Line Current in a 2 phase transformer

AI Thread Summary
To calculate the primary line current for a 2-phase 30kVA transformer using two phases from a 3-phase source, the approach is similar to single-phase calculations. The voltage between the two phases (L1 and L2) is 400V, leading to a current calculation of 30kVA / 400V = 75A. The discussion clarifies that this scenario effectively treats the two-phase connection as a single-phase system for current calculations. Concerns about safety and qualifications for working with transformers were also raised, emphasizing the importance of consulting a qualified electrician for practical applications. Understanding the phase relationships and voltage levels is crucial for accurate calculations.
anoor
Messages
2
Reaction score
0
I am a graduate engineer and have been set a small task to work out the current (primary side) in a 2 phase 30kVA 415:650 transformer. The 2 phases have been utilized from a 3 phase source and are hence 120 degrees out of phase.

I understand had it been a 3 phase 30kVA transformer I could calculate my current by 30kVA / 415 / route*3 = 42A.

If it was a single phase then simply 30kVA / 415 = 73A.

However if I am only using 2 phases from a 3 phase source yet still need to produce 30kVA of power, how do I calculate the line current?

Thanks in advance.
 
Engineering news on Phys.org
Hello Anoor and Welcom :

I think we will need a little more info -- you are describing a 30KVA trans but the Voltage is 415:650? And by 2 phase - is the secondary like an Open delta - or some other arrangement? Best bet is to post a diagram of the nameplate info.

Lastly -It is not clear if you are actually working on this physically? In the USA you would not be a " qualified person" - working on this is extremely dangerous, does your University have a qualified electrician that you can work with?.
 
I am not working on it physically its just in theory.

Maybe its my poor explanation ill try again!

If I have a standard 230/400V switchboard and want to connect a transformer it would normally be a 3 phase (400V) or single phase-neutral (230V). However if I wanted to connect a transformer to phases L1 & L2, instead of the neutral (giving me 400V). What would my line current be on the primary and how would I calculate it? I apologise if my ignorance doesn't allow me to adequately suscribe the situation! I have attached a pdf showing an extract of the schematic, I hope this helps!

Thanks again.
 

Attachments

OK the diagram help a little. If you think of the "phase" as between the lines, as in L2-L3 - this is really a single phase question - IN the USA we refer to this as Line to Line. In this case there is no phase angle - so the Line current is KVA/V - also the transformer input or out put is only a 2 wire device - right?

The lines L2 and L3 are only out of phase 120Deg relative to the neutral
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...