Measuring MVARs in the Field: EMS Systems Explained

AI Thread Summary
MVARs are measured in the field by utilizing line current to derive VA, and with the power factor, watts or Kvars can be calculated. Modern meters equipped with loop sensors can detect the phase lag between voltage and current, enabling accurate calculations of watts and Vars using the relationships defined by trigonometric functions. The discussion highlights the use of analog methods to measure three-phase quantities, emphasizing the significance of phase shifts in calculating Vars. For balanced systems, the 90-degree phase shift between voltage and current is crucial for accurate MVAR measurement. Overall, advancements in metering technology have simplified the measurement of MVARs in EMS systems.
traijan
Messages
15
Reaction score
0
How are MVARs actually measured in the field? How do EMS systems know the difference between MW and MVARS as opposed to an absolute value of MVA? Thanks!
 
Engineering news on Phys.org
traijan said:
How are MVARs actually measured in the field? How do EMS systems know the difference between MW and MVARS as opposed to an absolute value of MVA? Thanks!

Since watts, Vars and VA are all related, if you measure your actual line current, you can then get your VA.

If you then have your power factor, you can get easily find your watts or Kvars from there.

Or if you have two pieces from your triangle, like watts and Kvars, you can easily calculate VA and power factor from there.

Today's meter's calculate this stuff easily with their "loop" sensors. I believe the loop sensors (magnetic field sensors) can see the lag between voltage and current kinda like a oscilliscope, once you have that, you pretty much have it all.
 
Watts = VICos(Θ)
Vars = VISin(Θ)
and sin is just cos shifted by 90 degrees...

The analog ones I'm accustomed to pick from among the three-phase quantities available convenient ones to measure.
For example - draw your individual phasors
notice that with everything balanced and unity power factor, Voltage between phases A and C is 90 degrees out of phase with phase B current.

Aha ! there's the 90 degrees phase shift we need to calculate Vars.
An analog multiplier IC with inputs of Va-c and Ib will produce a signal that can be wired straight to a DC voltmeter having scale calibrated in Vars. It should be a zero-in-the-center type meter.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...