In a heat exchanger scenario with varying water temperatures and flow rates, the pressure drop is influenced by water properties such as density and viscosity. When properties are held constant, the pressure drop remains stable for a given flow rate. However, using the IAPWS EOS to account for variable properties reveals that higher inlet temperatures lead to lower density and consequently a reduced pressure drop. Additionally, increased volume flow rates correlate with a higher pressure drop, demonstrating a nearly quadratic relationship. Understanding these dynamics is crucial for accurate heat exchanger simulations and design.
rideway
Messages
6
Reaction score
0
Hello everybody

The problem is about a very simple heat exchanger.

One pipe with cold water at the inlet and at some points heat is applied uniformly. Assumed no buoyancy. Wall is smooth and with no slip.

I simulate different a matrix of volume flow rates and inlet water temps. For 5 l/min, water inlet temp varies from 50°C to 150°C; same for 10 l/min and 20 l/min.

My questions are:

1.- If the water properties (density, viscosity, heat capacity, thermal conductivity) are constant, should the pressure drop be constant for a given volume flow rate?
2.- If I simulate water accordingly with variable density and viscosity, should the pressure drop increase with the increase of density or decrease?

I don't know if I explained correctly. Dont hesitate to ask if needed.

Thank you very much in advance!
Regards
 
Engineering news on Phys.org
Anyone can help me? I am still stucked with it.
Thanks!
 
rideway said:
Hello everybody

The problem is about a very simple heat exchanger.

One pipe with cold water at the inlet and at some points heat is applied uniformly. Assumed no buoyancy. Wall is smooth and with no slip.

I simulate different a matrix of volume flow rates and inlet water temps. For 5 l/min, water inlet temp varies from 50°C to 150°C; same for 10 l/min and 20 l/min.

My questions are:

1.- If the water properties (density, viscosity, heat capacity, thermal conductivity) are constant, should the pressure drop be constant for a given volume flow rate?
2.- If I simulate water accordingly with variable density and viscosity, should the pressure drop increase with the increase of density or decrease?

I don't know if I explained correctly. Dont hesitate to ask if needed.

Thank you very much in advance!
Regards
Hi rideway. Fluid flow and pressure drop through pipes and networks of pipes including through pipes making up heat exchangers can be done using the Darcy Weisbach equation. If you're not familiar with that you can look through the Pipe-Flo document I posted here:
https://www.physicsforums.com/showthread.php?t=179830

I did a quick analysis using a program I have to see how pressure drop changes for water over a large range of temperature as well as looking at properties. First, your temperature of 150 C means the water is above atmospheric pressure, so I arbitrarily selected a pressure above the saturation point so it would remain liquid for the analysis. I found the viscosity changed considerably over a large change in temperature but density not so much. The resulting pressure drop difference was relatively small so my conclusion was that viscosity doesn't have a large impact on pressure drop, but that was a relatively superficial analysis assuming subcooled water.

Note that the heat capacity and thermal conductivity of water doesn't enter into the Darcy Weisbach equation so it can't affect pressure drop with the exception that those factors influence the water's change in temperature as it flows through a pipe with heat transfer. Hope that helps.
 
Thank you very much! It really helped a lot

That pdf document is really good, it confirmed what i was thinking.

I realized with my calculations that if I define all properties constant, the pressure drop is not changing. Then I set the water properties as IAPWS EOS (International Association for the Properties of Water and Steam Equations Of State) and as I thought, pressure drop changed for every case:

I post some conclusions that might help.
- The bigger the inlet temperature, smaller the density and smaller the pressure drop. By high volume flow rates up to 500Pa for a 80°C delta in a 2 meter long pipe. The density change was aprox 1%.
- The bigger the volume flow rate, the bigger the pressure drop. This one was quite obvious. It was an almost a quadratic result.

Thank you very much for your help! :)
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
Back
Top