • #14
I agree this is a complex matter. The point is, I have a professional power distribution meter that's giving me currents on L1, L2 and L3 (all positive) and kWh consumption on L1, L2 and L3. These current values are positive and not identical, so it pushed me to believe that somehow the currents on the single phases could be treated separately.

I mean, if in the end you have kWh for each phase, then you must also have currents on each phase, this is common sense. By looking at the kWh consumption for each phase, L1 is increasing by 3 kWh at each reading, L2 by 1 and L3 by 2. Different kWh, different currents. From my ignorant perspective, this means I can actually monitor the different currents and voltages that are causing this.
 

1. What is a three phase system?

A three phase system is an electrical power distribution system that uses three alternating currents of equal frequency but with a phase shift of 120 degrees between each other. It is commonly used in large scale power generation and distribution.

2. How do currents on a three phase system differ from single phase systems?

In a three phase system, there are three separate currents that are evenly distributed over time. This allows for a more efficient use of power compared to single phase systems where there is only one current. Additionally, three phase systems can deliver higher amounts of power and are more stable.

3. What is the purpose of using a three phase system?

The main purpose of using a three phase system is to efficiently distribute electrical power. It allows for higher power transmission with less energy loss, making it ideal for large industrial and commercial applications.

4. How is the current divided in a three phase system?

In a three phase system, the total current is divided into three separate currents, each flowing through their own phase. The currents have the same magnitude but are out of phase with each other by 120 degrees. This results in a more balanced and efficient distribution of power.

5. What are some common applications of three phase systems?

Three phase systems are commonly used in industrial and commercial settings, such as factories, power plants, and large buildings. They are also used in electric motors, air conditioning units, and other high-powered equipment that require efficient and stable power distribution.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
Replies
2
Views
1K
  • Electrical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
26
Views
2K
  • Electrical Engineering
Replies
4
Views
704
  • Electrical Engineering
3
Replies
77
Views
5K
Replies
13
Views
3K
Replies
35
Views
2K
Replies
13
Views
2K
  • Electrical Engineering
Replies
19
Views
2K
Back
Top