Can a Loss of 30 Volts Cause an Electric Motor to Overheat?

AI Thread Summary
A 30-volt loss in power supply can contribute to an electric motor overheating, especially if the motor is operating near its maximum current draw. The motor's insulation class may allow for higher temperatures, but inadequate ventilation or external heat sources could exacerbate the issue. It's essential to ensure that the generator's output matches the motor's frequency and specifications. Increasing the generator's voltage may not resolve the overheating if the underlying issues, such as mechanical load or ventilation, are not addressed. Further readings and checks on the motor's specifications are recommended to diagnose the problem accurately.
Joe P
Messages
2
Reaction score
0
Hello, looking for some information on electric motor theory for a problem I encountered on a friends machine. An on site generator is our power supply, our motor requires 480v/ac 3phase, our generator is providing 500v/ac but we are losing 30 volts under load from our extension leads. our motor is running very hot but not tripping overload relays. My question is - could the 30 volt loss of power cause this problem. Also if I increase the voltage output on my generator will it solve the problem. Thanks joe
 
Engineering news on Phys.org
Without knowing how the overload relays are sized, the mechanical load and current drawn by the motor vs. the nameplate max current it is hard to recommend anything. Accepting 30 volts of loss in the wiring is not exactly good practice even if it does put the voltage at the motor right where you want it. Also, 'very hot' is a relative term. It can depend on if the motor is ventilated in the way that the designers intended.
 
Is it possible the motor has a problem? If so, maybe that's where the 30 volt drop is coming from.
 
Presuming the overload protection is suitable set on then the current it is in its correct limits. Elevated voltage could raise the no-load current-this could be checked of course. Usually the rated voltage is 460 V so 500 V [if this is the measured voltage at motor terminals] but 8.7% more it is not so elevated voltage.
The motor could be “very hot” if the insulation permits this. Insulation class H permits a conductor temperature of 180 dgr.C and 70-80 dgr.C outside stator surface could be permissible.
However the overload protection does not “protect” the motor against a defective ventilation or if a heat source in vicinity may deliver a substantial heat –even sunshine or else.
 
Joe P said:
our motor is running very hot but not tripping overload relays.

Hi Joe P. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

Check that the generator is matched to the motor's frequency, e.g., both 60Hz.
 
Last edited by a moderator:
Thank you for the the helpful info, We are going to take more readings and check the motor tag specifications,
Thanks all Joe
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...