Japan Earthquake: Nuclear Plants at Fukushima Daiichi
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #8,651
If core would hit groundwater we would see KABOOM, but anyway it is hard to say where cores are, sensor data are different for A and B, and also there is not much sensors at all in drywell. If someone would trust current data then it could say that unit 1 core is in drywell, unit 2 part of core in torus, and unit 3 is unknown, temperatures are increasing there but radiation isnt, so we can assume that it is cooling problem. Also parts of cores can be in concrede under drywell or around torus in the basement...
  • #8,652
I've read research that says the amount of steel and concrete mixed in with a melted core makes it improbable it could melt through the concrete floor. The more concrete and steel mixed in with the fuel decreases the temperature, so it slows the whole mess down.
  • #8,653
The KABOOM theory seems to have been dis-proven along with the China Syndrome.
When corium meets water, the Leidenfrost effect comes into play.
We are learning so much from Fukushima!
  • #8,654
Quim said:
Here is a paper which discusses "aquifer recharge" which has been used to combat salt water intrusion into the underground aquifer in Japan. The Japanese have been fighting saltwater intrusion into their aquifer by injecting fresh water into wells and by creating freshwater ponds (basins) over porous stratum. This paper discusses the basin method of aquifer recharge.
http://www.igme.es/internet/Boletin/2009/120_2_2009/311-320.pdf
Current circumstance in Fukushima suggests that the corium have now reached (become at one with) the groundwater. This is a first ever, in this respect the accident in Fukushima has surpassed events in Chernobyle.
Possibly, it is time for those managing the accident to get ahead of events and do whatever is necessary to prevent the spread of contamination to the deeper stratum of groundwater in Honshu.
This forum is sorely lacking the expertise of a geologist as shown in the previous mudstone/bedrock discussion.
Could a poster from Japan find a knowledgeable contributer to join the discussion?
The "battle of Fukushima" would seem to now be an underground battle.
Could you please show the information, link or theory that suggest the corium has now reached the groundwater. I would need to understand your basis before coming to the same conclusion.
  • #8,655
In post #7728 Jorge Stolfi offered this version of events:
"If you dilute very hot molten metal with cooler molten stuff, such as concrete, it will immediatly cool down and remain cool. If you confine a ton of liquid metal in a closed container, it will stay there and slowly cool down. If you cool the surface of a lump of lava, it will form a solid, relatively cool crust and then slowly cool down throughout.
None of these "common sense facts" seem to apply to corium, because its radioactive contents will continue to generate heat from "nowhere" at the same total rate, no matter how much it is diluted or how it is confined. (Mixing with boron can prevent it becoming critical but has absolutely no effect on the decay heat generation.) If that heat has nowhere else to go, the corium will keep getting hotter and hotter until it boild away. (And even then the vaporized material will continue generating heat at the same rate.) If you dlute the corium 100 fold with molten concrete, and then keep that mass isolated, the rate at which its temperature increases with time will be reduced a 100 fold perhaps, but it will remain positive.
So the entire mass --- original corium plus mixed concrete --- will continue to get hotter and hotter without limit; it will only take 3 months to reach the boiling point, instead of a day."
Also, in this case, the groundwater has apparently risen up to make contact with the corium instead of the more expected version of the process.
  • #8,656
That sounds plausible for this situation as well.
The slightly larger reactor at TMI did not melt through the reactor pressure vessel, despite the meltdown from a mistaken cooling cutoff. The Fukushima reactors were battered by the earthquake beforehand, so they may be more leaky than the TMI reactor was, but the only precedent we have suggests the bulk of their cores are still collected at the bottom of their pressure vessels.
  • #8,657
Would we?
The groundtable is not liquid water, just an area of "very wet" dirt with a rather fuzzy top boundary. So, if the molten corium managed to bore into the ground and get down tho the water table at all, I would expect a gradually increasing release of steam, as the dirt is first heated then melted into slag (somewhere between 1000C to 1500C, I guess). That steam would create bubbles in the molten slag and will presumably contribute to insulate the corium from the dirt below it, slowing its descent. The steam pressure will rise until it can push the frothy slag back up through the hole created by the corium, creating a miniature volcano on the drywell floor.
On the other hand, the increased insulation provided by the frothy slag will cause the corium to get hotter. Presumably things will reach an equilibrium where the lava's temperature and pressure are just enough to keep the channel open, and the rate of conversion (dirt+water) ==> (slag+steam) is just enough to carry away the heat produced by the corium.
However the corium may also mix gradually with the slag and thus be carried up with it, until the massa that remains in the hole is too small to melt the dirt around it. Uranium oxide has a much higher density than molten dirt, and its melting point is much higher; so it may be slow to dissolve, as a drop of honey in a glass of water. If the fuel mass is mostly metallic, it may not mix with the slag at all.
  • #8,658
not sure that i would be total agreement that the above quote is what is going on, and there are three reactors... each in different stages and locations, IMOP that is... but would you please clairify what your definition of groundwater is? There seems to be different definitions used by dif. sources.
  • #8,659
There has been a recent (last three days) discussion of a large amount of water in the basement of the #1 building. This water appears to be groundwater seeping in through an earthquake damaged building foundation.
(posts 8559. 8601, #8607 etc)
  • #8,660
Absent any outside cooling, this would surely be true.
However, TEPCO has been jumping through hoops for the past 12 weeks to ensure that outside cooling was always present. That suggests a truce of sorts is currently in effect, with the corium getting enough cooling the keep it in place.
Of course, TEPCO is now struggling to find places to put the massively contaminated water produced by this cooling. If the ground water rises up as suggested, it might have the unwanted effect of reducing the corium cooling, as there would no longer be a flow to carry the hot water away. Not sure how that plays out, sort of a steam volcano, but only powered by 4-6 megawatts of decay heat.
  • #8,661
We can't say what is under reactors now, science 3 months they don't pump off ground water, if we add that water level increased after earthquake, plus water which is leaking from reactors, plus reactors location not far from sea... There could be a lot of water...
  • #8,662
There has been water in the basement for as long as I can remember. There has been way to many reports as to the cause of the water to list. I would agree that some maybe going to be groundwater, not sure if we are using the same defintion as to what is groundwater.
But one would also have to figure that the water going into the reactors for cooling is going to collect in the buildings, along with several other things that could be possible but I don't have time to post the proper links, so I'll leave them out
  • #8,663
However the TMI core was only partially, uncovered through the whole incident, so only a cubic meter or so of the fuel actually melted down. At Fukushima it seems that most of the core melted, at least in one reactor. (Isn't this TEPCo's own assessment now?)
Although the molten fuel at TMI did not breach the RPV, it did melt its way through internal shrouds and baffles on its way to the bottom head. So a breach of the RPV at Fukushima does not seem so unlikely.
  • #8,664
Also in TMI if I understand correct only upper part of core melted and corium doesn't hit RPV
  • #8,665
just a question of curiosity, do you know "abouts" not exact the thickness of the bottom head? the rod intrusion ports seem quite congested and robust.. also when the statement is made that the ...fuel is melting through... are we talking "glob" .. "small particles" ... or "fluid such as water would be" what size would be pertent to flow around/through the rod ports? thanks
  • #8,666
We were discussing about the unit #6. You must be careful not to make conclusions about the unit #1 based on that conversation
In the unit #6 it really makes sense that some groundwater might be seeping in although other explanations also exist. But in the unit #6 there is no corium.
In the unit #1 all water in the basement of the reactor building could have come from the cooling water they have injected into the reactor.
On the other hand groundwater has been medium-level contaminated below #1 - #4. But we don't know the source. It might be that only one of them is leaking and contamination has spread all over (best case) or all of them are leaking (worst case).
Nevertheless, the main thing is to keep eye on the inland deep well which so far has not been contaminated suggesting that groundwater is moving towards sea. The last page here:
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110602e15.pdf
  • #8,667
Maybe I am stupid but I can't understand how unit 5 have 300m3 from ground water and unit 6 13500m3 from ground water, they are so close and 45 times difference...
  • #8,668
That's a good question.
I guess the level of groundwater doesn't have to be the same although they are near each other.
Also the size of leak (through damaged waterproof systems or through concrete only) can differ - it can be "small", "big" or something in between.
Also the tsunami might have left more water in one place than other. Remember that two dead guys were found in the unit #4 turbine building and they were probably killed by tsunami waters. So the tsunami was probably able to hit directly at least turbine buildings.
Tsujitsu proposed this direct hit might also have happened in the reactor buildings. About that I don't know.
  • #8,669
True, but a compact molten mass is much harder to cool down than an intact core. Even if completely immersed in water, it may still remain molten and able to flow; it all depends on its size and heat generation. A solid crust will form, but it may be too thin to hold the mass in place. (Volcanic lava will flow underwater for a while, even at the bottom of the ocean.)
In the best scenario, the fuel did not manage to breach the RPV (yet), and the drywell is flooded until the RPV bottom is underwater. The molten core is sitting at the bottom of the RPV, covered by water. Water pumped into the RPV mixes with the water inside, and the steam plus any excess water exits through some leak/pipe/breach on the side wall. Most of the heat produced by the corium will go into boiling the water inside the RPV, but some will be conducted through the RPV wall and heat/boil the surroudning water.
A previous post analyzed this situation and (IIRC) concluded that heat conduction through the RPV wall woud be so low that the water next to its outside surface may not even get to boil. However, if the corium is molten, the steel on the inside surface of the RPV will be at the same temperature as the corium. If that is over 1500 C, then the steel will melt locally. Depending on the corium's density, this layer of molten steel may float out of the way, exposing the steel underneath to the corium.
Since the corium is producing heat at a nearly costant rate, its temperature will be nearly constant too; so this process could go on indefinitely, until the wall is breached.. If this is happening at all, the rate of progress may be very slow, and it may perhaps take several months for the RPV to be breached.
Thus, IMHO, the current situation of apparent stability --- with low pressures and temperatures near 100 C --- does not guarantee that things are under control.
  • #8,670
Jorge Stolfi said:
Good explanation, thanks!
One thing I don't understand about theormocouples is why the bimetal wires are usually extended all the way to the voltmeter. Why couldn't they be extended only to some cooler place nearby (such as just outside the concrete enclosure), and then have the signal be carried by copper wires to the meter? That would result in lower resistance for the signal and reduced risk of electrochemical effects along the way.
Or is that in fact how it is done?
Thanks for the compliments and for the thorough analysis. As for them being "open", there is a continuum between having a small leak and being wide open, so it may not be a simple yes/no question. Also, for a small leak, the degree of opening may be sensitive to pressure, temperature, flooding, clogging, etc., and so may vary erratically with time.
Thanks! I think I saw mention of it in this forum, but hadn't the time to check it out then.
Thanks again. I am tempted to include those readings in my plots too, but first one question: do they reflect the conditions inside the reactor, or only of the external contamination? In other words, are those gammas and neutrons mostly created by fission and decay inside the reactor's concrete enclosure? If so, does the spent fuel in the SFP contribute to those readings?
Thanks, that is important information.
As for the temperature sensors, I have seen several diagrams showing their approximate location on the RPV, drywell and torus; but I still miss the key details. Namely, where precisely are the RPV temperature measured: on the outside surface of the RPV, or embedded into its wall? If the former, woud the reading be affected by the drywell atmosphere or by water leaks above the sensor? How far is the "water nozzle" temperature sensor from the nozzles and their feedpipes? And so on...
These details are important, for example, to analyze the pressure x temperature plots. The red boiling curve in those plots is relevant only if the temperature and pressure are measured at the same spot in the fluid. Barring gauge malfunctions, the pressure must be indeed that of the fluid at the gauge's intake point, which should be valid for the bulk space inside (except for the hydrostatic pressure gradient in the liquid-filled part). On the other hand, if the temperature is measured on the outside of a 15 cm thick wall, or even embedded into it, it will be some value intermediate between the temperatures of the two fluids in immediate contact with the wall. Thus, one can easily have superheated steam inside the RPV with a temperature reading well below the boiling curve, or (less likely) liquid water inside with a temperature reading well above the boiling curve.
Couldn't find exact locations of individual thermocouples, but extracted the attachment from an old training reference. It shows that RPV thermocouples are surface mounted.
  • #8,671
100% agree in case of turbine buildings, but how water flooded 2 basement floors of reactor 6 building...
  • #8,672
Your answer is as good as mine. :wink:
  • #8,673
There is much uncertainty about how much has melted/relocated and where it is, true, but there is no obvious way for molten corium to get into the torus. Dropping straight down out of the RPV does not intersect any part of the torus, even if you pass through all the steel and concrete below.
The torus water can be highly radioactive depending on how many fission products have passed through it, but it seems highly unlikely that anything liquid or solid from inside the RPV could make its way there.
  • #8,674
YES! This is the doomsday scenario, and it is VERY hard to tell if such a process is happening or not!
You can think everything is heading toward a stable outcome, and then suddenly, BOOM! a huge radioactive steam blast.
  • #8,675
Connection to other metals causes an additional thermoelectric potential to develop. If you measure the temperature of that "cold junction" and compensate for it in the instrument, then you can do this. If the temperature of the cold junction is not known, then the error is also not known, and that could be a bad thing.
To maintain best accuracy, you should have no terminals, connections, or other hardware in the thermocouple loop other than the exact thermocouple alloys. So, terminal blocks, splices, etc. all are made from the same alloys.
In cases like this, the error might be pretty small, just a degree C or so worst case, but with uncontrolled mixing of various alloys (bare copper, tinned copper, brass terminal strips with nickel coating, and on and on) the error could be cumulative and totally unknowable.
So, that's why they typically run thermocouple wire all the way back to the indicator.
Jon
Jon
  • #8,676
Bandit127 said:
[URL]http://www.tepco.co.jp/en/news/110311/images/110601_01.jpg[/URL]
I presume this is the heat exchanger for the Unit 2 SFP.
No, yes, no yes, Maybe?
http://nuclearstreet.com/nuclear_power_industry_news/b/nuclear_power_news/archive/2011/06/01/tepco-starts-spent_2d00_fuel-cooling-system-at-fukushima-unit_2c00_-reports-oil-leak-060102.aspx"
  • #8,677
nice document on those thermocouples. Copper-constantan is a nice choice because neither alloy rusts.
""So, that's why they typically run thermocouple wire all the way back to the indicator.""
or at least to a place where the transition to copper is at a known temperature.
or to an electronic device in the field that takes the microvolt temperature signal, applies correction for local temperature and translates into a convenient higher level for transmission to control room.
Lots of industrial measurement is done with a linear signal of 4 to 20 milliamps as bottom and top of scale . That way if the system loses power the meter pegs low, because 0 milliamps is 25% below bottom of scale and there's no question the instrument is dead.
in my day they were simple analog devices, nowadays they're smart.
  • #8,678
From the press photo archives:2011.5.14
http://www.tepco.co.jp/en/news/110311/index-e.html
"Carrying Work for New Cooling System (Air-cooled) for Residual Heat Removal System in Fukushima Daiichi Nuclear Power Station
(pictured on May 13th,2011)"
Heat Exchanger and drain http://www.tepco.co.jp/en/news/110311/images/110514_f1_1.jpg
Fan http://www.tepco.co.jp/en/news/110311/images/110514_f1_2.jpg
NHK Article http://www3.nhk.or.jp/daily/english/31_42.html
  • #8,680
Derpin said:
I have a couple questions:
• What is the current status of reactors 1-4?
• What techniques/work have nuclear engineers done to achieve this status?
• Are reactors 5 and 6 really worth mentioning relative to 1-4?
StrangeBeauty said:
You ask some questions with potentially some very long answers ;) You might start here:
http://www.jaif.or.jp/english/news_images/pdf/ENGNEWS01_1306898792P.pdf
or here
http://en.wikipedia.org/wiki/Fukushima_Daiichi_nuclear_disaster
Thanks, I tried the wikipedia article before but it was just way too information-intensive, that is to say I couldn't digest everything they were saying. I'll try to take what I need out of this pdf. :smile:
  • #8,682
If fuel is indeed molten, what are the chances of heavier elements collecting together?
Can the Uranium and Plutonium separate from the boron and steel?
  • #8,684
The scale of such a blast could be estimated. The cores are currently producing between 4-8 megawatts of thermal decay heat each. That amount of heat will generate 5-10 tons of steam per hour, roughly speaking.
TEPCO is currently cooling the reactors with about double that amount of cooling water each hour. This is not quenching all of the steam, but we do not currently have volcanic steam eruptions, but rather a steady strong boil.
So afaik the risk from a core melt into a flooded drywell is that the steam that continues to be produced cannot be released effectively and consequently ruptures the containment more seriously. Or am I missing something?
  • #8,685
It's a waiting game. Chernobyl timeline is another 125 years (give or take) before the remnants of the melted core (corium) can be approached for removal because to this day it is so radioactive.
Here you have 3 cores melted down awaiting enough time to elapse for cooling down just to begin containment, let alone worry about where all the contaminated cooling water ends up.
If the design works for the corium then its path is meant to flow to the bottom of the secondary containment (drywell), spread out, sit there and cool down. Bottom of the drywell is concrete with part of the steel containment shell embedded in the concrete which the corium would have to dissolve/melt through both and then encounter a mass of thick concrete below the shell before it could find natural earth. Cracks in the concrete would not have been envisioned neither would the corium traveling somewhere it's not suppose to like the torus (wetwell). Still it would have a thick concrete foundation to dissolve and melt through but should cool down before that happens.
So, you need time, cooling and keep the corium in place until it cools down. Further contamination is a given, hopefully it can be just localized.
Aside:
Concrete consists mainly of small rocks (example 3/4" or 1") and sand with cement as the binder (glue) and its major usefulness in this case is a hardened thick mass but nothing magical even with embedded steel reinforcement or maybe some type of plating. As the cement itself hardens over its approximate 116 year lifetime (before becoming inert) it takes about 45 years for it (the cement) to become as hard as the natural rock it contains (now concrete is referred to as having a half life of 50 years or so depending on the mix design).
  • #8,686
I have two questions/comments:
1. All the news stories about cooling the #2 SFP say that the point of this operation is to reduce the humidity inside the #2 building. Does anything establish that the humidity actually comes from the SFP? Presumably, there are holes in the containment vessel, and probably in the RPV, and steam is escaping. The steam can be seen in photos of the blow(n)-out panel in the east wall of unit #2. Can the high humidity result from the reactor steam instead of from the SFP steam?
2. A lot of Cs and Sr isotopes have already been washed out of the cores (and, for Cs, vaporized in the first couple of days). Over time, more will be washed out. If the core is molten and covered with a solid shell that is permeable is any way, and the core is immersed in flowing hot water, then almost all the soluble radioisotopes will eventually be washed out. I am pretty sure that the chemical forms of Cs and Sr that occur in corium are readily soluble in water (generally, these are oxides, which dissolve in water to make the corresponding hydroxides). This dissolution will have a very bad effect on the water collection and purification efforts. However, the loss of these materials from the corium should greatly reduce its heat-generating ability and its radioactivity. The fissionable materials should have already decayed (or mostly decayed?), and most of the heat produced now (and in the longer term) is from radioactive decay (unless I'm missing something). It seems to me that TEPCO could end up with very hot water (that Areva thinks they can cleanse and I think will mostly end up in the ocean) and not-that-hot cores that will actually solidify and not pose the type of explosion risk that some posts suggest.
  • #8,687
The water level in the basement of the incinerator building has stopped decreasing. As the water leaked into the corridor between buildings, the measured radiation increase in nearby ground water is believed to be mainly caused by the rain : http://www3.nhk.or.jp/news/html/20110601/t10013241691000.html .
The water level decrease in the basement of unit 1 reactor building is suspected to be caused by a leak on the unit 2 side : http://mainichi.jp/select/jiken/news/20110603k0000e040073000c.html
If nothing is done, the contaminated water from unit 2 and unit 3 will start leaking into the sea on June 20th, but the water purification system is supposed to start on June 15th. However it is possible that heavy rains may cause a leak before June 15th : http://mainichi.jp/select/jiken/news/20110603k0000e040073000c.html
In mid-August, [Tepco] will also install an underground storage tank that can hold 100,000 tons of highly radioactive water.
http://www3.nhk.or.jp/daily/english/03_19.html
  • #8,688
No, I don't think that it is from SFP, unit 2 SFP power is much smaller than in unit 4, and unit 4 wasnt generating steam always, also unit 2 SFP temperature was for example 45C but steam was still there, and unit 2 core and drywell are at atmospheric pressure, also on pne of movies when they zoom in into hole in wall we can see some debris and that steam is not only from left (sfp location) but also from center
  • #8,689
According to the following Tokyo Shinbun article, the earthquake caused cracks in the walls of unit 5 and unit 6, through which ground water has been leaking. From April 4th, about 10000 tons of that water were released into the sea in order to prevent the diesel generator(s) and pump(s) at those units from being flooded : http://www.tokyo-np.co.jp/article/feature/nucerror/list/CK2011052002100005.html
I see one more possibiliy explaining the larger amount of water remaining now in unit 6 : the sea discharge could have been mostly from unit 5.
  • #8,690
As far as the documentation suggests, that temperature is for the skimmer surge tank, not the fuel pool itself. Thats why the temperature goes up when they inject water, because it causes some of the hot pool water to move into the skimmer tank.
I am very interested to learn how much of the steam in unit 2 is from the pool vs the reactor. I doubt that TEPCO or the regulators are very sure either, I have heard them say that steam may be coming from both, but that they believe a lot comes from the pool and cooling it will help a lot. This may be based more on wishful thinking than evidence, but it is possible that their explorations inside unit 2 building taught them something. We will all just have to see what happens when they get the pool cooling working for long enough to make a theoretical difference. I would not be shocked if the reactor was causing a lot of the problem, and they are just dealing with the fuel pool because its much easier to solve this than the reactor problems, but you never know, a lot of the steam really might be from the pool.
  • #8,692
It seems the discussion here about unit 2 cooling was timely, we don't have long to wait to see if the pool cooling has helped humidity:
http://www3.nhk.or.jp/daily/english/03_03.html
TEPCO cools storage pool in No.2 reactor building
The operator of the Fukushima Daiichi nuclear power plant says it has succeeded in lowering the temperature in a storage pool for used nuclear fuel at the No.2 reactor after it started operating a cooling system there.
Tokyo Electric Power Company says the temperature in the pool dropped to 38 degrees Celsius on Thursday from about 70 degrees previously.
TEPCO had anticipated that it would take about one month to lower the temperature to about 40 degrees.
In the No. 2 reactor building, steam released by the storage pool has been pushing up the humidity level to 99.9 percent. Such excessive humidity has prevented recovery efforts so far.
The company installed a circulatory cooling system to lower the pool temperature in order to reduce humidity and began operating the system on Tuesday.
Since the temperature has sharply decreased TEPCO plans to inspect the interior of the building as it suspects humidity has also declined. If the situation has improved, it will install systems to remove radioactive substances.
The company plans to start operating similar cooling systems at the storage pools in the No.1 and 3 reactor buildings in June, and in the No.4 reactor building in July.
Friday, June 03, 2011 05:11 +0900 (JST)
I'll have to double check my time correlations but I think I was looking at TEPCOS live feed early Friday JST and the usual steam coming from reactor 2 building was apparent, so I do have my doubts as to whether TEPCO will discover a much better situation in reactor 2 when they enter, but I hope to be wrong.
  • #8,693
Thanks, I translated it using Google translate. One paragraph says:
According to the Toukyoudenryoku and Nuclear Safety Agency, METI, diesel generator No. 6 reactor building basement, five or six pumps were in the basement of the turbine building of the Unit. The earthquake cracked walls, underground water had flowed.
Original:
経済産業省原子力安全・保安院や東京電力によると、ディーゼル発電機は6号機原子炉建屋の地下、ポンプは5、6号機のタービン建屋の地下にあった。地震で壁にひびが入り、地下水が流れ込んでいた。
It's really hard to tell if they mean unit 6 turbine building walls were cracked or unit 6 reactor building walls also. The latter would be more serious.
  • #8,694
~kujala~ said:
Thanks, I translated it using Google translate. One paragraph says:Original:It's really hard to tell if they mean unit 6 turbine building walls were cracked or unit 6 reactor building walls also. The latter would be more serious.
I would translate the sentence quoted from http://www.tokyo-np.co.jp/article/feature/nucerror/list/CK2011052002100005.html as follows :
According to sources such as the NISA and Tepco, the diesel generator(s) were located in the basement of unit 6 reactor building and the pumps were located in the basements of unit 5 turbine building and unit 6 turbine building. Cracks were created in walls during the earthquake and the groundwater flowed inside.
In the following article published on May 8th, Tepco is reported as acknowledging the presence of cracks in the underground walls of turbine buildings, but the article does not say which units are concerned. An unnamed Tepco manager is quoted as saying "Because of the earthquake, cracks have expanded and new cracks have been created, so that there is a possibility that ground water is leaking inside. The earthquake resistance of turbine buildings is not as high as that of reactor buildings" : http://www.tokyo-np.co.jp/article/national/news/CK2011050802000039.html
A Chunichi article published on May 4th quotes an unnamed Tepco employee who was working at unit 6 when the earthquake struck : "cracks were formed on a part of the inside wall of the turbine building". Plant manager Masao Yoshida is quoted as saying that originally water was seeping in large amounts at units 5 and 6 before the earthquake : http://atmc-tokyo.com/radiation/1285/
1) Do you mean I (Tsutsuji, not Tsujitsu) ?
2) Could you provide a link to the post where I could have said this ? I don't remember.
  • #8,695
Sorry, I guess what you meant was the unit 6 turbine building was hit by the tsunami and then from there a flow of water could reach also the unit 6 reactor building:
What about #4 : Unit 6 hit and flooded by a tsunami ?
I thought you were referring to the unit 6 reactor building here as I was also talking about the reactor building:
https://www.physicsforums.com/showpost.php?p=3310809&postcount=7821
https://www.physicsforums.com/showpost.php?p=3310818&postcount=7822
  • #8,696
Thanks for the links. I must have overlooked the fact that the preceding discussion dealt specifically with the reactor building. I confess that what I had in mind when I made that reply was unit 6 as a whole.
Anyway, the inundated area extends west of unit 6 reactor building, above the OP+13 m ground level as reported on http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110409e9.pdf and even west of units 5 and 6's high voltage transformer building as reported on page 29 of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_110525_01-e.pdf
  • #8,697
It is strange that tepco doesn't show us any pictures from unit 5 and 6, there is no much information about those units, they are working in control rooms there ?
  • #8,699
Steve Elbows wrote:
"""Re: Japan Earthquake: nuclear plants
A new pressure indicator for reactor 1 is being installed, tech details here:
http://www.tepco.co.jp/en/nu/fukushi...10602_02-e.pdf
Same planned for reactors 2 & 3 if they can ever get working conditions inside the buildings improved."""
At Last! that will put to rest wondering about the sense point locations, elevation differences and health of existing instruments. i note their elevation head equates to 0.18Mpa not quite two atmospheres.
  • #8,700
The following article is reporting the detailed contamination data for the two nuclear power plant operators previously reported ( page 531 of this thread : https://www.physicsforums.com/showthread.php?p=3329327#post3329327 ) as "may exceed the 250 mSv limit" :
The 30 year old one has 210~580 mSv of internal contamination adding to the 74 mSv external contamination.
The 40 year old one has 200~570 mSv adding to 89 mSv.
http://www.yomiuri.co.jp/national/news/20110603-OYT1T00778.htm
49K
449K
274K
16K
11K