Load Flow Order of Jacobian Matrix Power System

AI Thread Summary
The discussion centers on the order of the Jacobian Matrix in the Newton-Raphson Method for load flow studies, specifically questioning the formula used in a textbook example. The correct order is suggested to be N + Np - 1, where N is the total number of buses and Np is the number of P-Q buses. For a system with 40 buses, 9 P-V buses, and 1 slack bus, the order is calculated as 69 x 69. However, there is confusion regarding the treatment of the slack bus in the formula, with some participants believing it should be included. Ultimately, the consensus leans towards the book's answer being incorrect, highlighting the importance of accurately defining bus types in calculations.
jaus tail
Messages
613
Reaction score
48
I'm studying Newton Raphson Method in Load Flow Studies. Book has defined Jacobian Matrix and it's order as: N + Np - 1
N = Total Number of Buses
Np = Number of P-Q Buses

But in solved example they've used some other formula. I'm not sure if it's right.
upload_2017-12-29_17-59-28.png

Shouldn't order be: N + Np - 1
N = 40
Np = number of P-Q buses = (total number of buses) - (number of P-V buses) - slack bus = 40 - 9 - 1 = 30
So order = N + Np - 1 = 40 + 30 - 1 = 69
Order = 69 X 69
But none of the option is this.
Why have they ignored slack bus in the formula?
 

Attachments

  • upload_2017-12-29_17-59-28.png
    upload_2017-12-29_17-59-28.png
    7.2 KB · Views: 5,265
Engineering news on Phys.org
It has been a long time since I did this, but I think you are correct 69x69.
 
So I guess book answer is wrong. Thanks.
 
slack bus is also voltage controlled bus, so the book is correct
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...