Is it OK to use 220V Solenoid Valve in a 230 V Environment

  • Thread starter Thread starter Green Light
  • Start date Start date
  • Tags Tags
    Solenoid Valve
AI Thread Summary
Using a 220V solenoid valve in a 230V environment is generally acceptable, as domestic power supplies can vary by up to 5%. While the valve will function at 230V, operating at this voltage may reduce its lifespan due to increased heat. It's advisable to source a solenoid rated for 230V or 240V to ensure compatibility with local voltage standards. Many regions, including the UK, have transitioned from a nominal 240V to a 230V specification, but actual voltages may still hover around 240V. Overall, components rated between 220VAC and 240VAC should operate effectively within the 230VAC framework.
Green Light
Messages
4
Reaction score
0
I would like to know whether it is ok to use 220V Solenoid Valve in a 230V Environment.

This is the Valve I am taking about.
31pv5GvcxjL.jpg


This is the Circuit I am going to make with this.
http://www.electroschematics.com/6161/power-switch-with-infrared-proximity-sensor/

Thanks in Advance :)
 
Engineering news on Phys.org
The simple answer is yes, it will work.
Domestic supplies are designed to vary by up to 5%. If rated at 220V it should work happily at 231V. The problem may be lifetime since it will run slightly hotter at 230V than 220V. Domestic rated solenoid valves like that pictured have a limited lifetime. The solenoid part is designed to be replaced as required.
 
  • Like
Likes 1 person
Baluncore said:
The simple answer is yes, it will work.
Domestic supplies are designed to vary by up to 5%. If rated at 220V it should work happily at 231V. The problem may be lifetime since it will run slightly hotter at 230V than 220V. Domestic rated solenoid valves like that pictured have a limited lifetime. The solenoid part is designed to be replaced as required.

Very Helpful,Thanks a Lot Bro :)
 
Depending on your location the 230v Environment maybe misguided figure. Here in the UK we had a 240v set-up for many years but to conform with EU legislation this was changed to 230v. The power we use is still a majority 240v as the measured average voltage rarely meets the 230v figure in favour of the 240v.

This will as above have a life shortening effect on the coils expected lifespan - you would be better sourcing a 240v/230v coil as this will fall within the tolerances of the solenoid - you could always check with tech' of the manufacturers as most are wise to our actual voltage and theoretical voltage.
 
In your circuit, the S201S02 will switch up to 400V (i.e. 280V AC) according to the data sheet.

The best solution would be to buy the solenoid valve from a supplier in your own country, so you get one that is designed to work with your country's electricity supply.
 
World standards are gradually being harmonised.
AC supply voltages in the range 220V to 240V are moving to the global 230V specification.
Sometime during this process, the voltage actually provided may move closer to 230V.

The 230V specification is +/– 5% with up to 5% more lost due to a customers resistive line loss.
This allows supplies between 218.5V and 241.5V to be called 230V.

I once had 240V. For over three years now the supplier has called it 230V.
But my meters still measure it as 240V.

Anything in the range 220VAC to 240VAC should work OK under the 230VAC specification.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top