How to choose a fan for open circuit wind tunnel?

AI Thread Summary
Selecting a fan for an open circuit wind tunnel involves matching the system friction loss curve with the fan performance curve to find the operating point. The desired volume flow rate is 5100 cfm with a total pressure difference of -32 WC, which indicates a significant static pressure requirement. Achieving this pressure level is challenging and typically necessitates a fan with at least 35 horsepower. Both axial and centrifugal fans can be considered, but the high static pressure complicates the selection process. Proper fan selection is crucial for efficient wind tunnel operation.
help_pls
Messages
9
Reaction score
1
Hi all,

I am trying to design a open circuit wind tunnel, and I've got to the point where a fan should be selected. However, I am not familiar with fans at all, so I am wondering if you could help me!

My understanding is that the fan selection process is quite similar to the pump selection process; create a system friction loss curve (pressure vs flow rate) and match that curve with the fan performance curve (pressure vs flow rate), and then the intersection point will be the operating point. Is that correct?

So for my wind tunnel, CFD analysis using ansys aim tells me that with a desired volume flow rate of 5100 cfm, the total pressure difference between the inlet and right before the outlet is -8 kPa, or -32 WC. Does that mean that, doesn't matter if it is an axial fan or a centrifugal fan, or if it located upstream or downstream, I just need to look for a fan that can generate 5100 cfm against 32 WC of pressure?

Thank you
 
Engineering news on Phys.org
help_pls said:
Hi all,

I am trying to design a open circuit wind tunnel, and I've got to the point where a fan should be selected. However, I am not familiar with fans at all, so I am wondering if you could help me!

My understanding is that the fan selection process is quite similar to the pump selection process; create a system friction loss curve (pressure vs flow rate) and match that curve with the fan performance curve (pressure vs flow rate), and then the intersection point will be the operating point. Is that correct?

So for my wind tunnel, CFD analysis using ansys aim tells me that with a desired volume flow rate of 5100 cfm, the total pressure difference between the inlet and right before the outlet is -8 kPa, or -32 WC. Does that mean that, doesn't matter if it is an axial fan or a centrifugal fan, or if it located upstream or downstream, I just need to look for a fan that can generate 5100 cfm against 32 WC of pressure?

Thank you
Yes, but 32" is a ton of static pressure. It isn't easy to find a fan for that and will require at least 35hp.
 
  • Like
Likes help_pls
russ_watters said:
Yes, but 32" is a ton of static pressure. It isn't easy to find a fan for that and will require at least 35hp.
Ok, thank you!
 
  • Like
Likes russ_watters
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...