Is a Contactor Suitable for High Power 3 Phase Transfer Switching?

AI Thread Summary
The discussion focuses on the suitability of using a contactor for a high-power, 3-phase transfer switch rated at 480VAC and 300 amps. Participants suggest that while contactors can be found for this rating, automatic transfer switches (ATS) are typically preferred due to their interlocking features that prevent simultaneous connections. Static switches using SCRs are also mentioned as alternatives for handling such power levels, particularly in critical applications. Concerns are raised about the design process and the necessity of having professional electrical engineering knowledge for such projects. The thread concludes with a warning about the risks of discussing high voltage and power issues in public forums.
littleblackdo
Messages
4
Reaction score
0
I am designing a transfer switch to switch main power to Generator when main power is lost. Main power is 3 phase, 480VAC and rated at 300amps. Is a contactor a good choice for this? I cannot seem to find one rated this high of power.
 
Engineering news on Phys.org
I'm curious. Why design and not just purchase a Automatic Transfer Switch?

http://www.abrahamindustrial.com/buy/images/upload/thum/ASCO_Series_300.jpg

Anyway, just do a google search on "3 phase 300 amp contactors". There's a bunch.
 
There are also "static switches" that easily handle 300 A at 480VAC. They use SCRs and are commonly used in large UPS installations.

For instance, http://www.redoups.com/F24156/static_transfer_switches_singlethree_phase_251000amp.html

Cheers,
Bobbywhy
 
Last edited by a moderator:
Are you looking for a True Transfer Switch - these are typically interlocked (electrically or mechanically) so both sources are not connected at the some time ( I prefer mechanical because electricians LOVE manually pushing contactors closed - so think of manually pushing the Gen Contactors closed when the line contactor is being used - ugly)
So there are mechanical "kits" for some of the larger 3 phase contractors so that both units are not in the same device -

I just googled Surplus ATS and they pop right up

Typically Static Switches ( Thyrisotr / SCR ) are not needed (or are cost justified) due to start up time of Generators - but in critical loads this is sometimes done - can also help with the transfer back to the line(utility)
 
I have to "conceptually" design this for a work project and was looking for ideas prior to meeting on it.

Main voltage is 480VAC, 3 phase Wye with 300A maximum. The Emergency/Alternate Source is 480VAC, 3 phase wye Generator. I was thinking of connecting the Main Source to 3 phase, 4 pole contactor. When power is lost, contactor closes time delay relay which will close another contactor after time limit expires to send start signal to Generator. Does the Contactor need to be rated at 277V or 480? Am I even on the right track with my ideas?
 
What if the generator doesn't start?
 
I am working on transfer switch. I should not have said "send start signal to Generator". I guess it will close contacts in start circuit.
 
littleblackdo said:
I have to "conceptually" design this for a work project and was looking for ideas prior to meeting on it.

Main voltage is 480VAC, 3 phase Wye with 300A maximum. The Emergency/Alternate Source is 480VAC, 3 phase wye Generator. I was thinking of connecting the Main Source to 3 phase, 4 pole contactor. When power is lost, contactor closes time delay relay which will close another contactor after time limit expires to send start signal to Generator. Does the Contactor need to be rated at 277V or 480? Am I even on the right track with my ideas?

Why try to formulate a "conceptual design" in a vacuum? The protection of "critical loads" with an UPS and diesel generator is a mature technology and has developed over many decades. Hundreds of equipment suppliers and thousands of consultants can easliy answer all your questions.

Cheers,
Bobbywhy
 
Thread closed temporarily for Moderation...
 
  • #10
So, littleblackdo, I'm uncomfortable with your lack of professional EE knowledge and the powers involved in your "project". If you have been given this as a work assignment, you should have the professional EE qualifications to answer these questions on your own. Posting high power high voltage questions in a web forum is not a good thing, and is against the PF rules for a reason. This thread is closed.
 
Back
Top