Connecting 380v 50hz 3ph euro motor in Canada?

  • Thread starter Thread starter Not_Newton
  • Start date Start date
  • Tags Tags
    Canada Motor
AI Thread Summary
Running a 380V 50Hz three-phase Euro motor in Canada, where the standard is 60Hz, poses challenges. A step-down transformer can be used for voltage adjustment, but if the motor requires variable speeds, a Variable Frequency Drive (VFD) is necessary, which can be costly. The motor in question is for a car lift, and while it can be connected in a star configuration, it may only deliver reduced power and RPM, making it unsuitable for heavy loads. Replacing the motor with one compatible with Canadian electrical standards may be a more practical solution. Understanding the specific requirements of the machinery is crucial for safe and effective operation.
Not_Newton
Messages
2
Reaction score
0
Hi guys,

I got a question that I can only assume you guys stand a chance of responding properly to. Here is my problem I just received a shippement with machinery to open my new business. Now I am stuck with this problem I am in Canada running 60hz can get voltages of 110-220-440 is it possible to run this motor here in Canada? Got any advice other then don't deal with China? Here is a photo of the technical info on the motor.

[PLAIN]http://garagego.ca/images/IMG00063-20110124-2140.jpg

Thanks guys...
 
Last edited by a moderator:
Engineering news on Phys.org
Welcome to PhysicsForums!

If you don't mind us asking, what is the machine the motor is attached to? Is the motor being driven directly from the wall (i.e. on-off operation), or is there a speed controller on the machine somewhere? If there's only one speed, and you don't mind it running a little fast, you can probably get away with just using a three-phase step-down transformer. If not, you may need a VFD (Variable Frequency Drive) to switch the input frequency from 60 to 50 Hz.

Unfortunately, since all of the above costs money (possibly more than what you paid for the machine) you might be better off just replacing the motor with a similar one with the same torque and speed rating.

EDIT: IANAPE (I am not a power engineer)
 
Fair question, it is the motor of a car lift for a mechanic garage. Witch is why I have limited ressources other then the internet to figure out a solution. So VFD is that expensive ? thing is that I actually have quite a few of these as a matter of fact I was expecting normal so to say electrical devices that plug into the wall like normaly you would expect. I also have the same questions about a welder that I am not to crazy about trying out without knowing what's going to happen when you pull the trigger.
A step down transformer is for voltage right?

Anyways thanks a lot it is one of those problems I wish I did not have.
 
Dear Not Newton,
According to my knowledge, your 440volts are generated from two wires of 220volts by shifting their phases 180 degree out. You can confirm it by
1. individually checking these two wires with neutral first(Voltmeter will show 220V in both wires)
2. Checking the voltage across these two phases (Voltmeter will show 440V)
After confirming the above statements, you can connect the motor in Star.

As per your motor's name plate. It is 3phase motor having 2 poles and 5% slip. You can connect this motor in star. Following is the connection of Star.
Short out U2, V2 and W2 by cable or jumper.
Connect the one phase with U1
Connect the other phase with V1
Leave W1 unconnected.
Your motor will start rotating but it can deliver only 2 horse power ideally (Approx 1.5KW) and slip percentage will increase from 5% to above. Hence motor rpm will reduces from 2850 to below value. It is not suitable for heavy load applications.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...