Measuring the gas temperature inside a vessel on the outside of the vessel

AI Thread Summary
To measure the gas temperature of SF6 inside a vessel without inserting a probe, clamping a temperature probe to the vessel's exterior can provide a realistic reading, assuming the gas and vessel are in thermal equilibrium. The temperature of the tank should match that of the gas, but factors like wall conductivity and environmental conditions may affect accuracy. It's advisable to measure temperature at multiple points and average the readings, while also considering the impact of any coatings on the vessel. If the gas is constantly entering and exiting the tank, this method may not yield reliable results due to insufficient time for temperature equalization. Careful attention to the probe's attachment and the acceptable variance in density calculations is crucial for accurate measurements.
Sierra1934
Messages
1
Reaction score
0
Hello,

I got a pratical problem; I want to know the gas temperature of SF6 gas inside a vessel. I can't insert a temperature probe to measure the temp. What i can do is clamp a temp. probe to the ouside of the vessel. Does this gives me a realistic reading, bare in mind the wetter conditions, sun shine ect...? I need the temperature to measure the density of the gas, i do know the gas and pressure.

Thanks in advance
 
Science news on Phys.org
In equilibrium the temperature of the tank must equal the temperature of the gas - since the gas in contact with the walls will heat or cool to the same temperature.
Dependign on how conductive thewalls are(assume it's a metal tank?) you might have to measure the temperature at a few places and average them. You might also have to remove any paint or coating when you apply the thermometers.

If the tank is a part of a process and new gas is entering and exiting all the time then this won't work as it won't have time to reach equalise.
 
To do it with that method, you need to look at two things:

1) Define how much variance you can accept in your density calculation. You will already have some due to instrumentation. However, the method of application of the thermocouple and the length of time you average out the temperature readings will all contribute to that variance.

2) You need to pay very particular attention to how the TC or whatever you use, is adhered to the vessel. You can induce quite a bit of error from the junction interface alone.
 
I was watching a Khan Academy video on entropy called: Reconciling thermodynamic and state definitions of entropy. So in the video it says: Let's say I have a container. And in that container, I have gas particles and they're bouncing around like gas particles tend to do, creating some pressure on the container of a certain volume. And let's say I have n particles. Now, each of these particles could be in x different states. Now, if each of them can be in x different states, how many total...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Back
Top