Determining a heat pump's yearly energy output

AI Thread Summary
To estimate a heat pump's yearly energy output for a building, start by calculating the total heat loss at the coldest outdoor design temperature and the internal heat gain. The difference will indicate the heat required on the coldest day. Next, determine the lowest temperature at which the heat pump can fully heat the building, and analyze local outdoor temperature history. By calculating the heat needed and the heat provided by the heat pump across varying temperatures, you can sum these values to ensure they meet the building's annual energy requirement of approximately 80,000 kWh. Accurate insulation details and temperature variations are crucial for precise calculations.
TSN79
Messages
422
Reaction score
0
A building needs a certain amount of energy during a year (kWh) for room heating. An air to water heat pump has been installed to provide heat to a radiator system (55/40°C). How do I go about estimating how much of the yearly energy need the heat pump will cover? What confuses me is that the outside air temperature varies from -15 to +20°C during the year, and I don't know how to consider that variable. Not that I would know what to do if the outside temperature was fixed :frown: Does one usually use some average yearly temperature? Could anyone provide som basic procedures here? Thank you!
 
Engineering news on Phys.org
TSN79 said:
A building needs a certain amount of energy during a year (kWh) for room heating. An air to water heat pump has been installed to provide heat to a radiator system (55/40°C). How do I go about estimating how much of the yearly energy need the heat pump will cover? What confuses me is that the outside air temperature varies from -15 to +20°C during the year, and I don't know how to consider that variable. Not that I would know what to do if the outside temperature was fixed :frown: Does one usually use some average yearly temperature? Could anyone provide som basic procedures here? Thank you!
The quality of the insulation in the building walls and roof will be a major factor, as well as what kind of doors are used for ingress and egress (assuming no windows get opened). Do you have any information on the building insulation?

I'll page @russ_watters to get a better reply for you...
 
berkeman said:
Do you have any information on the building insulation?
Not really, but that kind of information has gone into a calculation that sombody else has already done, resulting in a total energy need over a year (for room heating) of about 80 000 kWh.
 
A basic procedure:
1) Calculate total heat loss at the outdoor "design temperature", the typical coldest outdoor temperature.
2) Calculate the internal heat gain.
3) The difference is how much heat is needed to heat the building on the coldest day.
4) The OP implies that the heat pump will not provide the amount of heat calculated in step 3. If so, calculate the coldest temperature at which the heat pump will fully heat the building.
5) Find the outdoor temperature history for your area.
6) Calculate the heat required, and the heat provided by the heat pump, for the range of temperatures from the coldest day to coldest temperature at which the heat pump provides 100% of the heat.
7) Add up the results. The total heat from the heat pump, plus the additional heat needed on the coldest days, should add up to about 80,000 kWh. If so, you are done. If not, start over.
 
TSN79 said:
How do I go about estimating how much of the yearly energy need the heat pump will cover?
I don't understand. Why don't you think the answer is simply, "all of it"?
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...
Back
Top