Do I need a feedback card to acquire motor RPM from a VFD?

AI Thread Summary
To obtain RPM feedback from a motor controlled by the DURApulse GS3 series VFD, a feedback card is not strictly necessary, as the VFD provides configurable outputs that can deliver a 0-10V speed signal, which can be converted to RPM. Using MODBUS communication with Labview allows for effective control and monitoring of the motor's performance. The feedback card is primarily used for closed-loop control applications, where precise speed, acceleration, or position feedback is required to minimize error. Depending on the application, the VFD's frequency output may suffice for estimating RPM if the motor's design slip factor is known. Ultimately, the choice of using a feedback card depends on the precision needs of the project.
belae1ka
Messages
13
Reaction score
0
The VFD I plan on using;
DURApulse GS3 series AC drive: https://www.automationdirect.com/static/specs/gs3drives.pdf
Model: GS3-22P0

The feedback card accessory for the VFD: https://www.automationdirect.com/static/specs/gs3fb.pdf

Hi everyone, I would like to know if I need this feedback card to obtain RPM of a motor that is being wired using the VFD specified above. I plan on controlling a 3 phase motor with the program Labview. I will be using MODBUS to communicate between the VFD and Labview.

The end goal of my project is to plot the force of a load cell with respect to an increasing motor RPM so I was wondering how to get the RPM feedback from the motor. What exactly is the main purpose of this feedback card? In what kind of applications would this card be needed?
 
Engineering news on Phys.org
belae1ka said:
What exactly is the main purpose of this feedback card?
You can make a closed loop controller.
The feedback is subtracted from the feed forward signal, which results in a speed ( or acceleration or position ) error.
This error is integrated, increasing or decreasing the torque, until the speed is accurate ( error = 0 ).
A digital controller will give you a speed, that is as accurate as the crystal controlling the clock frequency in your controller ( measured in parts per million ( ppm ) ).
 
belae1ka said:
Hi everyone, I would like to know if I need this feedback card to obtain RPM of a motor that is being wired using the VFD specified above.
No, it comes with multiple configurable inputs and outputs. You can get a 0-10V speed output, which you can translate into RPM.
 
  • Like
Likes belae1ka
Depending on the precision required, If you know the design slip factor of the motor, (based on load, read AMPS) Frequency output of the VFD may be close enough.

Some VFD's offer "conversion" calculations to display "motor RPM" based on similar input.
 
  • Like
Likes belae1ka
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top