Understanding Short Circuit Duty in the Grid

AI Thread Summary
Short circuit duty refers to the maximum overcurrent that electrical devices, like transformers and circuit breakers, can withstand during a short circuit event. This high current can cause significant heating and magnetic forces, potentially damaging equipment. Circuit breakers are rated with an "interrupting rating," indicating the maximum current they can safely interrupt, which is crucial for system design. The I²t value, representing the energy during a short circuit, is essential for selecting appropriate fuses and breakers. Evaluating short circuit duty is vital when integrating new generation sources into the grid to ensure existing equipment can handle potential overcurrents.
westsidegirl
Messages
2
Reaction score
0
Can someone explain what short circuit duty is? I see this a lot in my field but I don't know what it means. I see it in the context of new generation coming onto the grid and needing to interconnect to the current transmission system.
 
Engineering news on Phys.org
when a piece of electrical gear, say a transformer or circuit breaker, is subjected to a short circuit overload, the current that flows is quite high.

the high current heats the conductors.
the high current exerts magnetic forces on the conductors.
in a circuit breaker, when the contacts separate to interrupt the current, the current makes an arc that tries to melt the contacts or weld them together.

short circuit duty is a description of the severity of overcurrent that a device can reasonably be expected to withstand.
transformer windings must be stout enough to absorb the heat and withstand the magnetic forces during such an event.
circuit breaker contacts must be robust enough to not melt, and in big ones there must be nonconductive vanes surrounding the contacts to break up the arc.
cut open a big round industrial fuse and you'll probably find it stuffed with sand to quench the arc.

next trip to a hardware store, examine a household circuit breaker like the ones in your electrical panel.
on the back of say a 20 amp breaker you'll see something probably called 'interrupting rating' with a preposterously large number of amps like ten or twenty thousand.
the breaker should successfully interrupt that much current, once.
it's up to the electrical designer to assure that the breaker is never put into equipment that could ask more of it. to that end, it shouldn't physically fit into such equipment.

there's a term (I squared t) , which is the product of current^2 X time(seconds) for an overload. It is proportional to the energy available during a short circuit. You'll find i^2t ratings in fuse and breaker datasheets, and power semiconductor datasheets always tell you what i^2t fuse to use.

best introduction i ever saw to the subject was a little book from International Rectifier called "Semiconductor Fuses". There's also IEEE books on the subject, if you're a member (i'm not).

i hope you're not offended by my oversimplification. it's best to get the basic concept then go out and fill in the details. hopefully this will help you clear up some of those mysterious numbers on datsheets.

old jim
 
That's very helpful. So the short circuit duty studies are essentially seeing whether the new generation being interconnected could result in the potential overcurrent being more severe than what the existing circuit breakers could withstand. If the current circuit breakers that are in place can't withstand it then upgrades need to be done.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...