How Long Should My Double Pipe Heat Exchanger Be for a 22kW Capacity?

AI Thread Summary
The discussion focuses on designing a double pipe heat exchanger for a capacity of 22kW, utilizing chilled water at 7°C and return water at 12°C. The user is facing challenges in determining accurate heat transfer coefficients, with discrepancies between lookup values and their own calculations leading to significant differences in required pipe length. The calculated coefficients of 1189 and 823 W/m²K suggest a much shorter length of 41m compared to the 104m derived from standard values. Questions arise regarding the use of thermal conductivity for water instead of copper and the feasibility of achieving specific temperature changes in the heat exchanger. Overall, the user seeks clarification on their calculations and assumptions for optimal design.
thestudent101
Messages
21
Reaction score
0
I'm trying to design a double pipe heat exchanger for two different water lines. One line is chilled water of approximately 7degC and the other is chilled water return from an air handling unit, of around 12degC. I want to design this heat exchange for a capacity of approximately 22kW. The part I'm having trouble with is the heat transfer coefficients of the water. I'm planning to have a counter-current flow, with the 12degC on the inside copper pipe, with the chilled water running the opposite direction surrounding the other copper pipe. I've assumed there is sufficient insulation around the outside of the system so the overall system is adiabatic. I've tried a few different methods of finding the heat transfer coefficients. One way is simply looking them up, and another calculating them from the Reynold's number and Nusselt number. Both have given me very different answers. My objective is to calculate how long this heat exchanger needs to be for it to have an overall capacity of 22kW. The flow rate can be up to 8L/s and the pipe sizes have no real constraints.

Here's some pictures of what I've calculated and assumed
https://ibb.co/mxz0T5
https://ibb.co/f1GQvk

When looking up the heat transfer coefficients, on the engineering toolbox it listed the coefficients for water-copper-water as 340-455W/m^2K http://www.engineeringtoolbox.com/overall-heat-transfer-coefficients-d_284.html

From my calculations though I've found the coefficients to be 1189 and 823W/m^2K, which changes the length required from 104m to 41m with the calculated coefficients. The engineering toolbox coefficients assume a "practically still fluid", but my velocities are only 0.33m/s and 0.11m/s. This just seems like a very big difference in length required for such low velocities, so just wondering if I went wrong somewhere in my calculations.

One other question, when calculating h1 & h2, I've used the thermal conductivity of water rather than the copper pipe. Is this correct?
 
Engineering news on Phys.org
Also if I wanted to increase the capacity of the heat exchanger, is there anything wrong with assuming the LMTD can be far smaller. If I have the air handling unit return water at 12degC and the chill water inlet at 7degC, is it practically possible to have the 12degC cooled to 7.5degC, and the 7degC chill water heated to 11.5degC?
 
I looked over your calculations, and they looked OK. I got a little lower values for the liquid side Nussult numbers, but not drastically lower. I got about 165 for the tube side using the Seider Tate equation. See what you get.

Using the thermal conductivity of water was the correct thing to do.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Back
Top