Single Phase Voltage from 3-Phase Line: Explained

AI Thread Summary
In a 3-phase line with a 25kV line-to-line voltage, the voltage of a single phase line is typically 14.4kV when referenced to a neutral. This is calculated using the formula L-N = Vl/sqrt(3). Single phase transformers are used to convert the higher voltage to a user-friendly level, and the neutral is essential for creating a complete circuit. In distribution systems, the preference is for line voltages without using the neutral directly, and the single phase voltage is determined by transformer ratings. Overall, the single phase voltage does not remain at 25kV but is stepped down to a safer level for distribution.
louie
Messages
10
Reaction score
0
If I'm considering a 3 phase line (25kV line-to-line voltage) that comes to a point and splits into single phase lines, what is the line voltage of one of the single phase lines ?

Does it remain 25 kV or is it 14.4 kV because you're only dealing with 1 phase and a neutral now ?

Any explanation would be great

Louie
 
Engineering news on Phys.org
Normally, they do not distribute L-N = Vl/sqrt(3)=14.4kV, only L-L =25kV. The phases can split AB, BC, CA. The single phase transformers convert 25K--> user voltage with the ground reference applied at the secondary neutral.
 
A single phase line by definition is a circuit with only one phase. So you need a neutral side to create a loop. The voltage differential between the line and the neutral is, of course, +/- 14.4 kV and not 25 kV.

If you use both line (AB, AC, or BC) ... I don't think that a single phase line. It may be within the category of two phase line :-)

aaNg
 
For distribution purpose only line voltages preferred so neutral is not used. And 25KV will not be splitted into single phase directly it will be step downed and than you will get a sinle phase line. sinle phase line voltage depends on the transformer rating.
rgds
Mahadev
 
Actually, The main method of urban and suburban over head and URD is done single phase with line-neutra *in the usa*, europe is 3-phase secondary distribution 3-phases+ 2*line voltage = 8* the secondary line distance over the US, the neutral designation is MGN, or multiple grounded neutral, It is a lower wire of the four, or sometimes used as a top wire overhead shield in lightning prone areas. the L-N is used as the final distribution to the LNL +120 N -120 final use in typical residential apps.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...