Thermal power of the air extracted from a building

AI Thread Summary
To calculate the thermal power of the air extracted from a building, the formula P = Cp·flow·DeltaT is suggested, where P is power in watts, flow is in m³/sec, DeltaT is the temperature difference, and Cp is the specific heat. It's important to convert volumetric flow to mass flow using the air's density to ensure the units are consistent and yield power in watts. The specific heat of air is necessary, and the enthalpy may also be considered depending on temperature and humidity. The discussion emphasizes the need for accurate unit conversions to achieve correct calculations. Understanding these principles will help determine if the thermal power exceeds 80kW.
ricardo46
Messages
3
Reaction score
0
Good afternoon.
I need to know if the thermal power of the air extracted from a building is greater than 80kW.
I know the flows entering and leaving the building. Also, I know the temperature of the air inside and outside the building.
How do I calculate the power of the air extracted?
thank you
 
Engineering news on Phys.org
ricardo46 said:
Good afternoon.
I need to know if the thermal power of the air extracted from a building is greater than 80kW.
I know the flows entering and leaving the building. Also, I know the temperature of the air inside and outside the building.
How do I calculate the power of the air extracted?
thank you
You'll need to know either the specific heat of the air at the temperatures encountered or know the enthalpy of the air. The latter will depend on temperature and humidity.
 
  • Like
Likes ricardo46
SteamKing said:
You'll need to know either the specific heat of the air at the temperatures encountered or know the enthalpy of the air. The latter will depend on temperature and humidity.
Ok. I know the specific heat. I have solved problems like this in the past. I am just a bit rusty.

I think I have found the solution:
P = Cp·flow·DeltaT

I am just not sure about the units:
P- power (W)
flow- m3/sec
DeltaT- temperature diference between the inside and the outside of the building
Cp- specific heat (J / (kg . ºK))

Is this correct?
 
ricardo46 said:
Ok. I know the specific heat. I have solved problems like this in the past. I am just a bit rusty.

I think I have found the solution:
P = Cp·flow·DeltaT

I am just not sure about the units:
P- power (W)
flow- m3/sec
DeltaT- temperature diference between the inside and the outside of the building
Cp- specific heat (J / (kg . ºK))

Is this correct?
Seems to be.
 
SteamKing said:
Seems to be.
I think I can't use the flow like this. If i use it like this i won't get the power in watts but this W.m3/kg.
What should i do to get watts?
 
ricardo46 said:
I think I can't use the flow like this. If i use it like this i won't get the power in watts but this W.m3/kg.
What should i do to get watts?
You can convert the volumetric flow to a mass flow, using the temperature of the air to find its density.
 
  • Like
Likes ricardo46
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...

Similar threads

Back
Top