Why the Square Root of 3 in 3-Phase Voltage Drops?

Click For Summary

Discussion Overview

The discussion revolves around the appearance of the square root of three in calculations related to three-phase voltage drops, particularly in the context of different connection types (Delta vs. Wye) and the implications for voltage measurements in three-phase systems.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant seeks clarification on why the square root of three appears in voltage drop calculations for three-phase systems.
  • Another participant provides a mathematical derivation showing that the voltage between phases A and B can be expressed as VAB = sqrt(3) * V, where V is the magnitude of either phase voltage.
  • A participant questions the relevance of line-to-line voltages in a balanced three-phase load, suggesting that only the voltage drop across a single conductor should be considered.
  • Discussion arises regarding the differences between Delta and Wye connections, with some asserting that line and phase voltages are not the same in Wye configurations.
  • Concerns are raised about the accuracy of voltage drop calculators that do not differentiate between connection types.
  • Another participant emphasizes the importance of line-to-line voltages in certain load configurations, countering the earlier claim about the lack of return load.
  • One participant challenges the initial subtraction method for calculating VAB, suggesting it should be a sum instead, leading to further clarification about phasor representation.
  • Another participant supports the subtraction method, explaining that voltage is a potential difference and referencing phasor diagrams.
  • Further discussion includes the geometric interpretation of phasors and the trigonometric basis for the square root of three's appearance, with references to vector diagrams and triangle properties.

Areas of Agreement / Disagreement

Participants express differing views on the calculation methods for voltage drops and the relevance of line-to-line versus line-to-neutral voltages. The discussion remains unresolved with multiple competing perspectives on the correct approach.

Contextual Notes

Some participants note that assumptions about connection types and load configurations may affect the validity of certain calculations and interpretations. The discussion includes unresolved mathematical steps and varying interpretations of phasor relationships.

jimbrosseau
Messages
3
Reaction score
0
Banging my head against a wall trying to prove to a coworker why the square root of three shows up in a three-phase voltage drop calculation...any ideas?
 
Engineering news on Phys.org
The voltage at VAB comprises of VA - VB (which are equal in magnitude):

VAB = VA - VB = V@0 - V@-120 = V [1@0 - 1@-120]

V [1@0 - 1@-120] = V [cos(0) + jsin(0) - {cos(-120) + jsin(-120)}] = V [1 - cos(120) + jsin(120)]

V [1 - cos(120) + jsin(120)] = V [1 + 1/2 +j sqrt(3)/2] = V [ 3/2 + j sqrt(3)/2]

V [ 3/2 + j sqrt(3)/2] = V [sqrt(3)@30]

Therefore the Voltage between A & B is sqrt(3) the magnitude of either A or B and is 30 degrees out of phase.
 
Thanks Zryn, however, I'm still not clear how that implies the voltage drop on a three-phase load involves the Sqrt(3). After all, there is no return load on a balanced three-phase load, and thus why would one consider line-to-line voltages? It just seems to me that considering anyone of the three phase conductors at a given voltage (say 120V) would result in a voltage drop of V=IZ where Z is the impedance of the conductor and I being the motor's draw. I'm not convinced yet :(
 
If you have a 'Delta' connection the line and phase voltages are the same, so I'll assume you have a 'Wye' connection.

In a 'Wye' connection VA (line) = sqrt(3) VAB (phase), so when you say V = IZ and you are talking about a single conductor, do you mean V/sqrt(3) = IZ?
 
That's the thing! It doesn't matter. You look up any 3-phase voltage drop calculator and they do not discern between Delta or Wye connected loads or sources.
 
Do you have a link to the specific calculator you are using? They are probably just using certain assumptions which validate the result.
 
"After all, there is no return load on a balanced three-phase load, and thus why would one consider line-to-line voltages?"

on a 3 phase system, phase b is phase a return, phase c is phase b return, and phase a is phase c return.

The voltages are different line to line than line to neutral because of the proof than zyrn posted.

So there are in fact cases where the line to line voltages are important... i.e. any load connected between two or even three phases?
 
sorry to bump this old thread but wait...

Shouldn't voltage Vab be the sum of the two phase voltages Va and Vb, not the difference as Zyrn suggests?

is it really Vab = Va-Vb, that would suggest The difference between A and B is smaller than Va to ground, which isn't the case, because Vab is obviously 1.73 times larger... So the proof works, but it isn't correct, is it?

Can someone please set me straight here?
 
Yes, Zyrn is right. Voltage is potential _difference_, hence the subtraction. If you know phasor notation/diagram (similar to vectors), look here:
http://www.electronics-tutorials.ws/accircuits/acp50.gif

Where Vab is an phasor with arrow at Va, and tail at Vb. Hence Vab=Va-Vb (normal vector subtraction/addition)
 
  • #10
that link does not work for me.

Yeah, I drew the circuit, Vab is a vector whos head is at a , tails at b.

Current flows from a, returns on b

so voltage is dropped across a and b in the opposite direction as Vab?... therefore its the sums of Va and Vb that make up Vab?

Still not getting this
 
  • #11
is the volt drop on Va opposite with respect to the volt drop on Vb?

I mean current only flows in one direction through the two phases,

That is why I have trouble seeing how it could be the DIFFERENCE of the voltages

Hmm...

I think I might get it now.

Maybe Va and Vb are opposite.
 
  • #12
Don't mean to dredge this up from the past, but I think you've got the vector addition incorrect.

Vab = (-Va) + Vb = Vb - Va

As was stated earlier, Vab is a voltage phasor (or vector) whose tail is at "a" and whose head is at "b", thus meaning phasor from "a" to "b". To traverse this vector path one has to go backwards along Va (hence the minus) and then forwards along Vb, this leads to the minus sign when the re-arrangement is done as above.

Regards
Darryl
 
  • #13
The reason for the "Root Three" turning up is the trigonometry involved with the phasors. Your three phasors point from the origin in three directions, separated by 120°. The potential between any two of these phasors is 2V0Cos(60°), which is √3V0. Draw out the vector diagram and work out the distance between the vertices of the triangle made up of the ends of the vectors.
 
  • #14
Recall that a 30-60-90 degree triangle has sides with proportion 1-2-√3.
Three phase is rich in those particular angles.

Draw the phasors, as Sophie said...
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 15 ·
Replies
15
Views
6K
Replies
38
Views
7K
Replies
14
Views
6K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
8
Views
4K
  • · Replies 3 ·
Replies
3
Views
5K
Replies
13
Views
4K
  • · Replies 77 ·
3
Replies
77
Views
9K
Replies
2
Views
5K