How to incorporate core losses in an ANSOFT 2D transformer model

AI Thread Summary
Incorporating core losses in an ANSOFT MAXWELL 14.0 2D transformer model can lead to significant simulation issues, such as incorrect line currents and phase relationships. Suggestions to resolve these problems include verifying the material properties of core sections, increasing mesh density for better accuracy, and potentially using a more advanced core loss model. Additionally, switching from a transient to a frequency domain solution type may yield improved results. If challenges persist, consulting ANSYS technical support can provide tailored assistance. Accurate modeling of core losses is essential for reliable transformer performance simulations.
Shantanav
Messages
9
Reaction score
0
I am designing a 2D model of a three-phase core-type transformer in ANSOFT MAXWELL 14.0. While doing so I have encountered a strange problem.

Start of the problem:-

While designing the transformer, I wanted to incorporate core losses. So, I did the following steps:-

Excitations -> Set Eddy Effects -> checked the various core sections in my model (because eddy current effects occur in the transformer core)

and also

Excitations -> Set Core Loss - > checked the various core sections in my model (because core loss effects occur in the transformer core)

Symptoms :-

Model simulated (using transient solution type) and then gives the following wrong results:

1) Line currents on the primary side (star-connected) are very high (about 10 times)

2) Secondary side (delta connected) phase currents lose their phase dependence, i.e. the phase currents are no more 120 degrees apart, they all are in phase now. However, the secondary line currents are Ok though.

Additional Information :-

If I do not consider eddy current and core loss effects, then the model simulates to give correct results.

Please provide me suggestions/hints/solutions to my problem - how to incorporate core losses correctly in my model.
 
Engineering news on Phys.org
I know nothing about ANSOFT MAXWELL 14.0, so this is a case of the blind leading the blind.

Forget about the transformer and merely add resistance to the circuit. There will be three resistors, each resistor will be line to line. These resistors will be the core loss.
Check that the phase voltages are all equal. Check that the phase currents are all equal.

Still without the transformer but with the resistors, add inductors line to line.(The inductors will be in parallel with the resistors) There will be three inductors. Check voltages and currents the same as before.

With the resistors and inductors installed, add the transformer. (Resistors and inductors should be between the input and the transformer) Repeat the checks, everything should be OK.

If there are still problems, post a schematic and someone may be able to help you.
 
Last edited:
Hello Carl Pugh,

Thanks for your suggestion. I would like to ask a question here - by 'resistors' and 'inductors' do you actually mean core-loss resistances and magnetizing inductances ?

Thanks,
Shantanav
 
Yes.

The transformer has a no load loss. (Core loss)
Divide the core loss by three. Select a resistor that has this loss when connected line to line.
Calculate the current through one resistor.

The exciting (Line) current for the transformer should be given.
The phase current (Current through the inductor) is the line current divided by 1.732.
The current through the inductor should be the phase current minus the current through the resistor. REMEMBER that the current through the inductor in at 90 degrees from the current through the resistor.

Good Luck
Carl
 


Thank you for sharing your problem with incorporating core losses in your ANSOFT 2D transformer model. Core losses are an important aspect to consider in transformer design, as they can significantly impact the overall performance of the transformer.

There are a few potential solutions to your problem:

1. Check the material properties of your core sections: It is important to make sure that the material properties of the core sections in your model accurately reflect the real-world material properties. If the material properties are incorrect, it can lead to incorrect simulation results.

2. Increase the number of mesh elements in the core sections: The accuracy of the simulation results can be improved by increasing the number of mesh elements in the core sections. This will allow for a more detailed representation of the core and its losses.

3. Consider using a more advanced core loss model: ANSOFT MAXWELL 14.0 has a built-in core loss model, but it may not be advanced enough for your specific transformer design. Consider using a more advanced core loss model that takes into account factors such as magnetic field distribution and frequency.

4. Use a different simulation type: Instead of using the transient solution type, you could try using the frequency domain solution type. This may provide more accurate results for your specific design.

5. Consult with ANSYS technical support: If you are still having trouble incorporating core losses in your model, it may be helpful to reach out to ANSYS technical support for further assistance. They will be able to provide more specific guidance based on your model and design.

Overall, it is important to carefully consider all aspects of your transformer design, including core losses, to ensure accurate simulation results. I hope these suggestions are helpful in resolving your issue. Best of luck with your transformer design!
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...