Motor Reversal and Noisy: Troubleshooting Tips

Click For Summary

Discussion Overview

The discussion revolves around troubleshooting a 3-phase motor that is running in reverse and producing noise after being replaced. Participants explore wiring configurations, phase connections, and potential issues related to motor types and starting methods.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant notes that the motor runs backwards and is noisy after being wired similarly to the old motor, suggesting a potential wiring issue.
  • Another participant proposes that switching two phases could reverse the direction of rotation.
  • A different participant recalls that incorrect color wiring could lead to the observed problems, indicating a possible mix-up in phase connections.
  • One participant requests more information from the motor data plate, mentioning that a six-lead motor could be configured for various starting methods, including Star Delta or part winding starts.
  • A later reply corrects the previous statement about contactor requirements for Star Delta starting, while expressing doubt about the motor type based on the measured resistance values.

Areas of Agreement / Disagreement

Participants express differing views on the cause of the motor's issues, with some suggesting wiring changes while others focus on the motor's configuration and type. No consensus is reached regarding the exact solution or cause of the problem.

Contextual Notes

Participants mention specific wiring colors and configurations, but there is uncertainty regarding the correct connections and the implications of the measured resistance values. The discussion also highlights the need for additional information from the motor data plate to clarify the motor type.

wolram
Gold Member
Dearly Missed
Messages
4,411
Reaction score
551
I have just replaced an inverter driven 3ph motor and wired it the same as the old one, it runs (cogs) backwards and is noisy.

The motor is 230 v 3ph, it has 6 wires, yellow, black, white, violet, blue and brown.
testing with ohm meter i have 45 ohms between yellow- black, white-violet
and blue- brown.
so i connected as yellow- white, violet- brown, blue- black, this should give me a delta circuit, testing on volts the readings are equal between the three terminals, what is wrong?
 
Engineering news on Phys.org
I think all you need to do is switch two phases to reverse the direction of rotation.

Regards
 
I havn't played with one of those since school.
IIRC getting the colors backward will cause problems like that. I think the high side colors are black, violet, and blue. Since you seem to be using yellow, white, and blue then running backward and cogging sounds about right.

School was a really long time ago
 
Motor data plate

Please supply more data plate information. In most industrial applications a six lead three phase motor is one of the following:
1.) Star Delta start (two or three contactors needed depending if it is open or closed transistion)
2.) Part winding start (two contactors needed)
3.) Two speed motor (three contactors needed)
 
Mistake

For a Star Delta start you need three contactors for open transition and four contactors for closed transistion. While I doubt you have this type of motor because of the ohms you measured it could be a two speed motor.:frown:
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 4 ·
Replies
4
Views
28K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 4 ·
Replies
4
Views
17K
  • · Replies 3 ·
Replies
3
Views
6K
  • · Replies 24 ·
Replies
24
Views
5K
  • · Replies 3 ·
Replies
3
Views
12K
  • · Replies 50 ·
2
Replies
50
Views
9K
  • · Replies 62 ·
3
Replies
62
Views
13K
  • Sticky
  • · Replies 705 ·
24
Replies
705
Views
123K