----- Phrak quote
Not so fast. An unloaded transformer draws current. This is called the magnetization current. You might be hard pressed to actually come up with a transformer that will self distruct, but in principle the magnetization current could exceed the rated current.
This leads to excessive heating of the core. This could cause the saturation flux density to rise past the saturation knee which leads to an increase in the magnetization current. The rising current adds to more core heating and could result in divergent thermal run-away.
At a guess, I'd think a wall wart with AC output is a good candidate for this sort of failure. Hook two of them up, back to back, and see if the output is 120 VAC, and what gets hot over time.
----- end quote
Begging to differ. First of all, I am well aware of what magnetizing current is. I designed xfms for a company well known for them. Just out of curiosity, have you designed xfmrs? If not, it's no big deal.
When you say the Imag exceeds the rated current, my first reaction is "run that by me again please!" Imag is typically around 5% of the rated load current. If the mag current was excessive, which it isn't, how does runaway take place? An increase in current through the windings incurs a larger IR drop due to the winding resistance. This results in a lower voltage impressed across the primary. The flux will not run away, but decrease with this condition.
If a xfmr is rated at 240V in, 12V out, then the high side, which has thinner wire, and carries lower current, carries an Imag around 5% of rated load. If we instead excite the low side, 12V as the primary, the exciting current times the turns changes very little for the same frequency. The flux is related to volts per turn so that 240V across 240 turns results in approx. the same flux as 12V across 12 turns. The N*Imag will be very close to the original in amp-turns. The core runs at the same temp, and the low side windings run around the same temp, as they are wound with heavier wire, carry more current, but again, sized for full load which is much greater than the Imag.
Regarding the wall wart, I've never seen one with ac output. The output is always, AFAIK, rectified into dc. If you connect 2 units back to back, of course the 2nd unit gets hot. Connecting dc across the 2nd units' winding will burn it up. No debate there.
This is pretty basic stuff. If I've erred I welcome and appreciate correction, but we're talking about transformers here. These are well documented and have been in use since the latter part of the 19th century. There are few mysteries involving xfmrs. BR.
Claude