Electrical Engineers: Need help with thermostat output options.

AI Thread Summary
The discussion focuses on controlling a heating plug element to maintain temperatures up to 1000°F using a thermostat controller. The user seeks clarity on output options, specifically whether to use DC pulse, relay, or 4-20mA for their application. It is confirmed that the controller can be wired directly to a 110-240VAC source without needing a separate power supply, and that a relay output is necessary for connecting the heating elements. The conversation also touches on the potential use of a PID controller, which may be more complex than required for this project. Overall, the importance of understanding the specific requirements and functionalities of the components is emphasized for effective temperature control.
pedalspikes
Messages
3
Reaction score
0
I'm working on a project were I will be using Heating Plug Element-
http://www.omega.com/ppt/pptsc.asp?ref=CSS_CSH&Nav=head01

I want to be able to control temperatures up to 1000 F using something likes this:
http://www.omega.com/Manuals/manualpdf/M4636.pdf

I would like to be able to control the temperature of the plug heaters so that I am able to set a maximum temperature, which is held for a period of time before shutoff. Nothing overly elaborate. There will be no other electrical components, just the plug heater and the thermostat controller.
I'm not clear on how controllers of this type work. The output for the controllers is either DC Pulse, Relay, or 4-20mA (is up to the buyer). For my described application which output would be the simplest? What additional hardware would I need for what is suggested?
Thanks!
 
Engineering news on Phys.org
The idea of a controller is to maintain its set-point temperature by minimizing the error signal (difference between set-point and measured temp), so you're going to have to have either a thermocouple (TC) or resistive thermal device (RTD) to get the measured temp.

You need to give more detail about what you are wanting to do. By "control temperatures up to 1000 F", do you mean just ramp the temp up to set-point value? And if so, how long do you want to maintain this temp? Sounds like you may need other electronics.

As far as to which type of output to use depends on what exactly you want to do.
 
I would like the temperature to ramp up until it reaches a desired set temperature, where it would remain until manually shut off. An automatic shutoff after x minutes would be nice, but it is not a necessity.

My confusion stems from the description of the temperature control unit.
-Do I need a separate power supply, or can I wire the controller directly to 110Vac?
-The output options allow you to choose a 5-20mA relay option, is SPDT relay built in, or is that something that must be independently connected?
-What is the difference between functionality of a relay output and DC pulse out put? Which is better for my described application?

Sorry for my vague-ness, I'm fairly new to designing parts with electrical components.
 
-No, you don't need an additional power supply. You can wire it directly to a 100vac to 240vac source with the line on terminal 11 and the neutral on terminal 12 (see page 6 of the Omega bulletin).

-The Short Cartridge Heaters can be bought for either 120vac or 240vac operation so you would need to supply that through a relay output as opposed to a dc pulse which would not drive the heater.

For industrial process control instruments, analog 4–20 mA and 10–50 mA current loops are commonly used for analog signaling, with 4 mA representing the lowest end of the range and 20 mA the highest. The key advantages of the current loop are that the accuracy of the signal is not affected by voltage drop in the interconnecting wiring, and that the loop can supply operating power to the device.
(see Current Loop)

edit: Check out how your proportional–integral–derivative controller (PID controller) works. It might be an overkill here. Just sayin'
 
Last edited:
Thanks!
The PID controller is most definitely overkill for what I plan on using it for, but figured I might use it for different applications in the future.

I had a feeling that the heating elements would have to be connected through a relay, rather than the DC pulse.
 
pedalspikes said:
I had a feeling that the heating elements would have to be connected through a relay, rather than the DC pulse.

You could use dc pulses as a input to a Solid State Relay that switches the ac to the heater however. Depending on the wattage of the heater you chose determines at what current rating you would need for one of these:

458px-Solid-state-relays.jpg
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...