How to power two floors with one inverter?

  • Thread starter Thread starter GingerLee
  • Start date Start date
  • Tags Tags
    Inverter Power
Click For Summary

Discussion Overview

The discussion revolves around the feasibility and implications of using a single inverter to power two floors with separate energy meters connected to different phases of a 3-phase electrical system. Participants explore concerns regarding potential leakage readings on energy meters, the safety of using a shared neutral, and the implications of the current wiring setup.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • One participant describes the setup where floor 1 is fully powered by an inverter, while floor 2 has a mix of direct and inverter-powered loads, raising concerns about using a neutral from one energy meter with a live from another.
  • Another participant questions the function of the inverter, clarifying that it is a UPS that provides backup power by converting DC from a battery to AC.
  • Some participants suggest that if the live and neutral are from different phases, there should be no connection affecting the energy meter readings, but they recommend testing for voltage between the neutrals.
  • One participant reports measuring 2-3 volts between the two neutrals, expressing concern about the implications for the inverter setup and potential leakage readings.
  • There are suggestions to run a separate neutral line to avoid complications, but the original poster expresses reluctance due to the cost and complexity of installation.
  • Concerns are raised about the practice of using a "borrowed neutral," with one participant questioning the credentials of the installer who set up the current wiring.
  • Participants discuss the lack of protection in the circuit and the implications for safety, particularly regarding RCCDs and MCBs in relation to the energy meters.

Areas of Agreement / Disagreement

Participants express a range of views on the safety and practicality of the current wiring setup. There is no consensus on whether the existing configuration is safe or advisable, and multiple competing concerns regarding leakage, safety, and installation practices remain unresolved.

Contextual Notes

Participants note the potential for voltage between neutrals and the implications of using a borrowed neutral, which may not be standard practice in some regions. Concerns about the adequacy of circuit protection and the qualifications of the installer are also highlighted.

Who May Find This Useful

This discussion may be useful for individuals dealing with similar electrical setups, particularly those considering the use of inverters in multi-floor buildings with separate energy meters and different phases.

GingerLee
Messages
20
Reaction score
0
Hi,

I have two floors with two different energy meters. Both energy meters are supplied electricity from different phases of a 3-phase single neutral electric source. The basic schematic is shown in the attached picture.
xVA1t.jpg


On floor 1, all load is connected through the inverter.

On floor 2, some load is direct while some load through inverter. The load through inverter uses live from 1st floor and neutral from 2nd floor.

Is this okay?
Will it cause the energy meter to show leakage?

Thanks engineers :)
 
Engineering news on Phys.org
Hi GingerLee. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

What does the inverter do, exactly?
 
Last edited by a moderator:
If the red lines are live and the black ones neutral then there is no connection from the right hand load to the meter 2. Therefore, you wouldn't expect the meter to register anything.
Is the inverter / battery a UPS?
 
NascentOxygen said:
What does the inverter do, exactly?
It is a inverter + battery. It is a UPS, used for power backup. In case power fails from main source, the inverter generates AC current from DC battery. When there is no power failure, it just connects load directly to the mains.

sophiecentaur said:
If the red lines are live and the black ones neutral then there is no connection from the right hand load to the meter 2. Therefore, you wouldn't expect the meter to register anything.
Is the inverter / battery a UPS?
Yes, it is a UPS. and yes red is live and black is neutral.

What I wanted to know, is it okay to use the neutral from one energy meter and live from another energy meter (through the UPS). Note that both energy meters are fed from different phases.

In case of no power failure.
load (shown on lower right) is fed from neutral from energy meter#1(EM1), and live from energy meter#2 (EM2). Is this okay? Will this cause EM2 to show leakage because current from EM1 would go through neutral of EM2?

I am worried if this would result in a short circuit, over voltage or increased energy bill (due to leakage reading, yes my energy meter also records leakage).

Thanks again for taking time to respond :)
 
GingerLee said:
What I wanted to know, is it okay to use the neutral from one energy meter and live from another energy meter (through the UPS). Note that both energy meters are fed from different phases.

Put a meter between the two neutrals to check but there should be no volts if they are directly off the same three phase transformer (as in the UK and Europe). If you find more than a few mV then you may have to think again. The acid test would be to see if and how the neutral-neutral Volts vary when you switch different loads onto the two phases. (And how the Joule Meter responds, too.
Good luck
 
If phases from your transformer secondary are Wye connected with the neutral as shown here:

http://www.federalpacific.com/university/T-Basics/Charts/section-3-scan-9.gif

there should be no problem sharing this neutral with the power meters. But if you're not sure if the neutrals are coming from the same transformer, do the test as sophiecentaur suggest.
 
Last edited by a moderator:
Thanks everyone for the replies. I put a digital multi-meter (700V AC) between the two neutral, the voltage was 2-3 volts (it kept changing between 2 and 3). I guess i have to remove the load from the UPS for second floor.

I don't want buy a new UPS for second floor. This would be costly :(

Thanks guys :)
 
If you touch the two neutrals together. Do you get a spark? Will your DMM show more than a few mA when connected between the two neutrals.? If no then no worries.
 
GingerLee said:
Hi,

I have two floors with two different energy meters. Both energy meters are supplied electricity from different phases of a 3-phase single neutral electric source. The basic schematic is shown in the attached picture.
xVA1t.jpg


On floor 1, all load is connected through the inverter.

On floor 2, some load is direct while some load through inverter. The load through inverter uses live from 1st floor and neutral from 2nd floor.

Is this okay?
Will it cause the energy meter to show leakage?

Thanks engineers :)

Do you pay the energy bill for both meters?
 
  • #10
berkeman said:
Do you pay the energy bill for both meters?

Good man! HaHa

But why not run a second (neutral) line, along with the red one and disconnect load 2 from the other supply completely?
 
  • #11
berkeman said:
Do you pay the energy bill for both meters?
Yes indeed. This place had two meters when I first came here and I let it be like this. The previous owner used to rent the floors to different people. And they quarreled over who uses more electricity so the owner had 2 meters installed.

I called the electricity company helpline to remove 1 meter and they said they would charge me for it. Why pay for removing something?

sophiecentaur said:
If you touch the two neutrals together. Do you get a spark? Will your DMM show more than a few mA when connected between the two neutrals.? If no then no worries.

Good man! HaHa
But why not run a second (neutral) line, along with the red one and disconnect load 2 from the other supply completely?
Great idea. I looked into it but I think I have to call a professional for this. Wiring is inside walls and I don't want to mess with it.

Actually the guy who installed UPS did install a wire for UPS running from 1st to 2nd floor. He just took 1 white wire (for live coming from UPS) and used the neutral coming from meter. I did not know then or I would have had him install extra neutral too.

Forgot to do this. I touched the neutrals , they do not create spark. DMM is not stable, it shows between 0 A to 0.010 A. The current stays 0 but when I switch something on (like ceiling fan), then it goes up for a second, then slowly comes back to 0.

Thanks :)
 
Last edited:
  • #12
GingerLee said:
Actually the guy who installed UPS did install a wire for UPS running from 1st to 2nd floor. He just took 1 white wire (for live coming from UPS) and used the neutral coming from meter. I did not know then or I would have had him install extra neutral too.

That worries me. The practice of 'borrowed neutral' is a poor one and I would question this guy's credentials. You would not be likely to find this happen in the UK, for instance. I should have expected a twin and earth cable (three conductors in a separate sleeve).
 
  • #13
I don't see any protection in this circuit I would expect any RCCDs installed upstream of the meters to trip all the time.
 
  • #14
Jobrag said:
I don't see any protection in this circuit I would expect any RCCDs installed upstream of the meters to trip all the time.
I have RCCD, MCB and Isolator. Just did not show in the circuit to make it simple as it was not relevant to the question I was asking.

sophiecentaur said:
That worries me. The practice of 'borrowed neutral' is a poor one and I would question this guy's credentials. You would not be likely to find this happen in the UK, for instance. I should have expected a twin and earth cable (three conductors in a separate sleeve).

He was sent by the place I bought UPS from. Thanks for the mention of borrowed neutral, I am going to have all wiring checked for this.
 
  • #15
GingerLee said:
I have RCCD, MCB and Isolator. Just did not show in the circuit to make it simple as it was not relevant to the question I was asking.
I, too, had observed that these circuits can't be protected by RCDs. You have just the two meters, and there is an RCCD associated with each of these meters?
 

Similar threads

Replies
9
Views
2K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 47 ·
2
Replies
47
Views
5K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
15
Views
1K
  • · Replies 21 ·
Replies
21
Views
3K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 1 ·
Replies
1
Views
1K