Why we use motorized circuit breaker?

AI Thread Summary
Motorized circuit breakers (CBs) are used for remote operation, allowing users to close or open the breaker using electrical signals. They function by charging a spring that closes the CB contacts, with local operation achieved manually and remote operation facilitated by a motor. To operate remotely, the CB requires close and open coils, which need auxiliary power to function. The under voltage trip (UTP) coil acts as a safety mechanism, ensuring the CB opens if auxiliary power is lost, preventing potential hazards. Understanding this mechanism is crucial for effective circuit breaker operation and safety.
Mateen-ud-din
Messages
12
Reaction score
0
hi all...
i want to know you buddy..
why we use motorized circuit breaker along with under voltage trip (utp) and how motorized circuit breaker works along with under voltage trip (utp)...
i want to know briefly about this procedure...
your answer will be appreciate.
thanks advance...
 
Engineering news on Phys.org
Circuit Breakers need a way to operate. This can be locally (when you stand in front of the CB) or remotelly by giving an electrical signal commanding the circuit breaker to close.
Before to be able to close CB you have to charge a strong spring inside CB. This charged spring is used to close CB contacts internally.

So for local operation you manually charge the spring using a particular lever for that purpose. With a button mounted on the CB front face, you press it and you close the CB.

When you want remote operation of the CB you need a kind of motor to charge the internal spring (so we call this CB motorized).
Moreover, for remote operation you need a couple of electrical reles (coils) such as "close coil" and "open coil". This coils are capable to be remotelly energized by a signal and thus can close / open the CB.

Since we talk about open/close coils it is clear that coils need auxiliary power to operate. If for some reason auxiliary power is lost, then you are not able to operate the coils (close / open). Imagine that you have sucesfully closed circuit breaker (by remotely energizing close coil) but during operation for some stupid reason auxiliary voltage is lost . As a result you can't open the CB!
UnderVoltage Coil comes to cover this hole.
In case auxiliary power required for the coils to work is lost, the undervoltage trip coil forces the opening of the circuit breaker.
Notice that undervoltage trip coil is optional. Close and Open coils is mandatory for remote operation.
 
thanks ge.vasiliou...this is go0d knowledge for me....
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...