what is the difference between emergency diesel generators and station blackout disel generator? Is Station blackout disel generator just a redundant sysyetm for emergency disel generators?
Thanks Astonuc
Which properties of SBDG's make them different from EDGs?
I mean for example why we don't use 3 EDGs instead of 2 EDGs and one SBDG ?
SBDG's may be larger if they handle more than just the emergency systems. If one has access to a FSAR or UFSAR, one might be able to compare specs. This stuff used to be online, but for security reasons, details from UFSARs have been taken off the internet.
Auxilliary equipment is outside my experience, but I would guess the SBDG's cover other services as well as being redundant to EDG's.
I was surprised to read the number of problems associated with them. :rolleyes:
I'm not familiar with that exact terminology, but I would imagine that the Blackout diesel gens are capable of 'black start', meaning they can start and supply the EPS bus with absolutely no other power available to them. I'm not really all that familiar with these, but normal generators would require fuel pumps, and cooling fans, and other electrical permissives to start up, whereas blackstart does it all from nothing.
Really SBDGs are smaller than EDGs.
In EPR reactor design SBDG must work within about 2 hours after station blackout, in which DC power supplies are available.
The question is why there are SBDGs with lower electrical capacity?
Maybe when you say "station blackout diesel" you really mean "alternate AC source." The reason AACs are smaller than the emergency diesel gens is because they were added to the plants' designs after original construction, in response to the blackout rule (10CFR50.63 ?). That rule addresses the very unlikely situation in which both of the EDGs fail to start following a loss of offsite power. The rule requires each plant to show that they can cope with the blackout for a predetermined time (usually 4 or 8 hours). The rule also allows credit for an AAC, for many units it was easier to add this smaller diesel (or in some cases a gas turbine, or other designs) than to show coping for 8 hours without any AC. Since no concurrent accident is postulated the engineered safety features components are not auto started, hence the AAC capacity is lower than that of the EDGs.
Thanx gmax
By the way what is the difference from safety aspect of a plant with 3 EDGs and 1 SBO diesel generator and the same plant with 4 EDGs?
Really I want to know the philosophy of using Diesel generator as an AAC source.
As opposed to what other source of AC power. Station blackout would like be due to destruction of the one of the transformers or loss of line - either one phase or all (usually 3) phases, so the plant cannot rely on offsite power. If one phase went out, then there would be a considerable load imbalance on the grid - nearest the plant.
Now diesel generators are proven technology. They have been used in railroad and marine service for decades - at least since the 1940's. DG's have an on-site fuel source, diesel fuel which is safe compared to say - natural gas, or propane or butane. The idea is to have an fully independent source of AC power on-site, which is also safe and reliable! Reliability however seems to be problematic in recent history. :rolleyes:
"SBO disel generator" or "emergency disel generator" the problem is!
Thanks astronuc but I didn't get my answer yet!
I think your answer says why Disel Generators are used in the plant as EDGs.
Please think about this question:
Your question can't be answered without some more info about the design of the plant you are considering. I'm not sure what kind of plant design you are thinking about, that would have four emergency diesels. I'm familiar with the plants in the US, these all (?) have two "trains" of engineered safeguards and therefore two emergency power trains and two diesel generators. Your plant, with 3 or 4 diesels wouldn't make sense unless there are 3 or 4 trains of safeguards (safety injection pumps, contanment sprays, vital HVAC, etc...). And depending on how many trains of ESF you have, that's how many diesels you need.
To reiterate, my understanding of what you mean by "station blackout diesel" is another power source, installed for postulated failures of all of the emergency busses. Since AFAIK, no one postulates an Loss of Coolant accident coincident with these failures, the SBO diesel only needs to power the normal RCS makeup and some HVAC loads (with the emergency feedwater powered by steam driven turbine(s), independent of any AC power). So, the SBO diesel is much smaller than the EDGs.
If the plant you are considering is based on a different design, then you can likely be guided by two ideas: (1) the EDGs each power a single train of safety features, and the number of trains required depends on the single failure criterion plus consideration of allowed equipment outages, and (2) the SBO is a "beyond design basis" event that postulates multiple failures in the AC system but does not assume a coincident accident.
Does that help, or is it more confusing?
In very simple terms an emergency generator is capable of suppling the critical items of plant on site that are required to keep things safe; for example cooling pumps and basic station lighting.
To start any power station up from cold it requires power and quite a lot at that. Normally when a power station is started from cold they are able to obtain the start up power from the grid. The problem that station back up generators address is what happens when there are no power stations at all operating on the grid. It is this load that the black out generator is sized for. The load being different from one power staion to the next.
The chances of no power station operating on the grid is actully higher than it first seems. The example that comes to mind is if there was a major earthquake the power stations arcoss a whole region will shut down, this on its own is not a problem as power can be drawn from outside the region across the HV grid. However if there was also a couple of HV lines comprioposed by the earthqauke that supplied the region then theer would be no power available to restart the stations until the comprosied part of the HV grid was repaired.
One thing in the power supply networks is that they love and addicted to reduncancy of systems and for good reason.
Related to Station blackout in nuclear power plants
1. What is a station blackout in a nuclear power plant?
A station blackout in a nuclear power plant refers to a complete loss of offsite and onsite power, which can result in the inability to cool the reactor and its fuel, leading to potential core damage and release of radioactive materials.
2. How does a station blackout occur?
A station blackout can occur due to a variety of reasons, such as natural disasters, equipment failures, human error, or a combination of these factors. For example, a severe storm or earthquake can damage the power supply lines, while equipment failures or human error can lead to a loss of power within the plant.
3. What are the consequences of a station blackout in a nuclear power plant?
The consequences of a station blackout can be severe and can include damage to the reactor core, release of radioactive materials, and potential harm to the surrounding environment and population. It can also result in a prolonged shutdown of the plant and significant economic and environmental costs.
4. What safety measures are in place to prevent a station blackout?
Nuclear power plants have multiple safety measures in place to prevent a station blackout, such as redundant power sources and backup generators, emergency cooling systems, and trained personnel to respond to emergency situations. Regular maintenance and testing of these systems are also conducted to ensure their effectiveness.
5. What is being done to improve the safety of nuclear power plants in the event of a station blackout?
Following the Fukushima nuclear disaster in 2011, many countries have implemented stricter safety regulations and guidelines for nuclear power plants, including measures to prevent and mitigate the effects of a station blackout. These can include enhancements to emergency cooling systems, backup power sources, and better communication and coordination with offsite emergency response teams.
  • Nuclear Engineering
  • Electrical Engineering