tim9000 said:
What I previously was getting at was that, since the Primary current is quite high and there would be a number of turns, then the MMFs are quite high,
Good. There will be large opposing mmf's .
But B in the core is quite low,
You're still speaking of transformer with short circuited secondary? Yes flux will be low.
then I was thinking the impedance of the transformer would still be quite high, and the inuctance would still be quite high
slow down... you take the stairs too many at a time..
wiki has a pretty decent link...
http://en.wikipedia.org/wiki/Transformer
"" impedance of the transformer would still be quite high, and the inuctance would still be quite high ""
Which impedance? Which inductance?
Fluxfrom Pri = Vpri/ [Npri turns*wfreq of supply
Remember that applied voltage divides between primary losses and counter-emf ,
so counter-emf is only that fraction of applied voltage not dropped as primary losses I X (Rp +jXp).
So your Vpri = Vapplied - I X (Rp +jXp) which will be fairly small .
i think the rest of that paragraph is okay though.
So since the Inductance of the TX is L = μ0μrN2Area/Length
That would be X
M, magnetizing inductance,
and μ depends on B which is low meaning μ is quite high,
i don't think that's right.
You've made a false leap . We all want the answer to be easy, and it is but it's several steps to get there not one.
The mind will concatenate words and fool us.
μ is quite high because the core is made from good ferromagnetic material.
http://hyperphysics.phy-astr.gsu.edu/hbase/solids/ferro.html#c5
When ferromagnetic materials are used in applications like an
iron-core solenoid, the relative permeability gives you an idea of the kind of multiplication of the applied magnetic field that can be achieved by having the ferromagnetic core present. So for an ordinary iron core you might expect a magnification of about 200 compared to the magnetic field produced by the solenoid current with just an air core. This statement has exceptions and limits, since you do reach a saturation magnetization of the iron core quickly, as illustrated in the discussion of
hysteresi
What is changing is not permeability and inductance. , but flux and counter-emf; induction..
That leaves primary current at the mercy of winding resistances Rp & Rs, and leakage reactances Xp & Xs.
Those are 'necessary evils' so kept low on purpose.
tim9000 said:
than L is quite high and X = 2wL
L is not changed
then the Icurrent in primary*X is a lot of Vars?
And a lot of watts.
Primary current is high because there's hardly any counter-emf induced to oppose it
so what limits Iprimary ?
Winding resistances and leakage reactances.
Both of those are 'necessary evils', kept low on purpose.
That's why primary current is high.
It's important to work your mental model until it leads you to the right formula.
μ is not truly constant but for first approximations we treat it as constant, refining only when called for.
You're getting there. Study that wiki equivalent circuit.
Visualize that flux inside the core.