Delta and Wye Elements wired in parallel

AI Thread Summary
Wiring a delta heater in parallel with a wye heater can lead to decreased overall circuit resistance, potentially causing the delta heater to draw more current than intended. There is concern that this configuration may create an imbalance in power distribution, with most current diverting to the delta heater. Proper sizing of power cables is crucial, as undersized cables may exacerbate issues related to higher line amperage. A diagram is recommended to clarify the circuit and resistances involved. Ultimately, careful consideration of the heater elements' ratings and configurations is necessary to ensure safe and efficient operation.
bramdam
Messages
20
Reaction score
0
I manufacture heating elements and a customer wired a delta heater in parallel with a wye heater. They claim that this lowers the overall resistance of the delta thus causing this element to draw more amps than what it was designed for. I disagree and do not see how the heater is eternally wired would make any difference and that each element will draw the appropriate amperage. Line current into the delta heater will be higher than the actual phase current in the heater itself but combining the two types of configurations in parallel should not cause a problem. I am just looking for some re-assurance.

Thanks.
 
Engineering news on Phys.org
Based on your general description I have to agree with you, especially since both elements are restive. Best bet ( as with almost every case) make a diagram for discussion.
 
I will try and dig up the schematic. I do not know the parameters of the wye heater, only the delta heater. But here is the email for which I do not agree. I do believe we undersized a power cable thus leading to the start of all this for we did not account for the line amperage being higher than our phase amperage. I will work on a diagram of some sort.Dave,

This is the problem... When you wire "Delta" and "Y" heat bands in parallel, the delta heat bands show less circuit resistance and the total circuit resistance will decrease causing an increase in total circuit amperage. In-fact, most of the current flow will divert to only the delta heat bands and there will be an imbalance in power distribution between all the heat bands. It is improper to wire delta and Y resistive circuits together in parallel. Please feel free to review this with an electrical engineer from your supplier. We need for you to send new (12 awg) cable assemblies for each of the heating bands that was on the order. I will be at the customer's site on April 7th, and I can exchange all of the cables on your heat bands at that time. This way, we are sure that all of them will be ok when they are wired into the system. With 12 awg wire cables, there shouldn't be any issues going forward (whether they are wired "Y", "delta", or parallel Y/Delta). This would be the fastest and easiest solution.
 
Wait - are you using the same heater elements in each leg? eg. You have a Delta with Element type A and Wye with Element type A? -- then the Delta will draw more than the Wye - but connecting the Wye will not cause the Delta to draw more than the Delta by itself ( there is no "diverting"). Ether way -- the two in parallel will draw more than ether one...the info above is still not entirely clear.
 
Windadct said:
Best bet ( as with almost every case) make a diagram for discussion.
Absolutely. You can draw no conclusions about a circuit until you actually draw it out and specify the resistances involved.
Calculate the voltages across the resistors in the two cases and then what will the resulting currents and power dissipation be?
 
bramdam said:
I manufacture heating elements and a customer wired a delta heater in parallel with a wye heater.
Comparing the Y with the Δ were their individual elements rated differently for voltage, in accord with the respective configuration?
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...