Span distance 150x50 steel tubing

  • Thread starter Thread starter DANger-is
  • Start date Start date
  • Tags Tags
    Span Steel
AI Thread Summary
The discussion centers on the feasibility of spanning 8 meters with 150 x 50 x 3mm steel tubing for a patio without a midspan post. It is noted that without a central post, the steel tube would be overstressed, necessitating additional support. The maximum allowable span between posts is calculated to be approximately 5.14 meters, assuming a tensile yield strength of 275 MPa and a patio height of no more than 1200 mm. Concerns are raised about the attachment of purlins to the steel tubing and the potential for lateral movement. Overall, proper structural support and adherence to building codes are emphasized for safety and stability.
DANger-is
Messages
2
Reaction score
0
I'm designing a patio which is connected to a house on one side, 8m x 2.4m

150 x 50 x 3mm steel tubing around the outside with 140 x 50 hardwood purlins, spaced at 1m intervals (2.4m long each).

I would like to span the 8m with only posts on the ends. Is this possible or will there be to much sag?

Thanks
Dan
 
Engineering news on Phys.org
DANger-is: With no midspan post, your given 8 m steel tube would be overstressed. Therefore, a post at the midspan of your given 8 m steel tube is also needed.
 
Isn't there standards for this? You can't lookup the building codes?
 
Thanks for getting back to me nvn. I'm trying to span as fare as possible withou having a support in the middle. Given that the beam can overhang the posts, I would think I could span the rhs 6.5 m between supports. Which would result in approximately 600 mm overhang on both ends. Any thoughts?
 
DANger-is: What is the material specification, and tensile yield strength (Sty), of your RHS? Assuming Sty = 275 MPa, then the maximum allowable span length between your two posts would be L1 = 5140 mm, using your current steel tube cross section size and wall thickness. This assumes your patio is no more than ~1200 mm above the ground. If the patio elevation exceeds roughly 1200 mm, then the allowable span length L1 would be less.

Are your "purlins" (joists) actually attached to your RHS? And is the midspan of your first RHS attached to the house? Or can your joists slip longitudinally (horizontally), such that your outer RHS has no midspan lateral (horizontal) support near its compression flange?
 
Last edited:
Thread 'I need a concave mirror with a focal length length of 150 feet'
I need to cut down a 3 year old dead tree from top down so tree causes no damage with small pieces falling. I need a mirror with a focal length of 150 ft. 12" diameter to 36" diameter will work good but I can't think of any easy way to build it. Nothing like this for sale on Ebay. I have a 30" Fresnel lens that I use to burn stumps it works great. Tree service wants $2000.
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...