The heat absorbed by a refrigerant during phase change at low pressure is not equal to the heat released at high pressure due to the work done by the compressor. The heat pump operates by utilizing the latent heat of the refrigerant, allowing it to absorb and reject heat efficiently at small temperature differences. The amount of heat required for phase change does indeed vary with pressure; lower pressure requires less heat for vaporization. Additionally, the heat delivered to the hot reservoir includes both the heat removed from the cold reservoir and the work done on the refrigerant. Understanding these principles is crucial for grasping the efficiency and functionality of heat pumps.
firecool
Messages
11
Reaction score
0
let's say some amount of heat is absorbed by a refrigerant for phase change at a low pressure. will this heat absorbed be equal to the heat given out by the compressed refrigerant at high pressure?
i know that the amount of heat required for phase change from liquid to vapour is less at low pressure.
similarly does the amount of heat required for condensation depend on how much pressure is being applied?
as far as i understand the heat pump functions using the latent heat(of phase change) property of the refrigerant to absorb and reject more heat at small temperature differences. so that more heat flows as the temperature doesn't change during the phase change. am i right?
and please answer the above two questions too. :) and in layman's terms.. :P
 
Science news on Phys.org
firecool said:
let's say some amount of heat is absorbed by a refrigerant for phase change at a low pressure. will this heat absorbed be equal to the heat given out by the compressed refrigerant at high pressure?
No. The heat delivered to the hot reservoir per unit of time (in the case of your refrigerator, the hot reservoir is the air in your kitchen) is equal to the rate at which heat is removed from the cold reservoir (ie. the inside of the fridge) PLUS the rate at which work is being done on the gas (ie. the work done by the compressor on the refrigerant).

AM
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...