How to Calculate Grounding Resistance with Two Electrodes?

AI Thread Summary
To calculate the grounding resistance of two electrodes connected by an ideal wire, the individual resistances of the electrodes are measured at 6 ohms and 7 ohms, with a measured resistance between them of 5 ohms. The correct total grounding resistance when connected is 5.2 ohms. Some participants provided incorrect calculations, including one claiming 1.2 ohms. The discussion emphasizes the importance of showing the circuit for clarity, but the thread was ultimately closed by the moderator. The final grounding resistance value is confirmed as 5.2 ohms.
Edg
Messages
2
Reaction score
0
Member advised to use the homework template!
Hi!

I can't find the method of the solution to this question, it was an exercise on an exam..

There are two grounding electrodes buried in the ground. We make three measurments. First, we measure the first electrode's grounding resistance, which is: 6 ohms. Then, the second's: 7 ohms. Then the resistance between the two electrodes: 5 ohms.
The question is, if we connect the two electrodes with an ideal wire (which has no resistance), then what will be the system's grounding resistance.
We only know this much, nothing more.

The correct answer is: 5.2 ohms.

How can you acquire this result?

3.23 ohms is not the right answer...

Thanks.
 
Physics news on Phys.org
I got a totally different answer of 1.2 Ohms (but I've been out in the rain all day so I may have made a mistake).

Best show us your circuit and attempt to solve. It's a forum rule anyway.
 
Thanks for the answer, but there is no circuit, I could show you. How did you get 1.2 ohms?
(I only know the final result, the 5.2 Ohms.)
 
Draw your own circuit?
 
Mentor's comment: Edg has asked to have the thread closed, so I'm closing it.
 