Wiring Generator: Connect 3 Phase Wild AC

  • Thread starter Thread starter Isimanica
  • Start date Start date
  • Tags Tags
    Generator Wiring
AI Thread Summary
Connecting two three-phase wild AC wind turbines in parallel requires careful consideration of their phase alignment to avoid potential damage. Each turbine's output should be rectified separately before being combined, as they may not operate at the same speed, leading to electrical conflicts. Using a second charge controller is recommended to manage the combined output effectively and ensure safe operation. Detailed specifications of the generators and charge controller are necessary for tailored advice. Engaging with dedicated wind turbine forums can provide valuable insights and practical guidance for system setup.
Isimanica
Messages
15
Reaction score
0
I have two wind turbines that I am trying to wire up for power generation. They are three phase wild ac. I have a charge controller setup with dump resistor but I want to know if I can take the wires and connect each of the three wires to their counter part from the other generator and then through a rectifier that is built into my charge controller setup?
 
Engineering news on Phys.org
Three phase generators can be connected in parallel only when they are "in phase" and can be expected to remain so. If one's phase tries to drift then maximum current tries to flow and that can mean smoke and fire! Accordingly, your two wind turbine three phase generators will probably need their power output rectified separately, and then summed together as DC.

You have not given enough detailed information about your system to expect usable advice. Can you please provide make/model numbers of both the generators and the charge controller? Can you show your proposed wiring diagram? Is there any battery storage in your planned system? All the technical specifications of each element in the system would be useful. What does "three phase wild ac" mean? What is a "dump resistor"?

Cheers,
Bobbywhy
 
That won't work unless both turbines ran at exactly the same speed and were just alike. They will just short each other out.

You can put rectifiers on each turbine before the charge controller and feed them both into it but the turbines will still tend to 'fight' each other electrically as it's unlikely they will both run at the exact same speed even if they were side by side.

The proper way to do it is by getting a second charge controller. They will both work at the same time connected up to a battery system. Also the second controller might not need to have the dump function if the first one can handle the total possible output from both turbines. You'll have to check your controller manual for info on that.

There are a number of wind turbine forum groups on the net (a couple of very good ones are on Yahoo) that can give you all the information you could want for setting up your system and it will be coming from people that have already done it and learned all the pitfalls.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...