Need some opinions on my experiment

AI Thread Summary
The wind tunnel test revealed that the smaller radiator (radiator 1) dissipated more heat than the larger radiator (radiator 2), despite the latter having nearly double the volume and area. Initially, the larger radiator's performance was misjudged due to incorrect fan settings affecting air speed during the first experiment. After conducting the test multiple times, it was confirmed that radiator 1 had a lower outlet temperature compared to radiator 2. The discussion highlighted the importance of flow rates, pressure drops, and potential filling issues in the larger radiator, which may have limited its cooling efficiency. Further analysis of tube dimensions and heat transfer coefficients was suggested to understand the discrepancies better.
knight92
Messages
100
Reaction score
0
I carried out a wind tunnel test on two radiators. Radiator 1 is a small radiator and radiator 2 is a bigger radiator with nearly twice as much volume and area as radiator 1.

Flow rate going into radiator 1 is 1.2L/min
Flow rate going into radiator 2 is 1.5L/min

the problem is radiator 1 dissipated more heat than radiator 2. Considering the larger area of radiator 2 I would have thought it would dissipate more heat, so the water entering at 90 degrees Celsius should exit at a lower temperature in radiator 2 at say a air speed of 8m/s but it doesnt.

My conclusion is that the radiator 2 did not get filled up completely due to the small flow rate. Can you guys input your opinions on why this might have happened ?

other than thinking the radiator wasnt getting filled up completely, I can't really figure out for the life of me why it would not cool the water more than the smaller radiator 1.

thanks
 
Engineering news on Phys.org
knight92 said:
I carried out a wind tunnel test on two radiators. Radiator 1 is a small radiator and radiator 2 is a bigger radiator with nearly twice as much volume and area as radiator 1.

Flow rate going into radiator 1 is 1.2L/min
Flow rate going into radiator 2 is 1.5L/min

the problem is radiator 1 dissipated more heat than radiator 2. Considering the larger area of radiator 2 I would have thought it would dissipate more heat, so the water entering at 90 degrees Celsius should exit at a lower temperature in radiator 2 at say a air speed of 8m/s but it doesnt.

My conclusion is that the radiator 2 did not get filled up completely due to the small flow rate. Can you guys input your opinions on why this might have happened ?

other than thinking the radiator wasnt getting filled up completely, I can't really figure out for the life of me why it would not cool the water more than the smaller radiator 1.

thanks

In your other thread, you said that radiator 2 was doing more cooling than radiator 1. Has this changed now? Give us some more data to play with. What are the temperature changes, the heat transfer areas, the tube diameters, the fin sizes, etc.

chet
 
Chestermiller said:
In your other thread, you said that radiator 2 was doing more cooling than radiator 1. Has this changed now? Give us some more data to play with. What are the temperature changes, the heat transfer areas, the tube diameters, the fin sizes, etc.

chet

Yes it has because I got a chance to do the experiment again for radiator 2 and realized in my previous experiment for radiator 2, I was setting the wrong fan frequencies so different wind speed. I carried out the experiment once on radiator 1 as well which showed the same results so results for radiator 1 are still the same. I was half asleep when I carried out the previous experiment for radiator 2.

I now carried out the experiment three times and this is what I got:

Radiator 1:
Water/Coolant:
T(inlet): 363.15
T(Outlet): 334.82

Air at 8m/s:
Before Passing radiator: 295.15K
After passing radiator: 323.15K

Radiator 2:
Water/Coolant:
T(Inlet): 363.15
T(Outlet): 343.15

Air at 8m/s:
Before passing radiator:295.15 K
After passing radiator: 308.48 K

Radiator 1 geometry:
Inlet diameter: 25mm
Outlet diameter: 15mm
Core Height: 115mm
Core Width: 250mm
8 tubes
Fin height: 14.3 mm

Radiator 2 geometry:
Inlet diameter: 25mm
Outlet diameter: 25mm
Core Height: 275 mm
Core width: 200mm
23 tubes
Fin height: 11.96 mm

Do you need anymore info ?
 
knight92 said:
Yes it has because I got a chance to do the experiment again for radiator 2 and realized in my previous experiment for radiator 2, I was setting the wrong fan frequencies so different wind speed. I carried out the experiment once on radiator 1 as well which showed the same results so results for radiator 1 are still the same. I was half asleep when I carried out the previous experiment for radiator 2.

I now carried out the experiment three times and this is what I got:

Radiator 1:
Water/Coolant:
T(inlet): 363.15
T(Outlet): 334.82

Air at 8m/s:
Before Passing radiator: 295.15K
After passing radiator: 323.15K

Radiator 2:
Water/Coolant:
T(Inlet): 363.15
T(Outlet): 343.15

Air at 8m/s:
Before passing radiator:295.15 K
After passing radiator: 308.48 K

Radiator 1 geometry:
Inlet diameter: 25mm
Outlet diameter: 15mm
Core Height: 115mm
Core Width: 250mm
8 tubes
Fin height: 14.3 mm

Radiator 2 geometry:
Inlet diameter: 25mm
Outlet diameter: 25mm
Core Height: 275 mm
Core width: 200mm
23 tubes
Fin height: 11.96 mm

Do you need anymore info ?

What were the tube IDs and ODs? What were the lengths of the tubes between headers? Is that the core width? Fin spacing? Did you calculate the heat loads and the overall heat transfer coefficients?

Chet
 
  • Like
Likes 1 person
Just a thought, but what is the pressure drop across the larger heat exchanger? If this is bigger than the pressure drop of the smaller heat exchanger, it will mean that the flow rate through the larger heat exchanger will be less - provided that the fan speed remains constant for both cases.
I'm not sure of your experimental set-up but in some wind tunnels, fans provide the air-flow. If this is the case and the pressure drop through the heat exchanger increases (due to more tubes in the heat exchanger) the mass flow of air will be less. This is assuming your wind tunnel fan speed has not changed from testing the small heat exchanger to the larger one. Obviously, the resulting smaller air flow through the heat exchanger will lead to less heat transfer.
 
  • Like
Likes 1 person
I checked the air velocities directly at the radiators and the velocity drop was the same for both radiators. I mentioned the water pressure across the larger radiator as it had a slightly higher flow rate coming out of it.

and chestermiller I am sorry for not replying earlier I was running out of time to complete my report so I didnt come online.
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...
Back
Top