Engineering How Do You Calculate Apparent and Reactive Power in AC Circuits?
The discussion focuses on calculating apparent and reactive power in an AC circuit with a power factor of 0.72 lagging and a true power of 375 W. The apparent power is calculated to be approximately 520.83 VA, while the reactive power is found to be around 361.44 VAR. The magnitude of the current flowing in the circuit is determined to be 4.34 A, and the impedance is calculated as a complex value, indicating the circuit is inductive. Participants also discuss the importance of understanding complex numbers for accurate impedance calculations, emphasizing the need for proper arithmetic with real and imaginary components. Overall, the calculations and concepts presented are validated and refined through collaborative input.
  • #51
Sorry this is how the learning material shows how to write it. It's not so much an L but a symbol that denotes an angle or am I missing the point.
Ztotal = 27.65 +44 degrees Ohms
Z = 21.52 +62.58 degrees Ohms
Regards
  • #52
Regards
Ah! Okay, understood. If you go to the Advanced editing panel to compose your post then you will find an actual angle symbol ∠ available in the Quick Symbols menu.
  • #53
Ok brilliant.
So is my answer now correct for the question (4) or is there anything else to do?
Thanks
  • #54
Electest said:
Ok brilliant.
Thanks
You're good to go with either representation of the impedance (they are after all just two representations of the same complex value).
  • #55
Thanks again
So my answer should show the Z values calculated not the Z totals. I've got it now :-)
  • #56
Hi, sorry to resurrect this thread but I'm confused by your working out. I understand your reason for using complex numbers but when I try and confirm the voltage drops they don't add up to the supply voltage 120V?
or am I missing something?
Thanks
  • #57
Thanks
There's no way to tell if you're missing something if you don't show us what you have...
Show your work!
  • #58
I was just using the equation Vs = √ VR2 + VL2
But I now see you can't because of the complex number.
  • #59
charger9198 said:
For the circuit given in the power factor is 0.72 lagging and
the power dissipated is 375 W.
Determine the:
(1) apparent power
(2) reactive power
(3) the magnitude of the current flowing in the circuit
(4) the value of the impedance Z and state whether circuit is inductive or
capacitive.
(1) Apparent power = True power / Power Factor (S=P/pf)
= 375 / 0.72
= 520.8333 VA
(2) Reactive Power = SQRT (apparent power^2) - (True Power^2)
= SQRT (520.8333^2)-(375^2)
= SQRT (130642.3264)
= 361.4448 VAR
(3) Magnitude of Current
Power= Voltage*Current *Power factor (P=V*I*pf)
375 = 120*I*0.72
I = P/(V*pf)
I = 375/(120*0.72)
I = 4.34 A
(4) Total ohms = Voltage/Current
= 120/4.34
=27.6498 ohms (minus 10)
z = 17.65 ohms
The power factor is lagging within the circuit therefore the the virvuit is inductive
Am i on the right lines here? or is there a better way of calculating the above results
Hello Charger and Oneill
I am currently going through the same coursework and just wanted to share my answers and thoughts- hoping for some feedback so that I can be sure that what my understanding is, is correct
Now...there are numerous equations that involve P, R and I the first one that jumps out is the P=VI or P=I^2R P = dissipated power V= supply voltage I = current
now my thinking is you can't use the P=VI as this would only give you the true power value, which in turn would not give you the correct I value
I then ventured onto P= I^2R - but then i thought this would only apply to a purely resistive circuit, which this obviously isn't as the pf is lagging 0.72
I then decided on (s) = Vs*I s= apparent power (which includes the total circuit voltage) Vs= voltage supply
I = 520.83/ 120 = 4.34 A
is this the correct way of thinking ?
  • #60
Yes, that will work.
  • #61
Is it correct to assume that the current value is the same throughout the circuit ? or would you obtain different value i.e. across the resistor
  • #62
It is a series circuit, so there's no option: The current must be identical throughout.