Motor Reversal and Noisy: Troubleshooting Tips

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
4 replies · 4K views
wolram
Gold Member
Dearly Missed
Messages
4,411
Reaction score
551
I have just replaced an inverter driven 3ph motor and wired it the same as the old one, it runs (cogs) backwards and is noisy.

The motor is 230 v 3ph, it has 6 wires, yellow, black, white, violet, blue and brown.
testing with ohm meter i have 45 ohms between yellow- black, white-violet
and blue- brown.
so i connected as yellow- white, violet- brown, blue- black, this should give me a delta circuit, testing on volts the readings are equal between the three terminals, what is wrong?
 
Engineering news on Phys.org
I think all you need to do is switch two phases to reverse the direction of rotation.

Regards
 
I havn't played with one of those since school.
IIRC getting the colors backward will cause problems like that. I think the high side colors are black, violet, and blue. Since you seem to be using yellow, white, and blue then running backward and cogging sounds about right.

School was a really long time ago
 
Motor data plate

Please supply more data plate information. In most industrial applications a six lead three phase motor is one of the following:
1.) Star Delta start (two or three contactors needed depending if it is open or closed transistion)
2.) Part winding start (two contactors needed)
3.) Two speed motor (three contactors needed)
 
Mistake

For a Star Delta start you need three contactors for open transition and four contactors for closed transistion. While I doubt you have this type of motor because of the ohms you measured it could be a two speed motor.:frown: