In a 3-phase line with a 25kV line-to-line voltage, the voltage of a single phase line is typically 14.4kV when referenced to a neutral. This is calculated using the formula L-N = Vl/sqrt(3). Single phase transformers are used to convert the higher voltage to a user-friendly level, and the neutral is essential for creating a complete circuit. In distribution systems, the preference is for line voltages without using the neutral directly, and the single phase voltage is determined by transformer ratings. Overall, the single phase voltage does not remain at 25kV but is stepped down to a safer level for distribution.
louie
Messages
10
Reaction score
0
If I'm considering a 3 phase line (25kV line-to-line voltage) that comes to a point and splits into single phase lines, what is the line voltage of one of the single phase lines ?

Does it remain 25 kV or is it 14.4 kV because you're only dealing with 1 phase and a neutral now ?

Any explanation would be great

Louie
 
Engineering news on Phys.org
Normally, they do not distribute L-N = Vl/sqrt(3)=14.4kV, only L-L =25kV. The phases can split AB, BC, CA. The single phase transformers convert 25K--> user voltage with the ground reference applied at the secondary neutral.
 
A single phase line by definition is a circuit with only one phase. So you need a neutral side to create a loop. The voltage differential between the line and the neutral is, of course, +/- 14.4 kV and not 25 kV.

If you use both line (AB, AC, or BC) ... I don't think that a single phase line. It may be within the category of two phase line :-)

aaNg
 
For distribution purpose only line voltages preferred so neutral is not used. And 25KV will not be splitted into single phase directly it will be step downed and than you will get a sinle phase line. sinle phase line voltage depends on the transformer rating.
rgds
Mahadev
 
Actually, The main method of urban and suburban over head and URD is done single phase with line-neutra *in the usa*, europe is 3-phase secondary distribution 3-phases+ 2*line voltage = 8* the secondary line distance over the US, the neutral designation is MGN, or multiple grounded neutral, It is a lower wire of the four, or sometimes used as a top wire overhead shield in lightning prone areas. the L-N is used as the final distribution to the LNL +120 N -120 final use in typical residential apps.
 
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...