Is there a significant pressure drop/loss here?

  • Thread starter Thread starter tectactoe
  • Start date Start date
  • Tags Tags
    Pressure
AI Thread Summary
The discussion centers on the pressure drop in a natural gas system flowing to a water heater, with a regulator set at 9 inWC and a mass flow meter causing a loss of about 3 inWC. The user is concerned about potential pressure loss through an 8-foot, 3/4" diameter convoluted metal hose, which could significantly affect the water heater's operation if the pressure drops below 4.5 inWC. Calculations suggest that the pressure drop through a rigid tube would be minimal, around 1/4 inWC, but convoluted hoses can increase this loss substantially, potentially exceeding the operational requirements of the heater. Suggestions include installing a pressure gauge at the hose's end for more accurate measurements, as the accuracy of the current flow meter is in question. Overall, the pressure drop's significance depends on the hose type and the accuracy of the measuring equipment used.
tectactoe
Messages
38
Reaction score
0
I've got natural gas flowing to a chamber with a regulator set at 9 inWC. The gas then goes through a mass flow meter with a 1/4" diameter hole, which causes a pressure loss of about 3 inWC (to verify this, I have another pressure gauge after the flow meter which accurately reads 6 inWC... After that gauge, it goes through a gas tube with quick-connects directly into a water heater. The tube is hefty, some kind of semi-rigid metal (not sure of the kind, can look it up) and the tube has a diameter of 3/4", and is about 8 feet long with two bends (90 degrees, but not sharp).

My question is - would this pipe cause significant pressure loss? The water heater needs at least 4.5 inWC to operate. I wouldn't imaging this tube casing a 1.5 inWC loss, but I could be wrong. Any insight? Thanks.
 
Engineering news on Phys.org
This is easy to compute.

What is your flow rate? What is the wall thickness of the 3/4" tube?
 
well, I think therein lies (one of) the problem(s)... the flow meter is giving us numbers, but we're not sure if they're correct. so we really don't know what the flow rate is.
 
My calculation for flow through an orifice gives about 2 SCFM. Problem is your measurements aren't very accurate so that's just a ball park guess. But it's probably accurate enough to answer your question about the pressure drop through the 8 foot of tube. If it's tube and not convoluted metal hose, then the pressure drop shouldn't be more than about 1/4 inWC. But if it's convoluted metal hose, it could be much higher and pressure could drop below 4.5 inWC. Convoluted hose has an equivalent length that's a function of the ID, number of convolutes, depth of convolutes, number of convolutes per inch, etc... but in general for hose that small, pressure drop is about 10 times higher than for tube of the same diameter (very roughly).
 
Ah, I see... the hose is, in fact, convoluted... Next time I am over in the lab, I will check to see the brand/type so I can give a more accurate description. It's nominal size is 3/4"... I'm not sure what the actual ID/OD measurements are, but the OD definitely looks < 1".

Perhaps it's worth it to put a pressure gauge at the end of the hose, even though that might be a pain in the butt, calculations with a convoluted hose seem like they have too many variables that could make your answers inaccurate.
 
I will preface my response by saying that I am not an ME or a physicist. I am a Master Plumbing, Heating, and Air Conditioning contractor. My son visits this forum frequently and we were discussing this topic.

I do not understand your need to know the velocity of gas flow to the water heater. Way beyond my education. All I can comment on is the actual application.

There is no appreciable pressure drop between the gas valve and the orfice. If you are interested academically, then it is possible to install a gauge in the orfice into the orfice tapping. However, from a purely combustion standpoint, the pressure drop is not important.

The supply regulator at the supply point is adjustable, but only as far as the reliability of the measuring equipment that the installer has available. The most reliable that I am aware of is in the +/-.03 " w.c.

Is this water heater a boiler or a commercial water heater application?
 
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'd like to create a thread with links to 3-D Printer resources, including printers and software package suggestions. My motivations are selfish, as I have a 3-D printed project that I'm working on, and I'd like to buy a simple printer and use low cost software to make the first prototype. There are some previous threads about 3-D printing like this: https://www.physicsforums.com/threads/are-3d-printers-easy-to-use-yet.917489/ but none that address the overall topic (unless I've missed...
Back
Top