What is the recommended size for a neutral conductor in a 3 phase 4 wire system?

AI Thread Summary
In a 3-phase 4-wire system, the recommended size for the neutral conductor can vary based on the application, with some suggesting it should match the phase conductor size for safety. The neutral is not typically expected to carry current except in fault conditions, particularly when powering motors, while it may carry current in low voltage (LV) distribution systems with unbalanced loads. Standards such as IEC or NEC may require the neutral busbar to be the same size as the phase busbar, although specific clauses were not cited in the discussion. Users are advised to err on the side of caution and use the same size conductor if unsure. Proper sizing is crucial for safety and efficiency in electrical distribution systems.
Zubair8
Messages
2
Reaction score
0
Hi,
Frankly, I'm new to this forum. So please do guide me if I posted wrongly.

I need some help in sizing the neutral wire. For a 3 phase 4 wire system (3Ph + N), what is the recommended size of the neutral conductor. Should it be the same as the phase conductor or should it be 50% of the phase conductor. Let say a power cable that is sized up to 300sqmm, does the neutral cable also need to be sized to 300sqmm or can it be less?

Is there any specific standard, IEC or NEC that mentioned the requirement for neutral conductor size. Appreciate if you guys can mention the IEC or NEC number.

Thanks.
 
Engineering news on Phys.org
Do you mean neutral or ground? There may be a difference depending on what you are running power to. When running 3 phase power to a motor for example, what you are calling 'neutral' isn't really neutral at all. It is not supposed to carry any current except in the case of a fault. It is to be grounded to the case of the motor. However, when running 208 or 240 volt power into a building the 4th conductor (combination neutral/ground) will carry some current because of lights and other 120 volt loads. You are always safest making the 4th conductor the same size as the other 3.
 
I agree with Averagesupernova. Use the same size conductor if in doubt.

Three phase systems may or may not have a neutral wire. A neutral wire allows the three phase system to use a higher voltage while still supporting lower voltage single phase appliances. In high voltage distribution situations it is common not to have a neutral wire as the loads can simply be connected between phases (phase-phase connection).
http://www.3phasepower.org/3phasewiring.htm"
 
Last edited by a moderator:
With motor its pretty straight forward, but main concerns are when dealing with LV distribution where unbalanced load exist.

For LV distribution, normally the power supply from LV Switchgear to LV MCC utilizes big cables (150sqmm - 300sqmm). The same case also applies to LV Switchgear Busbar Rating. To save copper, some people opt for lower neutral busbar rating compared to the phase busbar.

As I understand, recently either IEC or NEC requires the neutral busbar to be of the same size as the phase busbar. Can anybody point out to which clause in IEC or NEC that mentioned this.

Appreciated it. Thanks.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top