Heat exchanger in abandon oil tank

AI Thread Summary
Using an abandoned oil tank as a fluid-to-fluid heat exchanger for HVAC systems poses significant challenges, including legal and environmental concerns regarding underground storage tanks. The tank's design limits its effectiveness as a heat pump source or sink due to its small surface area and closed nature, leading to rapid temperature fluctuations that would render it inefficient. Additionally, the heat transfer to the surrounding ground would result in substantial energy loss. Alternatives like ground source heat pump loops are preferred because they provide greater surface area for heat exchange and maintain a more stable temperature by being buried deeper. Overall, the concept may not be practical or legally permissible.
megachase
Messages
1
Reaction score
0
Here in the NW most homes are or were heated by oil. The biggest cost of switching to gas (as geothermal is very expensive) is decommissioning the old buried oil tank, in many cases up to 675 gal. cap. I was pondering weather the old tank could be filled with a solution and somehow figure out how to get piping into the tank without digging it up and using it as a fluid to fluid heat exchanger for HVAC. Anyone want to run with that ball?
 
Engineering news on Phys.org
I wouldn't want to try to clean that tank. I also wouldn't want to be within a country mile if someone started welding fittings on it without a ton of inert gas.

You may have to check with your state environmental laws, but you may run into an issue with an underground storage tank not being used for it's expected intent. You may find out you can't legally do what you want to do without the hassle you are trying to avoid.

All of my tanks were either next to the house or in my basement. Neither were buried.

Even if you do get by all of that, what would you want to do with it? You would have a rather constant temp relatively cool fluid. If you wanted to heat it you would have to impart that energy to it. You would lose a ton of it in heat transfer to the surrounding ground since you are using an uninsulated steel tank. If you use it, you could possibly use it to cool in the warm weather.
 
The OP wants to use it as a source/sink for a water source heat pump.

Since the tank has a small aspect ratio (not much surface area, lots of volume) and is closed, you won't be able to use it as a heat pump source/sink. All you'll do is heat it up quickly in the summer and render it useless after a couple of hours and freeze it solid after a couple of hours in heating mode in the winter.

Ground source heat pump loops are dug deep for two reasons.
1. There is a lot of surface area to exchange heat with the ground without warming or cooling the ground to much.
2. Whether the system is open or closed, digging it deep will get it below the water table where water can flow past it and help keep it at a constant temperature.
 
Post #3 reflects my understanding...
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...