I'll try to briefly address two posts, apologies if I'm dragging conversation further off topic.
psparky said:
If you run two different phases and share a neutral [sic], ...However, I believe this shared neutral circuit is now "illegal" in USA...
It is not illegal, however code now requires that all ungrounded conductors of a multiwire (shared neutral) branch circuit must be disconnected simultaneously by the branch circuit overcurrent device. So where you could at one time have circuits 1 and 22 (L1 and L2 respectively) share the same neutral in single phase, or 1, 3, and 42 (phase A, B, C) in three phase, this is no longer allowable because the new code forces such shared neutrals to be fed from consecutave breaker spaces ie 1, 3, 5...22, 24...ect so that the handles can be mechanically tied together. The device for disconnecting is not required to be a common trip device however it is permissible. Short answer is you need handle ties or multipole breakers in order to share neutrals legally with the latest NEC. This is really great for reducing the risks of getting into a live neutral on a two or three circuit multiwire branch in an installation which complies with the new code. Relating back to OP I would say this, if the engineer wants two circuits to feed the same switching device I would hope that a means would be provided to disconnect both at the same time for servicing.
Sophie, as to you latest on fusing you've more or less got it with appliance fusing. In essence, so long as there is a means within a piece of equipment such as a fuse or self-restoring breaker, or if it contains a motor or transformer source which is inherently protected or power limited, then overload should not create an issue where the conductors in the supply cord pose a fire hazard. As for short circuit and ground fault protection, one must remember that just as an electrical system can experience voltage transients, similarly just because you're connected to a branch circuit protected at 20 or 32 or whatever amps doesn't mean that is all that can get through. Ultimately you're connected to the so-called "infinite bus" and even at point of use on a small residential system a bolted or arcing fault can draw hundreds, even thousands of amps for a few cycles. The thermal-magnetic inverse time circuit breakers you will find in a modern breaker panel have a component (basically an electromagnet) that will trip instantly in this situation regardless of its rating as 15A, 20A, 30A, or otherwise. The relatively rare cicrumstance where an arcing fault creates a conductor overload relatively close to the rating of a circuit breaker is beginning to be addressed with the introduction of AFCI, or arc fault circuit interruptors which analyze the waveform for signatures of an arcing condition and trip the circuit similar to a GFCI.
The point is, over here it's left to the utilization equipment designer to either size their supply cord consistent with the plug configuration of the receptacle it is intended for use with, or provide some internal means to limit the current imposed on the cord during normal and some abnormal circumstances. It sounds to me as if in UK the means is essentially the same; however I see a greater potential for tampering with a fuse contained in a receptacle or cord cap versus one buried on a control board somewhere inside an appliance.
Sorry again if I'm not making enough effort to stay on topic as I'm finding the conversation here quite interesting and informative, I believe we've covered the original concerns of OP but in the process spawned another useful discussion of more generalized subjects somewhat related to the initial question.