Is the power delivered by 1 no. of 3 phase system the same as 3 no. of 1-phase system?

  • Thread starter Thread starter Jasper12
  • Start date Start date
Click For Summary
SUMMARY

The power delivered by one three-phase system is not necessarily equal to the power delivered by three single-phase systems, even when assuming the same voltage and current ratings. The actual power delivered depends on the configuration of the systems, particularly in high-leg delta configurations where line-to-neutral voltages differ. In balanced systems, a three-phase system can deliver three times the power of a single-phase system, but this is contingent on the specific connections and load characteristics. For example, in North America, the high-leg delta configuration complicates this equivalence due to unequal line-to-neutral voltages.

PREREQUISITES
  • Understanding of three-phase power systems
  • Knowledge of single-phase power characteristics
  • Familiarity with electrical circuit schematics
  • Basic principles of power calculations in AC circuits
NEXT STEPS
  • Research the differences between balanced and unbalanced three-phase systems
  • Learn about high-leg delta configurations and their implications on power delivery
  • Study the equations for power in single-phase and three-phase systems
  • Explore the impact of load characteristics on power delivery in AC circuits
USEFUL FOR

Electrical engineers, power system designers, and technicians involved in the installation and maintenance of three-phase and single-phase electrical systems.

Jasper12
Messages
2
Reaction score
0
is the power delivered by 1 no. of 3 phase system equal to the power delivered by 3 nos. of 1 phase system? Assuming same voltages and amps ratings
 
Last edited by a moderator:
Engineering news on Phys.org
Welcome to PF. This looks like homework but either way should be pretty easy for you to answer. Just look up and compare the equations for power for each case. Let us know what you find.
 
  • Like
Likes   Reactions: phinds
Welcome to PF.

Jasper12 said:
is the power delivered by 1 no. of 3 phase system equal to the power delivered by 3 nos. of 1 phase system? Assuming same voltages and amps ratings
Sorry, what does the abbreviation "no." stand for in your post? Thanks.
 
  • Like
Likes   Reactions: DaveE
berkeman said:
Welcome to PF.


Sorry, what does the abbreviation "no." stand for in your post? Thanks.
I'm assuming if you replace the word "no" with "set(s)", the question will make sense.
 
no. = number , thks
 
Ok, so 20 hours later you haven't been able to google and figure this out? FYI, Physics Forums is not google and is not a chat-bot. We're a forum for learning physics/science from subject matter experts. So you need to put some effort into learning in order to take advantage of what we can offer. At this point you're 21 hours into a problem that should have taken you 30 seconds to solve based on the approach I gave you in my first reply. Our goal here is to help you fix that deficiency. Please make an effort to do so.
 
  • Like
Likes   Reactions: berkeman
Jasper12 said:
is the power delivered by 1 no. of 3 phase system equal to the power delivered by 3 nos. of 1 phase system? Assuming same voltages and amps ratings
That all depends on how they are connected, and to what. It's not just "volts" and "amps", there are network and phase considerations. Please provide a more detailed description of the circuits, bonus points for a schematic!
 
Last edited:
"Same Voltages" is the tricky part of this question. If your single-phase supply is 120 VAC (L-N) and your 3-Phase supply is 120 VAC (L-N) [A.K.A. '208'], then the answer is 'yes.' 120*I : 3*120*I = 208*sqrt(3)*I.
 
  • #10
A three-phase system can serve as three single-phase systems and it can be said a three-phase system can deliver three times as much power as a single-phase system.

For high-leg delta three-phase systems this can not be said.
 
  • #11
Gavran said:
A three-phase system can serve as three single-phase systems and it can be said a three-phase system can deliver three times as much power as a single-phase system.

For high-leg delta three-phase systems this can not be said.
Care to expand on any of that?
 
  • Like
Likes   Reactions: Tom.G
  • #12
In Europe when delivering 3 phase power to the panelboard there is the same line-to-neutral voltage on all three phases and that means all three phases together can deliver three times as much power as one of them. In North America when delivering 3 phase power using a high-leg delta there is not the same line-to-neutral voltage on all three phases and that means the power delivered by a single-phase can not be the same for all three phases and all three phases together can not deliver three times as much power as any of them.
 
  • #13
In a single-phase machine with sinusoidal EMF instantaneous power is

e*i = EI[cosγ - cos (2ωt + γ)]

The first term represents constant power, the second term is a 2ω oscillatory torque/power superimposed on the average.

When increasing to two- or three-phase balanced machines, this secondary oscillatory term is cancelled out and the power becomes

NphEIcosγ = (1/ω)[Σ(eaia)] for a =1 -> Nph

I'll leave it up to you to find limits on e & i in different phases to determine actual power differences within a similar sized machine.
 
  • #14
Gavran said:
In North America when delivering 3 phase power using a high-leg delta there is not the same line-to-neutral voltage on all three phases and that means the power delivered by a single-phase can not be the same for all three phases and all three phases together can not deliver three times as much power as any of them.

There is nothing that says a single phase load has to be from hot to neutral. There are times when a single phase load is placed between the 'wild' leg (referred to as the B leg) and one of the others (A or C). It's not prohibited by code.
-
Also, there are lighting circuits that run at 277 volts in the USA. I don't get into 480 volt systems but I believe that voltage comes from the wild leg on high leg delta on 480 systems. It can also come from 480 Y leg to neutral. I was told 277 circuits exist to utilize an otherwise lightly load B leg.
-
Edit. I thought about this for a bit, the math doesn't work out to have 277 on 480 delta. It must be line to neutral on 480 wye.
 
Last edited:
  • #15
There is an article (https://en.wikipedia.org/wiki/Polyphase_system) and there is an introduction in the article and there is a sentence in the introduction which claims that compared to a single-phase, two-wire system, a three-phase three-wire system transmits three times as much power for the same conductor size and voltage.
 
  • #16
Gavran said:
the same conductor size
Yes, but you have more of them, so it's not the same amount of copper.
 
  • #17
Any time conductors can be shared and opposing currents are involved we can reduce the size of the wire and save copper. Edison's original DC system did the same thing.
 
  • Like
Likes   Reactions: DaveE

Similar threads

  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 27 ·
Replies
27
Views
833
  • · Replies 5 ·
Replies
5
Views
3K