Heat transfer between double window panes

AI Thread Summary
In designing a vertical farm prototype with low-e glass and an aerogel panel, calculations indicate a heat gain of 0.1233 kWh/(m^2*h) through the glass during peak sunlight in Boulder, Colorado. To estimate heat loss through the aerogel, it's suggested to use R insulation values for each layer and consider the thermal conductivity of the aerogel, which is typically around 0.03 W/(m^2K). Additionally, the solar heat gain coefficient (SHGC) is not applicable for the aerogel, as it primarily pertains to solar radiation. Concerns are raised about the cost-effectiveness of using aerogel compared to traditional double-pane glass, given its limited advantages. For more specific aerogel properties, contacting manufacturers specializing in aerogel technologies is recommended.
zzinfinity
Messages
47
Reaction score
0
I'm designing a vertical farm prototype and I'm trying to do some preliminary calculations to get an idea of how hot my crops are going to get. The basic design consists of a low-e glass (SHGC=.39) in the front and an aerogel panel in back(see attached diagram). I'm calculating for the hottest scenario, south facing glass at noon in July. The design is in Boulder Colorado (Lat~40N) and from what I can tell from tables, I can expect .1233 kWh/(m^2*h) to be gained through the low-e glass during the hottest part of the day. What I'm not sure how to calculate, is how much heat I can expect to loose through the aerogel panel in the back.

Does anyone know of a way to approximate this, or have a link to a site that can point me in the right direction? Can I just treat the aerogel panels like any other insulating material or do I need a SHGC for it? Don't need a high order of accuracy, just trying to approximate max and min temperatures for my cavity.

Thanks!
 

Attachments

  • Design.png
    Design.png
    5.1 KB · Views: 699
Engineering news on Phys.org
Yes, you use the R insulation values of each layer and add them up. You can use manufacturer's info for the specific glass. You can google the R value of aerogel.
 
zzinfinity said:
I'm designing a vertical farm prototype and I'm trying to do some preliminary calculations to get an idea of how hot my crops are going to get. The basic design consists of a low-e glass (SHGC=.39) in the front and an aerogel panel in back(see attached diagram). I'm calculating for the hottest scenario, south facing glass at noon in July. The design is in Boulder Colorado (Lat~40N) and from what I can tell from tables, I can expect .1233 kWh/(m^2*h) to be gained through the low-e glass during the hottest part of the day. What I'm not sure how to calculate, is how much heat I can expect to loose through the aerogel panel in the back.

Does anyone know of a way to approximate this, or have a link to a site that can point me in the right direction? Can I just treat the aerogel panels like any other insulating material or do I need a SHGC for it? Don't need a high order of accuracy, just trying to approximate max and min temperatures for my cavity.

Thanks!
You can get absolute maximum limit of temperature rise by just neglecting inside-to-outside heat transfer through the (aerogel-insulated) panels, and using approximation of 20 W/m2 for non-insulated fraction of greenhouse surface area.
For 75% of area been insulated, and 25% not insulated,
you get
(123.3*0.75)/(20*0.25) degrees temperature rise at maximum.
 
Your thermal conductivity value for aerogel seems rather high. I would expect something around 0.03 ##\frac W {m^2K}## but there is more to it.
First, you need to calculate the thermal conductivity to the ground
Next, I suppose you want to use transparent aerogel in order to pass the solar radiation through. That, would mean that there will be certain amount of radiation emitted by your soil in the infrared region. I do not know the aerogel transparency in the infrared. You would have to find that data and incorporate into your calculations.
From what I know, the conductivity aerogels at around ambient temperature is much lower than the energy transfer via radiation. That's why most commonly used aerogel materials have something added to reduce radiative heat transfer. Either white material (to scatter infrared) or black (to absorb it) but for your application you cannot use either.
The SHGC number is no good, it applies only to solar radiation.
I do have a feeling that using aerogel is not a good idea. It is expensive and does not offer your much advantage of having just one pane or double pane glass window (at much lower price). Besides, there is such thing as too hot for the plants.
 
  • Like
Likes trurle
www.aerogeltechnologies.com

Try contacting those people. Their business is tailoring aerogel properties for special purposes. It was the subject of this recent video

 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top