The discussion revolves around the discrepancies in calculating the specific work done by an isentropic pump in an ideal Rankine cycle using two different formulas. The calculations for a compressor operating between specified pressures and enthalpies yielded vastly different results: 388,670 J/kg using enthalpy differences and 488.16 J/kg using the volume and pressure difference. The confusion arises from the assumption that water is a saturated liquid at both states, while in reality, the process is isentropic, indicating that the water at state 2 is a compressed liquid. This misunderstanding of the state of the water leads to the significant difference in calculated work. Clarifying the state of the fluid in each calculation is essential for accurate results.
RoRoRo
Messages
2
Reaction score
0
In a certain thermodynamics textbook, specific work done by an isentropic compressor/pump in an ideal rankine cycles, is given by the following;

Wpump = h2 - h1
Wpump = v(P2 - P1), where v = v1

When I carry out these two calculations between any two states, I get vastly different answers.

For example, compressor in a rankine cycle operating between the following conditions for saturated water;

P1 = 20 kPa
v1 = 0.001017 m3/kg
h1 = 251.42 kJ/kg

P2 = 500 kPa
h2 = 640.09 kJ/kg

Wpump = h2 - h1 = 640090 - 251420 = 388 670 J/kg

Wpump in = v(P2 - P1) = 0.001017 ( 500000 - 20000 ) = 488.16 J/kg

I assume that I'm missing something. Is there any explanation for why I'm seeing such a huge discrepancy in results for two supposedly equivalent expressions?
 
Science news on Phys.org
Is the liquid water saturated in both states?
 
I was assuming that the water was a saturated liquid at both states but because the process is isentropic, its actually a compressed liquid at state 2. I think...
 
RoRoRo said:
I was assuming that the water was a saturated liquid at both states but because the process is isentropic, its actually a compressed liquid at state 2. I think...
Correct.
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...