What is the Amperage Rating of a 3-Pronged Edison Plug

  • Thread starter Thread starter Juxt
  • Start date Start date
  • Tags Tags
    Amperage Rating
AI Thread Summary
A standard three-pronged Edison plug is typically rated at 15 amps, which allows for a maximum of 1800 watts on a 120-volt outlet in the U.S. Most household circuits are designed to handle either 15 or 20 amps, and exceeding this can trip circuit breakers. When designing electrical systems, it's common to limit the number of outlets on a single circuit to prevent overload, with considerations for specific high-demand appliances. Additionally, electrical codes dictate that connected equipment should not exceed 80% of the circuit's ampere rating, especially for continuous loads. Proper understanding and adherence to these ratings are crucial for safety and efficiency.
Juxt
Messages
8
Reaction score
0
I know this isn't quite what you mean when you say electrical engineering, but, how many amps is a standard three-pronged edison plug rated at? Also, what is common house wiring rated at?

I believe that a three-pronged plug is rated at 15 amps and that logically the wiring should be able to carry at least that. By my calculations then in the US with good ol' 120-volts you should be able to carry 1800 watts on a wall outlet.

I'm just a layman at electricity and I just wanted to be sure. As much as some people dream about it I don't want to burn down my school.
 
Engineering news on Phys.org
You're correct, most circuits in most buildings will carry 15 or 20 amps. If you try to pull more than that, you'll just pop the circuit breakers.

- Warren
 
Originally posted by Juxt
By my calculations then in the US with good ol' 120-volts you should be able to carry 1800 watts on a wall outlet.
Yes, but as you know, generally more than one outlet goes to the same breaker. When designing a building, you put a maximum of 10 outlets (depending on known usage) on a circuit and assume 180w per outlet.
If you know (for example) that an outlet supplies power to a window air conditioner, you put it on its own circuit.
 
Right Russ. Code says "The rating of anyone cord and plug-connected utilization equipment shall not exceed 80 percent of the branch circuit ampere rating. Fixed in place equipment shall not exceed 50 percent where lighting and convenience outlets are also supplied". On anything with a continuous load (3 hours or more) ampacity should be at least 125 percent of full load rating of the equipment.(like heat, air conditioning, motors, etc...) Please be careful.
-Mike
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...