The discussion focuses on measuring static pressure pulsations in a duct using a high-frequency response pressure transducer connected to a short measurement tube. The tube's dimensions and the need to avoid high temperatures at the transducer are highlighted, as well as the importance of minimizing the tube's volume to improve measurement accuracy. The Helmholtz resonator theory is initially considered, but due to the lack of an appreciable resonator chamber, an alternative analysis akin to an organ pipe is suggested. The feasibility of using digital notch filtering to manage natural frequency content in the data is also explored. Overall, the conversation emphasizes the complexities of accurately measuring duct frequencies in varying temperature conditions.
Ron D
A high-frequency response pressure transducer at one end of a 7 inch long (approx. 0.6 inch ID) tube will be used to measure static pressure pulsations in a duct of flowing air. Interest is for air at 70 F and at 460 F. The transducer end of the measurement tube has no appreciable volume. What is the frequency response of the measurement system? In other words, what is the highest duct frequency that can be measured with reasonable engineering accuracy?
Are there references that outline the relevant acoustics theory?
Thanks. ...Ron
If you can wing it, it is always best to flush mount dynamic pressure transducers to the flowpath. However, if that is not possible, you will want to shorten the interface tube as much as possible. The Helmholtz resonator natural frequencies can be calculated from
f_n=\frac{c}{4 \pi} \left[\frac{\pi d^2}{V(L+.85d)} \right]^{.5}}
where
V= volume under sensing diaphragm
c = speed of sound
d = diameter of the tube
L = length of tube
If the volume of the tube can be reduced to about half of that of the resonator chamber, then the wave equation form can be used which is a bit simpler:
f_n = \frac{(2n-1)c}{4L}
First, a correction: The tube ID is about 0.06 inch, not 0.6 inch.
Comments to FredGarvin's response:
(1) Cannot flush mount x-ducer. Need to keep transducer away from 460 F air stream in the final test run, the real objective of test. The tube will be cooled over more than half its length to eliminate conduction as well as to cool the air column within.
(2) There is no appreciable resonator chamber. Transducer end of tube terminates in a free space of about 0.25" diameter by 0.008-0.010 inches from transducer diaphragm. Therefore Helmholtz freq. calculation is not appropriate.
It seems to me that this measurement tube system is more of an organ pipe (one end closed) analysis. If so, the natural frequency can be determined by calculation or recognized in the data. We should be able to "trust" pressure variation data (i.e., profile stucture) corresponding to frequencies below and above the region of that natural frequency, and perhaps even do some digital "notch filtering" to eliminate natural frequency content (please confirm). Am I expecting too much in this approach?
This has been discussed many times on PF, and will likely come up again, so the video might come handy. Previous threads: https://www.physicsforums.com/threads/is-a-treadmill-incline-just-a-marketing-gimmick.937725/ https://www.physicsforums.com/threads/work-done-running-on-an-inclined-treadmill.927825/ https://www.physicsforums.com/threads/how-do-we-calculate-the-energy-we-used-to-do-something.1052162/
Thread 'Is 'Velocity of Transport' a Recognized Term in English Mechanics Literature?'
Here are two fragments from Banach's monograph in Mechanics I have never seen the term <<velocity of transport>> in English texts. Actually I have never seen this term being named somehow in English. This term has a name in Russian books. I looked through the original Banach's text in Polish and there is a Polish name for this term. It is a little bit surprising that the Polish name differs from the Russian one and also differs from this English translation. My question is: Is there...
Hi there, im studying nanoscience at the university in Basel. Today I looked at the topic of intertial and non-inertial reference frames and the existence of fictitious forces. I understand that you call forces real in physics if they appear in interplay. Meaning that a force is real when there is the "actio" partner to the "reactio" partner. If this condition is not satisfied the force is not real. I also understand that if you specifically look at non-inertial reference frames you can...