The discussion focuses on controlling a heating plug element to maintain temperatures up to 1000°F using a thermostat controller. The user seeks clarity on output options, specifically whether to use DC pulse, relay, or 4-20mA for their application. It is confirmed that the controller can be wired directly to a 110-240VAC source without needing a separate power supply, and that a relay output is necessary for connecting the heating elements. The conversation also touches on the potential use of a PID controller, which may be more complex than required for this project. Overall, the importance of understanding the specific requirements and functionalities of the components is emphasized for effective temperature control.
pedalspikes
Messages
3
Reaction score
0
I'm working on a project were I will be using Heating Plug Element-
http://www.omega.com/ppt/pptsc.asp?ref=CSS_CSH&Nav=head01

I want to be able to control temperatures up to 1000 F using something likes this:
http://www.omega.com/Manuals/manualpdf/M4636.pdf

I would like to be able to control the temperature of the plug heaters so that I am able to set a maximum temperature, which is held for a period of time before shutoff. Nothing overly elaborate. There will be no other electrical components, just the plug heater and the thermostat controller.
I'm not clear on how controllers of this type work. The output for the controllers is either DC Pulse, Relay, or 4-20mA (is up to the buyer). For my described application which output would be the simplest? What additional hardware would I need for what is suggested?
Thanks!
 
Engineering news on Phys.org
The idea of a controller is to maintain its set-point temperature by minimizing the error signal (difference between set-point and measured temp), so you're going to have to have either a thermocouple (TC) or resistive thermal device (RTD) to get the measured temp.

You need to give more detail about what you are wanting to do. By "control temperatures up to 1000 F", do you mean just ramp the temp up to set-point value? And if so, how long do you want to maintain this temp? Sounds like you may need other electronics.

As far as to which type of output to use depends on what exactly you want to do.
 
I would like the temperature to ramp up until it reaches a desired set temperature, where it would remain until manually shut off. An automatic shutoff after x minutes would be nice, but it is not a necessity.

My confusion stems from the description of the temperature control unit.
-Do I need a separate power supply, or can I wire the controller directly to 110Vac?
-The output options allow you to choose a 5-20mA relay option, is SPDT relay built in, or is that something that must be independently connected?
-What is the difference between functionality of a relay output and DC pulse out put? Which is better for my described application?

Sorry for my vague-ness, I'm fairly new to designing parts with electrical components.
 
-No, you don't need an additional power supply. You can wire it directly to a 100vac to 240vac source with the line on terminal 11 and the neutral on terminal 12 (see page 6 of the Omega bulletin).

-The Short Cartridge Heaters can be bought for either 120vac or 240vac operation so you would need to supply that through a relay output as opposed to a dc pulse which would not drive the heater.

For industrial process control instruments, analog 4–20 mA and 10–50 mA current loops are commonly used for analog signaling, with 4 mA representing the lowest end of the range and 20 mA the highest. The key advantages of the current loop are that the accuracy of the signal is not affected by voltage drop in the interconnecting wiring, and that the loop can supply operating power to the device.
(see Current Loop)

edit: Check out how your proportional–integral–derivative controller (PID controller) works. It might be an overkill here. Just sayin'
 
Last edited:
Thanks!
The PID controller is most definitely overkill for what I plan on using it for, but figured I might use it for different applications in the future.

I had a feeling that the heating elements would have to be connected through a relay, rather than the DC pulse.
 
pedalspikes said:
I had a feeling that the heating elements would have to be connected through a relay, rather than the DC pulse.

You could use dc pulses as a input to a Solid State Relay that switches the ac to the heater however. Depending on the wattage of the heater you chose determines at what current rating you would need for one of these:

458px-Solid-state-relays.jpg
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...