In digital control system design, observer poles should be approximately ten times faster than controller poles for effective performance. The mapping from the s-plane to the z-plane is crucial, as vertical lines in the s-plane correspond to circles in the z-plane, affecting stability. To achieve faster observer poles, one can determine the controller poles, map them to the s-plane, adjust their real parts, and then map them back to the z-plane. However, this adjustment may also influence the damping ratio of the poles. The discussion confirms that this mapping approach is valid for determining observer poles in a digital context.
NeuralNet
Messages
24
Reaction score
0
When designing a State Observer for a control system the observer poles (eig(A-LC)) should typically be about 10 times faster than the controller poles (eig(A-BK)).

But when designing a digital control system what does it mean for the poles to be faster? For the analog case it simply means that to get more negative on the real axis, but since the s-plane is mapped to the z-plane, how does one determine how a pole is faster?
 
Engineering news on Phys.org
Vertical lines in the s-plane (real part = constant) maps to circles of constant radius in the z-plane with the origin as their center.

In the z-plane, as you move from within the unit circle to outside of it, you move from the stable region to the unstable, i.e. the time constant of the pole(s) increase in magnitude as you move away from the origin.
 
Okay, so the mapping from the s-plane to z-plane is as follows:
z=e^{sT}

And from s-plane to z-plane:
s=\frac{1}{T}ln(z)

Where T is the sampling period.

So if the observer poles are supposed to be "10 time faster" than the controller poles can I do the following, given a digital control system:
1. Determine the controller poles.
2. Map them to the s-plane.
4. Take the real part of the poles and multiply by 10. These will be the continuous Observer Poles.
5. Map the continuous observer poles back to the z-plane. These are the discrete Observer Poles.

Would that work?
 
Last edited:
NeuralNet said:
1. Determine the observer poles.
The "controller poles" yeah?

NeuralNet said:
4. Take the real part of the poles and multiply by 10. These will be the continuous Observer Poles.
You're going to affect the damping ratio of the poles as well if you do that. You can move them out along a loci of constant damping ratio (constant angle) until you get the time constant you want.

But yes, you're free to map back and forth as you please.
 
milesyoung said:
The "controller poles" yeah?

Yes, I meant "controller poles" (which I have edited).


You have answered my question. Thank you very much.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...