How to power two floors with one inverter?

In summary: No, you don't get a spark and the DMM won't show more than a few mA when connected between the two neutrals.
  • #1
GingerLee
20
0
Hi,

I have two floors with two different energy meters. Both energy meters are supplied electricity from different phases of a 3-phase single neutral electric source. The basic schematic is shown in the attached picture.
xVA1t.jpg


On floor 1, all load is connected through the inverter.

On floor 2, some load is direct while some load through inverter. The load through inverter uses live from 1st floor and neutral from 2nd floor.

Is this okay?
Will it cause the energy meter to show leakage?

Thanks engineers :)
 
Engineering news on Phys.org
  • #2
Hi GingerLee. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

What does the inverter do, exactly?
 
Last edited by a moderator:
  • #3
If the red lines are live and the black ones neutral then there is no connection from the right hand load to the meter 2. Therefore, you wouldn't expect the meter to register anything.
Is the inverter / battery a UPS?
 
  • #4
NascentOxygen said:
What does the inverter do, exactly?
It is a inverter + battery. It is a UPS, used for power backup. In case power fails from main source, the inverter generates AC current from DC battery. When there is no power failure, it just connects load directly to the mains.

sophiecentaur said:
If the red lines are live and the black ones neutral then there is no connection from the right hand load to the meter 2. Therefore, you wouldn't expect the meter to register anything.
Is the inverter / battery a UPS?
Yes, it is a UPS. and yes red is live and black is neutral.

What I wanted to know, is it okay to use the neutral from one energy meter and live from another energy meter (through the UPS). Note that both energy meters are fed from different phases.

In case of no power failure.
load (shown on lower right) is fed from neutral from energy meter#1(EM1), and live from energy meter#2 (EM2). Is this okay? Will this cause EM2 to show leakage because current from EM1 would go through neutral of EM2?

I am worried if this would result in a short circuit, over voltage or increased energy bill (due to leakage reading, yes my energy meter also records leakage).

Thanks again for taking time to respond :)
 
  • #5
GingerLee said:
What I wanted to know, is it okay to use the neutral from one energy meter and live from another energy meter (through the UPS). Note that both energy meters are fed from different phases.

Put a meter between the two neutrals to check but there should be no volts if they are directly off the same three phase transformer (as in the UK and Europe). If you find more than a few mV then you may have to think again. The acid test would be to see if and how the neutral-neutral Volts vary when you switch different loads onto the two phases. (And how the Joule Meter responds, too.
Good luck
 
  • #6
If phases from your transformer secondary are Wye connected with the neutral as shown here:

http://www.federalpacific.com/university/T-Basics/Charts/section-3-scan-9.gif

there should be no problem sharing this neutral with the power meters. But if you're not sure if the neutrals are coming from the same transformer, do the test as sophiecentaur suggest.
 
Last edited by a moderator:
  • #7
Thanks everyone for the replies. I put a digital multi-meter (700V AC) between the two neutral, the voltage was 2-3 volts (it kept changing between 2 and 3). I guess i have to remove the load from the UPS for second floor.

I don't want buy a new UPS for second floor. This would be costly :(

Thanks guys :)
 
  • #8
If you touch the two neutrals together. Do you get a spark? Will your DMM show more than a few mA when connected between the two neutrals.? If no then no worries.
 
  • #9
GingerLee said:
Hi,

I have two floors with two different energy meters. Both energy meters are supplied electricity from different phases of a 3-phase single neutral electric source. The basic schematic is shown in the attached picture.
xVA1t.jpg


On floor 1, all load is connected through the inverter.

On floor 2, some load is direct while some load through inverter. The load through inverter uses live from 1st floor and neutral from 2nd floor.

Is this okay?
Will it cause the energy meter to show leakage?

Thanks engineers :)

Do you pay the energy bill for both meters?
 
  • #10
berkeman said:
Do you pay the energy bill for both meters?

Good man! HaHa

But why not run a second (neutral) line, along with the red one and disconnect load 2 from the other supply completely?
 
  • #11
berkeman said:
Do you pay the energy bill for both meters?
Yes indeed. This place had two meters when I first came here and I let it be like this. The previous owner used to rent the floors to different people. And they quarreled over who uses more electricity so the owner had 2 meters installed.

I called the electricity company helpline to remove 1 meter and they said they would charge me for it. Why pay for removing something?

sophiecentaur said:
If you touch the two neutrals together. Do you get a spark? Will your DMM show more than a few mA when connected between the two neutrals.? If no then no worries.

Good man! HaHa
But why not run a second (neutral) line, along with the red one and disconnect load 2 from the other supply completely?
Great idea. I looked into it but I think I have to call a professional for this. Wiring is inside walls and I don't want to mess with it.

Actually the guy who installed UPS did install a wire for UPS running from 1st to 2nd floor. He just took 1 white wire (for live coming from UPS) and used the neutral coming from meter. I did not know then or I would have had him install extra neutral too.

Forgot to do this. I touched the neutrals , they do not create spark. DMM is not stable, it shows between 0 A to 0.010 A. The current stays 0 but when I switch something on (like ceiling fan), then it goes up for a second, then slowly comes back to 0.

Thanks :)
 
Last edited:
  • #12
GingerLee said:
Actually the guy who installed UPS did install a wire for UPS running from 1st to 2nd floor. He just took 1 white wire (for live coming from UPS) and used the neutral coming from meter. I did not know then or I would have had him install extra neutral too.

That worries me. The practice of 'borrowed neutral' is a poor one and I would question this guy's credentials. You would not be likely to find this happen in the UK, for instance. I should have expected a twin and earth cable (three conductors in a separate sleeve).
 
  • #13
I don't see any protection in this circuit I would expect any RCCDs installed upstream of the meters to trip all the time.
 
  • #14
Jobrag said:
I don't see any protection in this circuit I would expect any RCCDs installed upstream of the meters to trip all the time.
I have RCCD, MCB and Isolator. Just did not show in the circuit to make it simple as it was not relevant to the question I was asking.

sophiecentaur said:
That worries me. The practice of 'borrowed neutral' is a poor one and I would question this guy's credentials. You would not be likely to find this happen in the UK, for instance. I should have expected a twin and earth cable (three conductors in a separate sleeve).

He was sent by the place I bought UPS from. Thanks for the mention of borrowed neutral, I am going to have all wiring checked for this.
 
  • #15
GingerLee said:
I have RCCD, MCB and Isolator. Just did not show in the circuit to make it simple as it was not relevant to the question I was asking.
I, too, had observed that these circuits can't be protected by RCDs. You have just the two meters, and there is an RCCD associated with each of these meters?
 

1. How does an inverter work to power two floors?

An inverter is a device that converts direct current (DC) electricity from a battery or solar panels into alternating current (AC) electricity, which is used to power most household appliances. To power two floors with one inverter, the inverter must have a high enough wattage and be connected to both floors through separate circuits.

2. What is the ideal wattage for an inverter to power two floors?

The ideal wattage for an inverter to power two floors depends on the size and power consumption of the appliances on each floor. As a general rule, it is recommended to have an inverter with a wattage at least 20% higher than the combined wattage of all the appliances on both floors.

3. Can I use a single circuit to power both floors with an inverter?

No, it is not recommended to use a single circuit to power both floors with an inverter. This can cause overload and damage to the inverter, as well as potential safety hazards. It is important to have separate circuits for each floor to ensure proper distribution of electricity.

4. What type of inverter is best for powering two floors?

There are different types of inverters available, such as pure sine wave, modified sine wave, and square wave inverters. For powering two floors, a pure sine wave inverter is recommended as it provides a steady and stable flow of electricity, making it suitable for sensitive electronics and appliances.

5. How can I ensure efficient use of the inverter to power two floors?

To ensure efficient use of the inverter to power two floors, it is important to properly size the inverter, use energy-efficient appliances, and limit the use of high-powered appliances at the same time. It is also recommended to regularly maintain and monitor the inverter to ensure optimal performance.

Similar threads

  • Electrical Engineering
Replies
18
Views
2K
  • Electrical Engineering
Replies
1
Views
268
Replies
47
Views
3K
  • Electrical Engineering
Replies
21
Views
1K
Replies
19
Views
2K
  • Electrical Engineering
Replies
33
Views
565
  • Electrical Engineering
Replies
5
Views
1K
Replies
13
Views
4K
  • Electrical Engineering
3
Replies
77
Views
5K
  • Electrical Engineering
Replies
10
Views
869
Back
Top