Why isn't Reactive Power defined as Q = S - P ?

AI Thread Summary
Reactive power is defined as Q = VrmsIrmssinφ, which is derived from the complex representation of AC circuits, where apparent power S = VrmsIrms and average power P = VrmsIrmscosφ. This definition reflects the orthogonal relationship between average and reactive power, necessitating the use of Pythagorean principles rather than simple arithmetic. The discussion emphasizes that while reactive power may seem unintuitive, it represents the energy stored and returned by reactive components, rather than energy consumed. Some participants argue that defining reactive power as Q = S - P could misrepresent its physical significance, as it would not accurately reflect the peak power consumed by reactance. Ultimately, understanding reactive power is crucial for analyzing AC circuit behavior and power factor implications.
  • #51
sophiecentaur said:
Did you read the whole of that link I referenced?

And that expression is positive for half a cycle and negative for the other half - integrating to zero over a cycle. So it doesn't contribute to wasting energy. That is what I cannot get my head round.

I must try to find some source that doesn't just jump in, feet first with the 'power triangle'. There must be a lead in that justifies it better than just making assertions. Perhaps I shall have to reach for my pencil and paper.
Here's one perspective.
http://www.equitech.com/articles/bpng.html
 
Engineering news on Phys.org
  • #52
vintageplayer said:
Over the cycle it doesn't waste energy. The power station (or voltage source) always gets back what it puts out. The problem is that with a power station, this still amounts to the generator running even if you are capable of recouping all the energy back. This wears your plant and costs money because you have to pay staff. You also have maximum outputs on your generators so the more reactive power you put out, the less real power you can put out (and real power is what the power stations get paid for).

The power station would not be putting out nor recouping "Reactive" power. Reactive power may indeed be present within the transmission system and also within the various components in the system, but it is only reactive within the discrete environment it exists in. Once it has passed through each discrete system and is presented at an interface, the system at the other side of the interface does not distinguish between active and reactive, it simply sees a supply.
 
  • Like
Likes sophiecentaur
  • #53
jim hardy said:
Even though Q includes some Joules that do shuttle back and forth between generator and loads on a subcycle basis,
we consider reactive current to be Wattless since it won't turn the disc on a watt-hour meter.
If you want to be understood in practical circles , use terms in the way to which practical people are accustomed.

Agree. Just emphasising that reactive power is measurable in Watts, and has real practical effects on the output of a generator (i.e. it serves some useful purpose). The more reactive power you supply, the less real power you can supply (as per the capability curve you attached). It also costs a power plant real resources, and therefore dollars, to supply reactive power. These are some of the practical reasons why you would want to know / calculate reactive power.
 
  • Like
Likes sophiecentaur
  • #54
vintageplayer said:
Agree. Just emphasising that reactive power is measurable in Watts, and has real practical effects on the output of a generator (i.e. it serves some useful purpose). The more reactive power you supply, the less real power you can supply (as per the capability curve you attached). It also costs a power plant real resources, and therefore dollars, to supply reactive power. These are some of the practical reasons why you would want to know / calculate reactive power.

OP, post a link to validate that "Reactive power" is a measurable quantity at the supply-> interface.

I will also say that it is not measurable in Watts, which is a measure of Volt Amps.
Reactive power must be separated from apparent power, before it can be measured. VAR delineates that part that exists because of the Reactive components, it is still measured in Volt Amps but further sub-classed to differentiate it as a component of total VA.

When we measure VAR as it is segregated from apparent power, we can determine better what we expect "average power" to be, then after it has been reintegrated we should notice that we can obtain more frequent measures that are equal to "average power", which can be a benefit and especially in circuits that require wave rectification or to remove pulse and flutter, for example. These quantities may 'seem' more trivial in Hydro related concerns, but can certainly become important in Audiovisual and Data manipulation environments.

This, would seem to disagree with your notion above.
http://www.engineeringtoolbox.com/kva-reactive-d_886.html

Edit: to correct spelling.
 
  • Like
Likes sophiecentaur
  • #55
vintageplayer said:
Just emphasising that reactive power is measurable in Watts,
Wee-Lamm said:
I will also say that it is not measurable in Watts, which is a measure of Volt Amps.

If in a meeting of utility folks you described reactive power as WATTS instead of VARS , eyes would roll. Thereafter you'd be ignored or asked to keep quiet.

VARS can be measured with a wattmeter by shifting phase of current 90 degrees wrt voltage. One might hand it phase A-C volts and phase B current.
 
Last edited:
  • Like
Likes sophiecentaur
  • #57
It has taken 50+ posts for me to get any proper message about Reactive Power. I now realize that it's basically about how to charge the customers a realistic price for the Energy they are using. It's a sort of weighted sum of Energy and Generating Equipment Costs. Reactive Power gives a general idea about the various stresses that poor PF subjects the supply equipment to. I find it interesting that such a simple formula gives such an aparently useful parameter for Engineers to work with.
But most of what you can read about it seems to ignore the real context and reason for the quantity being used. They tell you the formula and give you some diagrams but not the whys and wherefores. Thank you Wee-Lamm for injecting a different slant on things into the thread. (And the rest of you too!)
 
  • Like
Likes Wee-Lamm
  • #58
sophiecentaur said:
It has taken 50+ posts for me to get any proper message about Reactive Power. I now realize that it's basically about how to charge the customers a realistic price for the Energy they are using. It's a sort of weighted sum of Energy and Generating Equipment Costs. Reactive Power gives a general idea about the various stresses that poor PF subjects the supply equipment to. I find it interesting that such a simple formula gives such an aparently useful parameter for Engineers to work with.
But most of what you can read about it seems to ignore the real context and reason for the quantity being used. They tell you the formula and give you some diagrams but not the whys and wherefores. Thank you Wee-Lamm for injecting a different slant on things into the thread. (And the rest of you too!)

Thank you too.

I think though, that you still see Reactive Power as something that is provided by the power supply. Reactive power is not something that can pass from one system to another and still be a measurable quantity. We may tend to imagine that hydro is sent directly from the coal plant to our fluorescent light bulb, but it is not that direct. To simply it immensely for this discussion, we must realize that there are several interfaces between the coal plant and our light bulb.

The power coming down the hydro lines may consist of a supply of 1,000 A at 700Kv. Our light bulb requires less than 1 amp at 120v. At the pole there is a step-down transform, which is a reactive device in reference to the supply lines within the delivery system domain, that filters the power into a format that my 200A-240V meter interface can cope with. My meter cannot tell if it the power it receives is reactive or not, and it really doesn't care.

The Ballast for my fluorescent lamp is also a reactive device, but the light-bulb itself cannot discern whether it has been supplied with active or reactive power, and it really doesn't care. The measure of Reactive power is only relevant within the unique system domain which caused it to be phase shifted or otherwise colored for the needs of that specific domain.
 
  • #59
Wee-Lamm said:
I think though, that you still see Reactive Power as something that is provided by the power supply.
No. Not me. Reactive power does represent a 'demand' on the system - otherwise no one would be bothered by it.
Wee-Lamm said:
but the light-bulb itself cannot discern whether it has been supplied with active or reactive
Now that's a strange comment. You yourself have made the point that Reactive Power doesn't come from the supply. The light bulb, itself is merely supplied with a Voltage and it 'chooses' how much current to take. If the tubne itself is purely resistive then the power that it consumes is V.I and that's what the power station needs to provide it with. The 'demand' that results from reactive elements in the load is not an Energy Demand; it just represents an overhead that's involved in extra current or volts associated with the generator (+ all the rest of the supplystuff).
I still must say, it strikes me as really strange that a diagram is drawn which involves a Mean Power and a Maximum instantaneous VI value. The coal that's shovelled into the boiler is somehow treated as the same as the extra spec needed for the components. Little wonder that 'they' tell you just to use the formula and 'get over it', without encouraging too much throught about what it all actually represents.
Wee-Lamm said:
My meter cannot tell if it the power it receives is reactive or not, and it really doesn't care.
If it is a Power Meter then it will only measure the in phase components of V and I. If your appliances happen to be very reactive, it will not be aware but still tell you the Energy dissipated per second.
 
  • Like
Likes Wee-Lamm
  • #60
sophiecentaur said:
If your appliances happen to be very reactive, it will not be aware but still tell you the Energy dissipated per second.

sophiecentaur said:
The light bulb, itself is merely supplied with a Voltage and it 'chooses' how much current to take. If the tubne itself is purely resistive then the power that it consumes is V.I and that's what the power station needs to provide it with. The 'demand' that results from reactive elements in the load is not an Energy Demand; it just represents an overhead that's involved in extra current or volts associated with the generator (+ all the rest of the supplystuff).
Draw the triangle, accept that as the old-timers deduced, reactive "power" isn't power at all it's just Volt-Amps-Reactive and is wattless.
That fits nicely with our use of RMS measurements for AC power which include averaging over some time duration of at least one cycle.

If somebody wants to study instantaneous volts, amps and power they should have at it because that's useful to understand why Vars are Wattless. That's about as far as it needs to go IMHO.
...
... But, Melville did give credit to his "sub-sub librarian" .
 
  • Like
Likes Wee-Lamm
  • #61
jim hardy said:
reactive "power" isn't power at all
There we have it: from the horse's mouth. :smile:
This has been a great, if rather inefficient way for me to get into this stuff.
 
  • #62
jim hardy said:
reactive "power" isn't power at all it's just Volt-Amps-Reactive and is wattless.

What SI fundamental units does reactive power have? What SI fundamental units does average power have?
 
  • #63
sophiecentaur said:
I still must say, it strikes me as really strange that a diagram is drawn which involves a Mean Power and a Maximum instantaneous VI value

sophiecentaur said:
Reactive Power gives a general idea about the various stresses that poor PF subjects the supply equipment to. I find it interesting that such a simple formula gives such an aparently useful parameter for Engineers to work with.

Reactive power is defined as (VI/2).sinφ. This is the amplitude of the second component in the equation:
p(t) = v(t).i(t) = (VI/2)cosφ[1 + cos(2wt)] + (VI/2).sinφ.sin(2wt)

But the above equation can also be written as:
(VI/2)cosφ + (VI/2).cos(2ωt -φ)

Why not define reactive power as the amplitude of the second component in the above equation instead? Q = (VI/2). Wouldn't this make more sense because it would tell you how much the power is fluctuating around the actual supplied real power?
 
  • #64
Power is a flow of energy from a source to a load.
Power is measured by work over time.
http://hyperphysics.phy-astr.gsu.edu/hbase/pow.html#pw said:
The standard unit for power is the watt (abbreviated W) which is a joule per second.
"Reactive power" does no work because it only shuttles energy back and forth between load and source.
So the quotient work/time for reactive power averages to zero
The work done by "Reactive power" is zero. So it's not power at all. It's wattless. It requires no torque from a prime mover.
This calculation is only for cases where the force is in the direction of the velocity, and there are many cases where that is not so. Then for instantaneous power, you just multiply the product of force and velocity by the cosine of the angle between them to get the power. In the more general cases where everything varies, one often calculates the work first and then divides by the time to get the average power.
ibid
vintageplayer said:
Why not define reactive power as the amplitude of the second component in the above equation instead? Q = (VI/2). Wouldn't this make more sense because it would tell you how much the power is fluctuating around the actual supplied real power?

Because VIsinθ works just fine
and we use RMS not peak or instantaneous values because that's what our meters indicate
and VARS do tell you exactly how much reactive power is many reactive volt-amps are circulating,
Our VAR meter is prominently located on the panel near the voltage regulator knobs that control VARS.

vintageplayer said:
Why not define reactive power as the amplitude of the second component in the above equation instead? Q = (VI/2).

"Q = (VI/2)"
?
That's "S" per your first post. We'd use RMS and call it KVA, of course multiplied by √3 for three phase.
 
Last edited:
  • #65
sophiecentaur said:
No. Not me. Reactive power does represent a 'demand' on the system - otherwise no one would be bothered by it.

Now that's a strange comment. You yourself have made the point that Reactive Power doesn't come from the supply. The light bulb, itself is merely supplied with a Voltage and it 'chooses' how much current to take. If the tubne itself is purely resistive then the power that it consumes is V.I and that's what the power station needs to provide it with. The 'demand' that results from reactive elements in the load is not an Energy Demand; it just represents an overhead that's involved in extra current or volts associated with the generator (+ all the rest of the supplystuff).
I still must say, it strikes me as really strange that a diagram is drawn which involves a Mean Power and a Maximum instantaneous VI value. The coal that's shovelled into the boiler is somehow treated as the same as the extra spec needed for the components. Little wonder that 'they' tell you just to use the formula and 'get over it', without encouraging too much throught about what it all actually represents.

If it is a Power Meter then it will only measure the in phase components of V and I. If your appliances happen to be very reactive, it will not be aware but still tell you the Energy dissipated per second.

It sounds like we are 'almost' saying the same thing much of the time but, I'll pause briefly to be sure I understand if and how PF affects my position.

I think though that we are not both thinking from the same reference point where my reference is inside my device whereas you are speaking from within the distribution network. If I am right on that point, then everything within the distribution/transmission realm would be part of that device.
 
  • #66
jim hardy said:
Power is a flow of energy from a source to a load.
Power is measured by work over time.

"Reactive power" does no work because it only shuttles energy back and forth between load and source.
So the quotient work/time for reactive power averages to zero
The work done by "Reactive power" is zero. So it's not power at all. It's wattless. It requires no torque from a prime mover.
ibid

OK I understand what you're saying here. I wasn't aware that the term "Watts" was reserved only for time rate change of work and not energy.

jim hardy said:
and VARS do tell you exactly how much reactive power is many reactive volt-amps are circulating,
Isn't this reasoning circular? Reactive volt-amps are by definition VARS?

jim hardy said:
"Q = (VI/2)" ?
That's "S" per your first post.
I know it's S. If S is capable of quantifying the circulating volt-amps on top of your average power, what is the utility of defining an additional quantity, Q and calling it the reactive power?

jim hardy said:
Because VIsinθ works just fine
Sure it works fine, but couldn't P and S do everything we need? What is the real reason for working with Q?
 
  • #67
vintageplayer said:
What SI fundamental units does reactive power have? What SI fundamental units does average power have?
I'm afraid that's not a valid argument. I could ask you what are the units for Work and Torque and a dimensional argument would tell us they are the same. They are not - and the difference is very much along the lines of the difference between W and 'Reactive Power'.
 
  • #68
Wee-Lamm said:
my reference is inside my device
If "inside the device" was all that counted, the PF of any appliance would have no effect on the system. But the effect of PF of multiple appliances on the system is additive.
You seem to be rather preoccupied with finding a good model for 'what's really going on. I am being more pragmatic and looking at the overall effect (cost) of PF. It seems to me that PF is only of concern to the supplier, as long as out Energy Meters just measure Energy and charge us for Watts only. The actual effect of a particular PF and a particular Load will vary from place to place because the supply equipment is very much a part of the (£$) equation. If the load demand on an isolated power station were to be reduced (say all the factories in a town closed down) then the PF of the remaining houses and equipment would be pretty well irellevant.
 
  • #69
jim hardy said:
and we use RMS not peak or instantaneous values because that's what our meters indicate
That could be real reason.
 
  • #70
vintageplayer said:
I know it's S. If S is capable of quantifying the circulating volt-amps on top of your average power, what is the utility of defining an additional quantity, Q and calling it the reactive power?
No, S is NOT capable of that
and maybe there's the miscommunication
what do you mean by "circulating" ? To us power guys "circulating amps" are reactive because they circulate between machines.
If you've never had control of two machines in parallel you cannot imagine the sense of wonder when tweaking one voltage regulator makes amps go up or down on both machines. The load doesn't need to accept those amps, they just circulate between the generators.S doesn't separate out of phase volt-amps from in phase volt amps
S is the hypotenuse as pointed out by Hesch in post #2
upload_2016-1-20_17-14-21-png.94557.png


in my power plant,
P i control by how much steam i admit to Mr Turbine and my wattmeter shows me P
Q i control by how much field current i apply to Mr Generator and my varmeter shows me Q
I don't have a S meter but i do have ammeters in series with the armature windings, which, at constant voltage are an indication of S ,
and i have voltmeters between phases ,
and for a sanity check on my instruments
at constant load (constant megawatts)
...i can adjust excitation to give minimum armature amps which means there's no reactive current
... then i verify varmeter reports zero and that's my zero check on Q meter (varmeter)
...and i verify my wattmeter reports VI√3, that's my check on S .
but of course i'd have to co-ordinate that testing with system dispatcher and nearby power plants so as to not upset the grid.

That's my utility guy perspective. The lingo is well established and is the dialect that's understood in my circles.
Reactive demand on the system is set by what is connected to the system
generators supplying that reactive demand share the reactive current amongst themselves , each supplying its share,
by means of adjusting their field currents individually
raising one machines' field current will affect armature amps on all nearby machines

Changing the language will not be well received. Utilities are just that way.
 
  • Like
Likes sophiecentaur
  • #71
sophiecentaur said:
If "inside the device" was all that counted, the PF of any appliance would have no effect on the system. But the effect of PF of multiple appliances on the system is additive.
You seem to be rather preoccupied with finding a good model for 'what's really going on. I am being more pragmatic and looking at the overall effect (cost) of PF. It seems to me that PF is only of concern to the supplier, as long as out Energy Meters just measure Energy and charge us for Watts only. The actual effect of a particular PF and a particular Load will vary from place to place because the supply equipment is very much a part of the (£$) equation. If the load demand on an isolated power station were to be reduced (say all the factories in a town closed down) then the PF of the remaining houses and equipment would be pretty well irellevant.

Yes, we are not both speaking from the same domain or at least, we haven't yet agreed on what a system is. I tend to not see everything as simply 1 system but rather, as a huge collection of systems, where each system can contain several devices or sub-systems. Can we view the power grid as a system of systems, to allow for a common reference point?

I still stand on my opinion that; my device does not care if the power it draws from the supply system, contains reactive or only active power. My device cannot tell the difference unless I design it to do so.

Having read a little more as encouraged by your comments, I agree that if my device includes components that create Induction or capacitance, which will put the E&I out of phase within my device, I should include properly valued Capacitors or Inductors to put them back in phase, at the exit point of my device. While this will avoid having the "power, returned off cycle" from being viewed as consumed power, it will also avoid the off-cycle overloading of the neutral side of the supply system. I could mention switching capacitors and such, but I suspect you are already ahead of me in that respect.

Being a good neighbor, by having a PF as close to 1 as possible, is definitely beneficial to anyone connected to the same grid and especially to the stability and safety of the grid itself, just as I would benefit if everyone else is a good neighbor and keeps everything at the interface, in the same cycle-phase relationship. Clearly if nobody else is a good neighbor, I will potentially suffer from periodic under-supply until the neutral line catches up, but I still cannot tell if the power I am receiving is made from burning coal, an induction network, or generated otherwise. As long as E & I are in phase, my local device will only see it as power.
 
  • #72
vintageplayer said:
Reactive power is defined as (VI/2).sinφ. This is the amplitude of the second component in the equation:
p(t) = v(t).i(t) = (VI/2)cosφ[1 + cos(2wt)] + (VI/2).sinφ.sin(2wt)

But the above equation can also be written as:
(VI/2)cosφ + (VI/2).cos(2wt -φ)Why not define reactive power as the amplitude of the second component in the above equation instead?

Having thought about this some more, defining reactive power in the first way is best because:
  1. Both Q and P are conservative at every node, whereas VI/2 isn't conservative. This allows a conservation of power approach to circuit analysis (much like a conservation of energy approach in physics).
  2. It ensures reactive power is not consumed by resistive loads. Reactive power is only consumed by reactive components. Even though you have sloshing of power across a purely resistive load, you might not necessarily want to call this a "reactive power".
  3. When φ is negative the reactive power is negative. This allows you to think of capacitors as supplying reactive power, and inductors as consuming reactive power.
  4. Q can be expressed as the imaginary component of VI*.
 
  • #73
vintageplayer said:
Having thought about this some more, defining reactive power in the first way is best because:
  1. Both Q and P are conservative at every node, whereas VI/2 isn't conservative. This allows a conservation of power approach to circuit analysis (much like a conservation of energy approach in physics).
  2. It ensures reactive power is not consumed by resistive loads. Reactive power is only consumed by reactive components. Even though you have sloshing of power across a purely resistive load, you might not necessarily want to call this a "reactive power".
  3. When φ is negative the reactive power is negative. This allows you to think of capacitors as supplying reactive power, and inductors as consuming reactive power.
  4. Q can be expressed as the imaginary component of VI*.

Q = VI Sinφ //Note: I > I/2
or
VAR =√ (VA2 – P2) //Where P = VI Cosθ and Q = VAR

The image of the Power Triangle should show that V & I are 90 degrees out of phase, in Reactive power.
http://www.electricaltechnology.org/2013/07/active-reactive-apparent-and-complex.html

1. I'm not sure if this applies to Reactive power, it's not so much conserved but time shifted.
2. I think Reactive power is still consumed by resistive loads, but the measurement must account for the phase differential.
3. A Capacitor creates an Electric field which causes E to lag behind I, whereas an Inductor creates a Magnetic field which causes I to lag behind E. You could say that a Capacitor "absorbs" voltage and that an Inductor "absorbs" current, but each one releases it again on the down-sweep of it's respective wave, but neither one consumes energy or power. (Except perhaps minimal heat loss of the materials the inductor or capacitor are made from).

I don't think φ can be negative. It indicates which angle is being measured in the power triangle.

4. Q is not imaginary, it simply has the V & I existing at different time points on the curve. φ is needed so we can measure the angle of shift, to determine how many degrees it has been shifted. Sin and Cos determine which angle we should measure to determine if it was E or I which has been held back in the cycle.
 
  • #74
Wee-Lamm said:
Q is not imaginary,

good for you

we call it imaginary because it's current that is shifted 90 degrees wrt voltage

Operator j shifts a sinewave 90 degrees and is called i for imaginary because that's equivalent to √-1, and multiplying a sine by j twice makes it negative implying j is √-1 .
But j must be imaginary because everybody knows negative numbers don't have square roots !
So we call the in phase and out of phase components real and imaginary ... and name the axes on our phasor diagram real and imaginary.
There had to be abundant lab humor back in late 1800's when this stuff was being first worked out from lab experiments. . Here's how Sylvanus P Thompson began his calculus book
Sylvanus P. Thompson, Calculus Made Easy
Considering how many fools can calculate, it is surprising that other fools think it is difficult...

Maybe some wag in late 1800's figured out that those out-of-phase volt-amps make no heat so he called them "imaginary watts" ?
 
  • #75
jim hardy said:
good for you

we call it imaginary because it's current that is shifted 90 degrees wrt voltage

Operator j shifts a sinewave 90 degrees and is called i for imaginary because that's equivalent to √-1, and multiplying a sine by j twice makes it negative implying j is √-1 .
But j must be imaginary because everybody knows negative numbers don't have square roots !
So we call the in phase and out of phase components real and imaginary ... and name the axes on our phasor diagram real and imaginary.

Thank you for the primer, it lead to further educational reading. :-)

There had to be abundant lab humor back in late 1800's when this stuff was being first worked out from lab experiments. . Here's how Sylvanus P Thompson began his calculus book

Maybe some wag in late 1800's figured out that those out-of-phase volt-amps make no heat so he called them "imaginary watts" ?

Or a Whig. :D
 
  • Like
Likes jim hardy
  • #76
Wee-Lamm said:
Or a Whig. :D
We don't get many political jokes (or historical ones) on PF. A double whammy.
 
  • Like
Likes jim hardy