Single phase transformer and net KVA output

AI Thread Summary
The discussion centers on determining the net kVA output of a single-phase transformer designed for 400 Hz when operated at 50 Hz. It is established that kVA output is proportional to frequency, leading to a calculation that suggests a kVA output of 0.5 kVA at 50 Hz. The transformer is intended to provide a 115V supply from a 230V source, but concerns arise regarding its operation outside the designed frequency. A reference indicates that the input voltage must be significantly reduced when using the transformer at a lower frequency to avoid damage. The conversation invites further critique on the proposed method of operation.
anand raj
Messages
17
Reaction score
0

Homework Statement


a 4 kva, 230/115 volt, 400 HZ, single phase transformer originally designed for use in air crafts, is available in a laboratory for obtaining 115 volt supply from standard 230 volt,50 HZ mains if overloading of the device is not permitted then net kva output is...

Homework Equations


The Attempt at a Solution

[/B]
here frequency is varying voltage remaining the same
kva being proportional to frequency
x = kva output for 50 HZ
4/x = 400/50
x = 0.5 kva
i don't know whether it is right or wrong, but the answer is this.
 
Physics news on Phys.org
The wording of the question seems to imply (but stops short of stating unequivocally) that the transformer is to deliver 115V at 50Hz. I can't offer a technical opinion, but according to this reference http://www.edn.com/design/component...sformer-at-a-frequency-it-wasn-t-designed-for
For a power transformer designed for 115VRMS at 400 Hz but used at 60 Hz, the input voltage must not exceed 115×60/400 = 17.25 VRMS

Perhaps others can offer a critique of the suggested scheme.
 